Solar system and Eskom supply, (a Neutral Question)

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • Tinman
    Junior Member
    • Jun 2012
    • 11

    #1

    Solar system and Eskom supply, (a Neutral Question)

    I am busy installing a Solar system(battries/inverter) which will supply just my lights and my plugs will still be good old Eskom.
    The problem I face is the neutral, should the neutral on the solar system be on its own or can the neutral be the same neutral bar as Supply N/bar. My gut feel is should be a separate and switched when reverting back to Eskom power.
    Can anyone can shed some light on this grey area I have.
  • Dave A
    Site Caretaker

    • May 2006
    • 22812

    #2
    I'd suggest read this thread on connecting generators to an existing installation. The principles should be the same.

    Essentially, the installation under alternative power should be seperated from the installation under mains power (which means a seperate neutral bar).
    Participation is voluntary.

    Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services

    Comment

    • Tinman
      Junior Member
      • Jun 2012
      • 11

      #3
      Thanks for confirming my gut feel. I did read your posting on generators. I have
      sent my control circuit for review and was told that one contactor can not
      do the switching as the arc between N/O and N/C, will trip the board.

      Back to the drawing Board.

      Comment

      • AndyD
        Diamond Member

        • Jan 2010
        • 4927

        #4
        Yep you should switch the live and neutral so the Eskom supply and your inverter output never meet.

        I've installed a few solar /inverter systems for lighting and it's often easier to add a small enclosure with an extra MCB or two next to your changeover switch.


        Click image for larger version

Name:	Drawing1.jpg
Views:	1
Size:	76.4 KB
ID:	261545
        _______________________________________________

        _______________________________________________

        Comment

        • Tinman
          Junior Member
          • Jun 2012
          • 11

          #5
          AndyD - That's what I wanted to achieve with the use of a contactor 2 x NO and 2 x NC but was advised that the arc would
          cause a major problem and that the reviewer had personal experience with such a circuit. I want to automate/remote the switching
          from Eskom to green and back to Eskom. I want to move my lights off Eskom by end of July. I am also buildind a vertical wind gen.
          So far the test have been encouraging.

          Comment

          • AndyD
            Diamond Member

            • Jan 2010
            • 4927

            #6
            I would use two contactors rather than a single one and add a small delay like 0.5 secs or even a mechanical interlock that physically prevents one of the contactors operating whilst the other is still energised. I agree a single contactor with 4-poles might be a problem with arcing plus a contactor with that 2 x NO and 2 x NC arrangement isn't a common item so it would probably be costly.

            A mechanical interlock with aux contacts is shown on this page.
            _______________________________________________

            _______________________________________________

            Comment

            • Tinman
              Junior Member
              • Jun 2012
              • 11

              #7
              Thanks, that what I'll have to do is user a delay between switching. The problem I want to overcome is that when the inverter
              switches off due to low battery voltage, Eskom must automatically be restored. I'll have a look at the page you sent me and
              do some "kop krap" and re-work my switching.

              Comment

              • AndyD
                Diamond Member

                • Jan 2010
                • 4927

                #8
                What you basically need is a standard automatic transfer switch. The difference is normally it would switch in an alternative power source if the Eskom supply failed, you need to configure it to work the opposite way around and give priority to the alternative source and use Eskom as a back-up so to speak.

                There are inverter units with all the controls built in such as these.
                _______________________________________________

                _______________________________________________

                Comment

                • Justloadit
                  Diamond Member
                  • Nov 2010
                  • 3517

                  #9
                  If you have computers connected to this line, then I suggest you get a mini UPS on each computer, so that during the switching period, the UPS ensures your PCs are running of stable supplies.
                  On some occasions during the switch over, depending if you have inductive loads or not, and CFLs are considered as an inductive load, and where the supply peaks are on ESKOM and your alternative supply are on opposite ends, The change over could create a surge in the load line which may hang up your PC and you may lose any unsaved information.
                  Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
                  Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

                  Comment

                  • Tinman
                    Junior Member
                    • Jun 2012
                    • 11

                    #10
                    AndyD – thanks again, I’m going to use the changeover switch to start off with and the
                    then setup semi auto, switching system. This project has taken a year to get this far.

                    Justloadit, thanks for the advice, but my green power will be powering my light only.
                    Last edited by Tinman; 19-Jun-12, 08:06 PM.

                    Comment

                    • kahoel117
                      Full Member

                      • Aug 2011
                      • 61

                      #11
                      Hi Tinman
                      i am interrested in your green power setup, that you are building for your lighting.
                      i want to do a similar solar setup for our lighting , although its not an replacement for our current lighting.
                      just basically an experiment for now to see how it works in the seasons and the type of lights i can use (cfl or led).
                      currently our lighting is 20 x 11w cfl and 3 x 150w floodlights(PIR).
                      thanks
                      kahoel

                      Comment

                      • Tinman
                        Junior Member
                        • Jun 2012
                        • 11

                        #12
                        Hi kahoel
                        Delay is that I have been away and also had loggin issues. I am moving my light off the grid, wanted to have automatic switching
                        but that will have to wait while I find my way around that obstical.
                        I am still sorting out the PV. I know what I need its just the price and supplier. I need to go and see the quality of PV.
                        Some selling at R10.00 Watt and Others at R13.00 Watt, so its down to quality, somthing lacking in SA today.
                        regards
                        Tinman

                        Comment

                        • SilverNodashi
                          Platinum Member

                          • May 2007
                          • 1197

                          #13
                          Originally posted by Tinman
                          Hi kahoel
                          Delay is that I have been away and also had loggin issues. I am moving my light off the grid, wanted to have automatic switching
                          but that will have to wait while I find my way around that obstical.
                          I am still sorting out the PV. I know what I need its just the price and supplier. I need to go and see the quality of PV.
                          Some selling at R10.00 Watt and Others at R13.00 Watt, so its down to quality, somthing lacking in SA today.
                          regards
                          Tinman
                          Be careful! If you pay peanuts, you get monkeys! Especially in the PV industry, don't buy the cheapest stuff. It will soon be a very expensive lesson to learn.