Good day, a client phoned last night telling me that they had no power in the house.
On investigating the situation I found the following
Fault 56 on the inverter, low dc, and no ac or pv input.
The breaker between the inverter and changeover was tripped and refused to reset.
After switching from Inverter mode to Eskom mode with the changeover everything worked normally.
The breaker that supplies ac to the inverter was on and the voltage tested normal at the top and bottom of the breaker.
Will be going back there this morning to open the inverter to test and see if the inverter had tripped inside the inverter
The system had been installed three months ago and it had not been giving problems since.
Any advice would be welcome