Originally Posted by
Derlyn
Regulations have become so complicated that trying to establish whether a 60W light fitting, fixed to a wall in a bedroom, ( NOT A HIGH BAY LIGHT IN A FACTORY ) wired with 3 core 2,5mm cabtyre flex, properly earthed and neatly clipped to the skirting board and plugged into a socket outlet is legal or not, is simply impossible.
The question to answer is what part of SANS 10124-1 does it contravene?
I've been watching the discussion with some interest. Yes, there are quite a few different mentions of luminaires fed off a socket outlet in the Code with requirements in particular circumstances. However, I can find no general exclusion that forces luminaires to be supplied off socket outlets only as per Sections 6.14.1.4 to 6.14.1.6.
Luminaires are also recognised under fixed appliances - as example in the Fixed Appliance section -
6.16.1.5 A socket-outlet shall supply only one fixed appliance. The use of flexible cords of length exceeding 3 m is not recommended. The reason for
this recommendation is an endeavour to ensure operation of the overcurrent protective device. (But see also 6.14.1.4 for luminaires.)
They are fixed appliances, but enjoy particular exemptions that are standard requirements of other types of fixed appliances (particularly the isolating device requirement). There are also circumstances where a luminaire may be supplied by a socket outlet without the socket outlet being on earth leakage. However, this does not mean that there may not be an isolating device in the supply to a luminaire, and that luminaires may not be supplied by a circuit that has earth leakage protection.
I think at the end of the day when "may" is confused with "must" (or "shall") - this is where the interpretative confusion starts...