Problem with outside lights

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • SparkyScott
    Full Member
    • Feb 2011
    • 46

    #1

    Problem with outside lights

    Hey guys I was just wondering if you could help me out please,I installed 2 outside lights eurolux FS96 floodlights about 2 months ago and been working fine.Yesterday the power was off most of the day,when they were suppose to come on the lamps started flickering and only 1 came on,tonight there doing the same one flickers and the other one doesn't do a thing.I checked the voltage and it was 183v at the light fitting then I checked the power at the mains and it was 189V,the sockets were 180v.do you think the power could be affecting the lights?

    Scott
  • bergie
    Email problem

    • Sep 2010
    • 308

    #2
    190 volts is very low. better get eskom in there quick before your appliances fry.

    Comment

    • AndyD
      Diamond Member

      • Jan 2010
      • 4946

      #3
      Wow, 180v at the sockets! I'm surprised anything electronic is working in that house. I would test the lights on a 220v supply before going any further. Why is the voltage so low? Is the neutral voltage elevated? I would run the usual barrage of tests at the incoming supply and see if the problem is in the house or Eskom.
      _______________________________________________

      _______________________________________________

      Comment

      • SparkyScott
        Full Member
        • Feb 2011
        • 46

        #4
        Morning guys,I checked the sockets this morning and the voltage was 197 and the same at the mains.I never done any other tests but I will do when I get home and I will let you guys know.

        Comment

        • Justloadit
          Diamond Member

          • Nov 2010
          • 3518

          #5
          Just a question -
          Is the battery in your meter good?
          is your meter reading correctly?
          How did you test your meter?
          Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
          Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

          Comment

          • Dave A
            Site Caretaker

            • May 2006
            • 22810

            #6
            Power out for most of the day.
            Voltage problems there after.
            Coincidence? Probably not.
            Participation is voluntary.

            Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services

            Comment

            • SparkyScott
              Full Member
              • Feb 2011
              • 46

              #7
              The municipality came out this morning and they said the clips on the mains cable in the street weren't on correctly and it was a new cable that was installed a few weeks back.there is now 210v at the mains and the outside lights are working.
              The tester is brand new and so are the batteries

              Scott

              Comment

              • AndyD
                Diamond Member

                • Jan 2010
                • 4946

                #8
                Well 210volts is still a little on the low side but a step in the right direction from being in the 180's range. Might be worth putting the installation under a decent load and rechecking the DB supply voltage and neutral-earth voltage etc. Glad to hear it's all working again anyway.
                _______________________________________________

                _______________________________________________

                Comment

                • bergie
                  Email problem

                  • Sep 2010
                  • 308

                  #9
                  at least its not 380 volts. i have seen a few times where city council gets mixed up and then they have to kak en betaal

                  Comment

                  • MGM
                    Full Member

                    • Apr 2012
                    • 55

                    #10
                    Well, if you train your artisans over a period of 18 months, module based, this is what happens. Problems.

                    Comment

                    • shani
                      Full Member

                      • Sep 2011
                      • 65

                      #11
                      Originally posted by SparkyScott
                      The municipality came out this morning and they said the clips on the mains cable in the street weren't on correctly and it was a new cable that was installed a few weeks back.there is now 210v at the mains and the outside lights are working.
                      The tester is brand new and so are the batteries

                      Scott
                      Glad to hear that.