Page 1 of 2 12 LastLast
Results 1 to 10 of 19
Thread: Earth leakage problem
    Jan 2019
    Centurion
    Hi guys
    I have just encountered the following problem.
    The earth leakage trips when test button is pressed. The earth leakage tester is plugged on the socket outlet and the 3 LED indicators light up to show that the connections are OK, but when the knob is turned to 30mA, the earth leakage does not trip.
    Can someone explain what could be the problem here?
    Jul 2008
    Germiston, South Africa
    Your earth leakage tester is faulty?
    High earth impedance at the socket maybe?
    Those plug in socket testers are notoriously misleading and inaccurate unless you buy an advanced one like this. http://www.socketandsee.co.uk/socket...et-tester.html
    Jan 2019
    Centurion
    Thanks guys, I think a different type of EL tester would be a good idea.
    It just that I have been using it all the time and I have never had any problems with it.
    Mar 2019
    East london
    Check your supply voltage.
    If you are using a Top Tronic TEL1TLB tester, it will not trip the earth leakage relay if the supply voltage is less than 213 volts.
    Have you checked that the socket outlet has actually been wired through the earth leakage ?
    Derek
    Mar 2018
    Western Cape
    Greetings
    Is that circuit wired through the earth leakage?
    Jul 2008
    Quote Originally Posted by SeanM View Post
    Greetings
    Very good point
    Jan 2019
    Centurion
    The supply voltage is healthy, measured value is 236V and the earth leakage has been used as a main switch. All the circuits are connected with the earth leakage from one neutral bar.
  9. #9
    planet earth
    Plug in the earth leakage tester...you said all 3 lights are on... now switch off the earth leakage unit and see if the 3 lights on the plug tester switch off... they should go off... if not you have a wring problem.
    Test the voltage:
    live - neutral = 236 v
    live to earth = should be the same (236 v) or about 1-2 volt different
    earth - neutral = should be around less than 5 volts
    do a loop impedance test at the socket outlet ...if the the result is within the required limit ...the plug is wired to the earth leakage unit then ...replace the earth leakage unit.
  10. #10
    Mar 2019
    East london
    Quote Originally Posted by Philani View Post
    Easy.
    Try another tester. If it works, replace the tester.
    If same problem, replace the earth leakage relay.
    Process of elimination with only 2 possible outcomes ( all others have already been eliminated )
    Derek
  1. How to isolate an earth leakage problem
    Last Post: 23-Jun-17, 10:53 AM
  2. Earth Leakage
    Last Post: 10-May-16, 10:11 PM
  3. [Question] Earth Leakage problem has experts stumped
    By Alistair Jones in forum Electrical Contracting Industry Forum
    Last Post: 25-Feb-14, 11:38 AM
  4. Earth Leakage
  5. Random earth leakage problem
    By BillH in forum Electrical Contracting Industry Forum
    Last Post: 23-Jan-12, 09:37 PM