    COC and Brass Heritage switch

    Had a phone call this morning in connection with a COC inspection being done in an old house , all refurbished with oregan pine wooden doors , floors etc.

    Need to ask all the clever people what you would do if you came across the old type Heritage brass switches ( similar to pic ) in an installation – The switches fit in beautifully with the finishes and anything else will ruin the finished look.
    The outer brass cover screws onto the brass toggle - The switches are mounted on the wooden door frame

    My feeling is that the switches need to be replaced with something as it is not possible to earth.
    I know Clipsal used to do the heritage range which made life simple , but it has been discontinued

    Interested to know what you would do

    Click image for larger version

Name:	Heritage  switch.jpg
Views:	1
Size:	5.4 KB
ID:	269672
  • Leecatt
    Silver Member
    • Jul 2008
    • 406

    #2
    The same thing happened to me when I did a COC in Johannesburg about 12 to 13 years ago.
    I called my contact at the ECA and was given the following advice.
    There is a space between where the wires are connected and the outer metal Parts Of The Switch. There was also a piece of porcelain distancing the actual switch rocker from the workings of the actual switch.
    I was advised to pass it as being reasonably safe which I did.
    To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

    Comment

    • Leecatt
      Silver Member
      • Jul 2008
      • 406

      #3
      Also see SANS 6.12.3.2
      Neither of the cover nor the toggle switch are touching a conductive surface and meet requirements in parts C4
      To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

      Comment

      • GCE
        Platinum Member
        • Jun 2017
        • 1488

        #4
        HI

        Also looked at 6.12.3.2 -(2) - need not be earth if ,2) out of arms reach from a structure that is bonded to earth

        Then read a bit further to 6.12.3.3 - Metallic frames and enclosures of electrical equipment shall be made electrically continuous

        Decide to check on definition of electrical equipment - item or combination of items , including wireways, which is used for generation , conversion, transmission or distribution of electrical energy.

        Seems that 6.12.3.3 is in direct contradiction to 6.12.3.2

        Wonder why I became a Sparky when I actually need to be an English professor, or Lawyer to try and understand what we can and can't do.

        Comment

        • AndyD
          Diamond Member

          • Jan 2010
          • 4951

          #5
          Can the toggle and cover no9t be classed as an extraneous conductive component if the IR to the MET is >7.6kΩ? I'd be tempted to hold it to a far higher standard of IR though if there's any other conductive items within reach that weren't extraneous.
          _______________________________________________

          _______________________________________________

          Comment

          • Leecatt
            Silver Member
            • Jul 2008
            • 406

            #6
            It seems there is a mistake in the SANS
            6.12.3.2 has two part C,s and one part A
            However.....

            6.12.3.2 The following do not need to be earthed:
            b) Exposed conductive parts of fixed electrical equipment that are
            4) not touching a conductive surface.( The bell cover is usually screwed onto a bakerlite base)

            6.12.3.3 deals with metallic frames and metallic enclosures
            6.12.3.3 Metalic frames and metallic enclosures of electrical equipment shall be made electrically continuous
            The bell cover is not a frame.
            The bell cover is part of the electrical equipment as a whole. An enclosure is a part that protects the electrical equipment from exposure such as a metal box or a DB

            Just my two cents worth
            To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

            Comment

            • Dave A
              Site Caretaker

              • May 2006
              • 22820

              #7
              Originally posted by Leecatt
              It seems there is a mistake in the SANS
              6.12.3.2 has two part C,s and one part A
              And no part b.
              Quite clearly a typo and needs to be passed onto the technical committee, I suggest.
              Good spot, Leecatt

              Question - When you remove that metallic cover, doesn't this expose conductive / current carrying parts?
              Participation is voluntary.

              Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services

              Comment

              • Leecatt
                Silver Member
                • Jul 2008
                • 406

                #8
                Originally posted by Dave A
                And no part b.
                Quite clearly a typo and needs to be passed onto the technical committee, I suggest.
                Good spot, Leecatt

                Question - When you remove that metallic cover, doesn't this expose conductive / current carrying parts?
                Yes, the conductive parts would be exposed, which would put it in contravention of SANS 5.2.1 b)
                Perhaps a strategically placed screw?
                To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

                Comment

                • GCE
                  Platinum Member
                  • Jun 2017
                  • 1488

                  #9
                  Hi Leecatt

                  Thanks , I think you are spot on and that under 5.2.1 the old type heritage switches would need to be removed .

                  Somebody will come back with the date of installation and that therefore they were allowed to be used then - I would agree as long as no rewiring has happened.
                  Most of those switches where installed in the day of VIR wiring so there would have been alterations to the installation.

                  I was contacted yesterday and told that GLO electric have a new heritage type switch with an earth pin.I would rather replace all the switches and sleep at night

                  Comment

                  • GCE
                    Platinum Member
                    • Jun 2017
                    • 1488

                    #10
                    Hi

                    Thought I would resurrect this conversation to see if anybody had a new view or idea

                    We have just been asked the question again and I still seem to think that VIR and old brass switches should be replaced