Hello
Does anybody know whether there is anything wrong with the following picture?? Or is the wiring correct. It has been declined for a COC.
Thanks
Hans
Hello
Does anybody know whether there is anything wrong with the following picture?? Or is the wiring correct. It has been declined for a COC.
Thanks
Hans
Last edited by Dave A; 09-Feb-11 at 11:29 AM.
Hi Oblivious,this is what is called exposed wiring.You can either put the connections in a joint box or use 5A Socket Outlets.Can't really see the wire size,but you should be safe with 1,5mm on 220V downlighters provided your distance is not very long.
Hi Oblivious and welcome to TFSA.
You'll probably get more attention if you start a new thread in future.
The picture clearly shows PVC insulated cables that are closer than 100mm to the 50w halogen dichroic lamp and directly above it. This is contrary to the 0142 regs and would be sufficient for it to fail a COC inspection. You could workaround this if LED lamps were in the fittings (or even CFL), however, the exposed wiring as already suggested could also be the cause for it not passing muster.
The cable sizes and the actual terminations look fine to me.
_______________________________________________
_______________________________________________
andy i do believe if the 100 mm clause had to be enforced correctly i could safely say 90 % of downlights in durban would be illegal....and a huge majoity of COC issued would have to be withdrawn.
i believe the only problem with that light is the cover missing...so long as the standard test finger cannot touch any live wires...
i believe there should have been a junction box with one wire feeding the light and with heat resistant wire or sleeved with asbestos tape...but unfortunately the reality that would be regarded as over doing it.
HI. Thanks all for your valuable input. I will inform you later of the outcome. Great week to you.
Oblivious
Another question, if I may..... I assume this is very stupid. Can I not tape it shut with some sort of special tape? I see murdock mentions something about tape. Chaw
Hi, you hit the nail on the head Andy. The exposed conductors are a small issue here because they cannot be made contact with during the normal use of the lights. The main reason would be the lack of heat resistant wire on the fitting. I must ask here though, is it 100mm or 200mm?
May I draw attention to the two lines ofsurfexflat twin & earth in the picture... There's more going on than just a light connection point here.
Participation is voluntary.
Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services
Well I disagree one one point you make but agree with another. I think the 100mm clause (which might turn out to be a 200mm clause) is important. The operating temperature of these lamps is ridiculously high and can deteriorate the pvc insulation very quickly, in a matter of hours in fact. I can see very good reason for the clause and I could see a significantly increased fire risk if it were ignored. Arguably, this risk may be even higher for the ELV 12volt lamps but that's a discussion for another day, it still holds true for the 220volt version as well.
I do agree that the termination box shown isn't adequate for two FT&e cables as well as the lamp holder wiring. There's only one cable anchor clamp for a start and it would be impossible to refit the lid no matter how tidy your terminations are. It also clearly breaches the 100mm rule so I'm hoping it isn't an SABS approved fitting
Hi Sparks,
I'm not 100% familiar with the 0142 rules, I refer to them for design purposes but don't do any kind of domestic work/installations or inspections. I'm not sure if you're being polite knowing that it is 200mm distance required or not :-) I'll dig out my copy of the regs later and post back to clarify.
I think the two FT+e cables is a normal layout if there's more than one light in the circuit and the particular light we're looking at isn't the last one. I'm assuming the third thinner cable is the wiring going to the ceramic lamp holder and it's probably glassfibre sleeved and the wiring possibly teflon insulated.
PS A roll of fibreglass tape is around R100.00, taping the terminations closed on several fittings won't be a cheap option.
_______________________________________________
_______________________________________________
it just looks like 2 twin+e connecting into the box and the other wire is the feed to the lamp holder...which should be heat resistant wire.