    Aircon circuit. Conductor and breaker size ?

    So you do an inspection for COC.
    You find an aircon circuit wired with 1.5mm wire protected by a 20A breaker. Problem.

    Now you have 2 options.
    A. Rewire the circuit with 2.5mm wire or B. Change the circuit breaker to 16A.

    Using a clip on tester you measure the current drawn by the unit is 5.8A.

    Would you quote to do A or B above and why ?

  2. #2
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,370
    Thanks
    38
    Thanked 323 Times in 271 Posts
    Think couple of more questions before giving a definite answer

    What is start up current , has the aircon maybe been changed to an inverter type along the line

    Would think that if it is still old aircon that somewhere along the line there was intermittent tripping and the CB was upgraded

    Problem with downgrading ,and it was an intermittent trip , you could be back there in the next month doing a rewire of the circuit at your own cost

  3. #3
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,500
    Thanks
    138
    Thanked 696 Times in 594 Posts
    Blog Entries
    1
    Alternative use a 16A type D circuit breaker designed for motor starting
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

  4. #4
    Junior Member
    Join Date
    Oct 2018
    Location
    Gauteng
    Posts
    20
    Thanks
    2
    Thanked 2 Times in 2 Posts
    Would also suggest 16A type D circuit breaker

    But also try google the aircon installation manual and check out the recommended circuit breaker sizing, or at least the startup current if available

  5. #5
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,938
    Thanks
    582
    Thanked 938 Times in 759 Posts
    Refer to manufacturers instructions. If they specify a 20A circuit you'll possibly void warranty if you downgrade it to a 15A circuit breaker.
    _______________________________________________

    _______________________________________________

Similar Threads

  1. Aircon circuit
    By Andrew_van_Zyl in forum Electrical Contracting Industry Forum
    Replies: 4
    Last Post: 07-Nov-23, 07:01 PM
  2. Which Circuit Breaker to use 3KA or 6KA?
    By Justloadit in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 21-Jul-23, 11:56 AM
  3. Size of Earth conductor
    By Andrew_van_Zyl in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 07-Jun-22, 01:36 PM
  4. Circuit breaker compliance
    By Pieter00 in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 24-Jul-20, 12:53 PM
  5. Effect of transformer size on main breaker
    By maseral in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 22-May-18, 04:46 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •