    Getting shocked when touching shower taps

    Hi Everyone, I live in a complex that is Sectional title. I have this problem of getting shocked/tingle everytime I'm use the shower. I've switched off the geyser and it still happens. I've switched off the mains and it still happens. I've called an electrician who insisted it was the geyser. His people said the geyser wasn't bonded. So they bonded it, but it still happens. My upstairs neighbors don't have this problem. My next door on either side neighbors don't have a this problem. Any ideas what it could be or else to do? It's also strange as it only happens towards the end of the shower not immediately when u get in.

  2. #2
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,702
    Thanks
    127
    Thanked 160 Times in 150 Posts
    1. Your geyser should be wired through the earth leakage. Check that it is.

    2. If your geyser is on earth leakage then I doubt very much if it has got anything to do with the geyser itself or the geyser element.

    3. To me it sounds like a high neutral loop impedance on the supply to your unit. 99% of the time this is the case.

  3. Thanks given for this post:

    Naynam (06-May-23)

  4. #3
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,507
    Thanks
    138
    Thanked 697 Times in 595 Posts
    Blog Entries
    1
    Quote Originally Posted by Naynam View Post
    It's also strange as it only happens towards the end of the shower not immediately when u get in.
    The reason, is now the water has moistened the tile grout improving the leakage voltage to earth.
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

  5. Thanks given for this post:

    Naynam (06-May-23)

  6. #4
    New Member
    Join Date
    May 2023
    Location
    Johannesburg
    Posts
    6
    Thanks
    3
    Thanked 0 Times in 0 Posts
    Feedback from my electrician:
    "They bonded the geyser but the whole bonding must go deep into the ground 2m deep. So they will come and run an earth cable and dig a hole and sink an earth spike."

    Is the geyser the only source of the problem? Can it be anything else? Has anyone had a similar problem and fixed it? Can you recommend me an electrician in johannesburg who can fix the problem?

  7. #5
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,702
    Thanks
    127
    Thanked 160 Times in 150 Posts
    They can earth as much as they like. Believe it or not, the better your earthing, the more pronounced that tingling on the shower taps is going to be.

    Get the electrician to check your neutral coming in for a high resistance connection somewhere. Could be in the stubby box or kiosk outside. Doesn't sound as if it's further down the line as you say your neighbours are not affected. In all my years of fault finding, when it came to tingling taps, it has always, without exception, been a neutral problem.

  8. #6
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,274
    Thanks
    60
    Thanked 103 Times in 98 Posts
    I would bet my old bicyle tubes that the water is leaking onto a live condutor, or someone has drilled a hole into the wall and a cable is damaged.

    Before wasting time with tracing a fault, what is the loop impedance test result L-PE and L-N and have you done an earth continuity test from the main earth to the exposed metal around the house.

    What is the levated neutral to earth voltage.

    Did anyone do any of these tests. IF your loop impedance test is whithin range why would you need to drop an earth spike?

  9. #7
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,443
    Thanks
    40
    Thanked 337 Times in 283 Posts
    Quote Originally Posted by Naynam View Post
    Hi Everyone, I live in a complex that is Sectional title. I have this problem of getting shocked/tingle everytime I'm use the shower. I've switched off the geyser and it still happens. I've switched off the mains and it still happens. I've called an electrician who insisted it was the geyser. His people said the geyser wasn't bonded. So they bonded it, but it still happens. My upstairs neighbors don't have this problem. My next door on either side neighbors don't have a this problem. Any ideas what it could be or else to do? It's also strange as it only happens towards the end of the shower not immediately when u get in.
    There was a previous post which also had suggestions and solutions - If anything it will show you that it is not always an easy fix or solution and once the problem is solved due to extra earthing the actual problem could rear it's head

    https://www.theforumsa.co.za/forums/...e-shower/page2

  10. #8
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,702
    Thanks
    127
    Thanked 160 Times in 150 Posts
    On a number of occasions in the past, people have requested assistance with problems they are experiencing and we've all without hesitation offered our services free of charge to try and assist.

    It would, however, be helpfull if they can, after finding the fault, give us a bit of feedback but sadly one never hears from most of them again.

    That feedback can, I believe, help us all in the future.

  11. Thanks given for this post:

    Gene (23-May-23)

  12. #9
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,702
    Thanks
    127
    Thanked 160 Times in 150 Posts
    Any feedback on tingling shower taps ?

    Are they still tingling ?

  13. #10
    Full Member
    Join Date
    Jan 2019
    Location
    Durbanville
    Posts
    40
    Thanks
    43
    Thanked 0 Times in 0 Posts
    Exactly the same happened to me but i live in a house - called the elect dept. and they found that the neutral was loose in their sub box in the road, tightened up and all was ok , (live took the route through earth thus the shock ,tingle)
    Just look for a loose neutral on their side

Page 1 of 2 12 LastLast

Similar Threads

  1. [Question] Taps in shower shock
    By Grumpy pixel in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 05-Mar-23, 02:28 PM
  2. Tingling on the taps
    By Isetech in forum Electrical Contracting Industry Forum
    Replies: 6
    Last Post: 02-May-22, 12:45 PM
  3. Tingling while fiddling shower taps during shower
    By Justloadit in forum Electrical Contracting Industry Forum
    Replies: 31
    Last Post: 08-Apr-13, 09:19 PM
  4. Shocked,White and SICK
    By IMGREG in forum General Chat Forum
    Replies: 7
    Last Post: 05-Dec-11, 12:14 PM
  5. can we still be shocked?
    By duncan drennan in forum General Business Forum
    Replies: 1
    Last Post: 25-Jul-06, 03:27 PM