    Gate motor circuit

    I have a situation where the buyer of a house for which I produced the COC, insists that the gate motor must be on it's own seperate circuit.

    It is presently wired to a plug circuit and has an isolator next to it.

    How do I prove to him that how it is presently wired is acceptable, or am I missing something ?

  2. #2
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,370
    Thanks
    38
    Thanked 323 Times in 271 Posts
    Request him to show you were in the regulations it states that it must be on it's own circuit or how he got to make that statement
    There is no where

    Gate motor falls under fixed appliances and there are specific fixed appliance's that state that it must be on its own dedicated circuit , like Aircons over 16 Amp , Cooking appliances over 16 Amp etc
    It is actually stated at the beginning of the specific section

    6.16.3.2.1 A dedicated circuit(s) shall be provided for cooking appliance(s)
    that are rated at more than 16 A


    On motors the regulations are quite on dedicated circuits which implies there is no such restriction - Logically if a circuit to an aircon or stove under 16Amp does not have to be separate then a clock motor, gate , garage door motor would not have that requirement
    A gate motor has built in protection and would not require the circuit protection to be sized accordingly as per 6.16.5.1.1




    6.16 Fixed appliances
    6.16.1 General

    NOTE The general requirements in 6.16.1.1 to 6.16.1.12 (inclusive) apply, except
    where otherwise required for specific cases.

    6.16.5 Motors
    NOTE Motors include the motors in automatic doors and gates, garbage disposal
    units, pumps (pool, fountain, spa, etc.), and the like (see also 6.16.1).

    6.16.5.1 Motor protection and control
    6.16.5.1.1 In addition to the requirements of 6.7, the circuit that supplies a
    motor shall have overcurrent protection unless the motor
    a) forms part of equipment that has built-in overcurrent protection,
    b) has an integral thermal protector with an accessible reset button,
    c) has an automatic resetting thermal protector and there is no likelihood of
    mechanical damage or of injury to persons when the motor restarts, or
    d) is of a high impedance type that can stall without overheating (such as the
    motor of an electric clock).


    6.16.5.1.4 Each motor shall be supplied by a manually operated disconnector
    or any other manually operated disconnecting arrangement such as a
    withdrawable circuit-breaker, a removable link, a fuse or by the removal of a
    plug from a socket-outlet
    , which provides at least the same isolating distance,
    for the sake of safety, as a disconnector that is
    a) readily accessible and mounted on or next to the motor, or
    b) visible from the motor, or
    c) lockable in the open position, or
    d) housed in a lockable enclosure other than a distribution board.

  3. #3
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,639
    Thanks
    121
    Thanked 153 Times in 145 Posts
    Thanks GCE.

    I couldn't see myself being wrong on this one, but you know how your mind plays games when you are confronted.

    The buyer works at Daimler Chrysler and one of those who thinks he knows everything.

Similar Threads

  1. DC gate motor, elec fence and garage door solution?
    By Andrew_van_Zyl in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 21-Dec-22, 09:27 PM
  2. D5 gate motor
    By Dylboy in forum Electrical Contracting Industry Forum
    Replies: 6
    Last Post: 15-Dec-21, 05:44 PM
  3. [Question] Gate motor\lights\Electric fence compliance
    By Ferdie_l in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 20-Sep-17, 08:57 PM
  4. Disconnecting a gate motor
    By Leecatt in forum Electrical Contracting Industry Forum
    Replies: 66
    Last Post: 05-Mar-16, 10:08 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •