Results 1 to 7 of 7

Thread: Surfix through wall

  1. #1
    New Member
    Join Date
    Nov 2015
    Location
    Johannesburg
    Posts
    3
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Question Surfix through wall

    In terms of "the code", does the aluminium sheath in Surfix cable negate the need for using conduit when passing through walls? i.e. is it acceptable to pass surfix through a 10 mm hole to mount a lamp without boring a 20 mm hole to install conduit, provided no fire can pass through the hole?

  2. #2
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,935
    Thanks
    581
    Thanked 937 Times in 758 Posts
    It's acceptable to install surfix either on the surface or under plaster without containment but reinstatement of a fire barrier back to its original spec is a different thing entirely.
    _______________________________________________

    _______________________________________________

  3. #3
    Bronze Member
    Join Date
    Mar 2012
    Location
    Account_Deleted
    Posts
    165
    Thanks
    122
    Thanked 23 Times in 18 Posts
    As Andy said: Only exclusion is concrete. Under screed it must be on E/Leakage. Also note UV issue.

    6.3.6 PVC insulated multicore cables with a bare earthing conductor
    and round cable with metal stiffening: (ROUND Surfix as we know it - not "flattex")

    6.3.6.1 The cables may be installed
    a) on the surface,
    b) under plaster,
    c) under a raised floor,
    d) in hollows (such as in walls and partitions) (no additional protection
    being needed),
    e) in roof spaces,
    f) direct in the ground (see 6.4.4.2, unarmoured buried cables),
    g) outdoors or exposed to water (but unless the manufacturer proves
    that the cables can withstand ultraviolet radiation, the cable shall be
    out of sight of the sky), and
    h) under screed if protected by an earth leakage protection device with a
    rated earth leakage tripping current (rated residual current) IΔn not
    exceeding 30 mA. Amdt 5
    6.3.6.2 These cables shall not be buried direct in concrete.

  4. Thanks given for this post:

    Dave A (04-Nov-15)

  5. #4
    New Member
    Join Date
    Nov 2015
    Location
    Johannesburg
    Posts
    3
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Quote Originally Posted by AndyD View Post
    It's acceptable to install surfix either on the surface or under plaster without containment but reinstatement of a fire barrier back to its original spec is a different thing entirely.
    Surely 8mm surfix in a 10mm hole is more fire resilient than 8mm surfix in 20 mm plastic conduit?

  6. #5
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,935
    Thanks
    581
    Thanked 937 Times in 758 Posts
    It's kinda a moot point because if you've penetrated a fire barrier neither would be acceptable, you'd still need to reinstate the fire barrier after the installation regardless of which method you've used.
    _______________________________________________

    _______________________________________________

  7. #6
    Bronze Member
    Join Date
    Mar 2012
    Location
    Account_Deleted
    Posts
    165
    Thanks
    122
    Thanked 23 Times in 18 Posts
    This might also help regarding wiring through walls: (and if it is a fire break)

    Page 149:

    6.4.8 Wiring through building elements:

    6.4.8.1 If wiring has to pass right through a building element such as a
    floor, a wall, a partition, or a ceiling, conductors and busbars shall be in a
    non-flammable enclosure or wireway.

    6.4.8.2 If the building element is a fire break, the space around
    a) a cable,
    b) a wireway, or
    c) the wiring in a wireway, if the internal cross-sectional area of the
    wireway exceeds 13 000 mm2,
    shall be completely filled with non-flammable material over the full
    thickness of the building element.


    NOTE 1 Mineral wool is non-flammable.
    NOTE 2 A local authority or fire officer could require extra safety measures to be
    taken.
    Last edited by ACEsterhuizen; 05-Nov-15 at 07:36 AM.

  8. #7
    Full Member
    Join Date
    Apr 2016
    Location
    South Africa
    Posts
    78
    Thanks
    34
    Thanked 1 Time in 1 Post
    Hi ,
    If one has existing surfix only through a house wall .Would the best way to rectify the problem be to disconnect and remove the surfix from the wall , drill and insert 20mm PVC conduit through the drilled hole , add a PVC elbow on either side of the wall to the 20mm conduit ,add 20mm pvc conduit to the elbows on both sides of the wall ,add a two way round box to the added 20mm conduit on both sides of the wall , add PVC glands to the two way round boxes on both sides of the wall , install the surfix cable through this setup. Would this be legal .How would one sort the problem out .

Similar Threads

  1. surfix
    By bergie in forum Electrical Contracting Industry Forum
    Replies: 8
    Last Post: 22-Oct-14, 01:06 AM
  2. Indoor LED Wall Washer
    By AndyD in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 29-May-14, 08:15 PM
  3. surfix in hazardous areas
    By bergie in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 16-Feb-13, 09:14 AM
  4. Wall Street's nightmare about to happen
    By wynn in forum General Business Forum
    Replies: 2
    Last Post: 24-Jul-12, 05:28 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •