    Insulation resistance test

    Reading through amendment 8, i noticed that you no longer have to carry out an insulation resistance test on an exsisiting installation.
    Comments are based on opinion...not always facts....that's why people use an alias.
  • Leecatt
    Silver Member

    • Jul 2008
    • 404

    #2
    Originally posted by ians
    Reading through amendment 8, i noticed that you no longer have to carry out an insulation resistance test on an exsisiting installation.
    How do you arrive at this conclusion when page 286 question 8 clearly requests the results of the insulation test.
    is there something else i am missing?
    To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

    Comment

    • ians
      Diamond Member

      • Apr 2010
      • 3943

      #3
      also on page 279

      8.7.8.2 The insulation resistance, measured as follows, shall be at least
      1,0 MΩ:
      a) to measure the insulation resistance to earth, apply the test voltage
      between the earth continuity conductor and the whole system of live
      conductors, or any section of it; and
      b) to measure the insulation resistance between the conductors, apply
      the test voltage
      1) between the phase conductors, and, when relevant,
      2) between the phase conductors and the neutral conductor.
      8.7.8.3 When there are sub-distribution boards and the total insulation
      resistance is less than 1,0 MΩ, the insulation-resistance test may be
      carried out by
      a) isolating and testing the wiring between the main supply and the subdistribution
      boards, and
      b) testing, as a separate section, each sub-distribution board connected
      to all the circuits that it feeds, but the insulation resistance in each
      section shall be at least 1,0 MΩ.


      Now you see thats what i also thought until i read the new amendment no.8 carefully.

      you will find this note...

      8.7.8 Insulation resistance
      NOTE 1 Before power is connected to any new or altered circuit, the test for
      insulation resistance should be carried out to ensure there is no short-circuit or
      high impedance faults in the installation, and that it is safe to energize. Amdt 8

      NOTE 2 In the case of existing installations where the power may not be switched
      off from certain circuits in order to carry out this test, the fact that the circuits are
      subject to the supply voltage can be regarded as evident that the insulation
      resistance is compliant. Amdt
      Comments are based on opinion...not always facts....that's why people use an alias.

      Comment

      • Dave A
        Site Caretaker

        • May 2006
        • 22810

        #4
        Originally posted by ians
        NOTE 2 In the case of existing installations where the power may not be switched
        off from certain circuits in order to carry out this test, the fact that the circuits are
        subject to the supply voltage can be regarded as evident that the insulation
        resistance is compliant. Amdt
        I suggest that only precludes installations where the power may not be switched off under any circumstances - a pretty rare occurence I should think.
        Participation is voluntary.

        Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services

        Comment

        • ians
          Diamond Member

          • Apr 2010
          • 3943

          #5
          " the fact that the circuits are subject to the supply voltage can be regarded as evident that the insulation
          resistance is compliant."
          Comments are based on opinion...not always facts....that's why people use an alias.

          Comment

          • Leecatt
            Silver Member

            • Jul 2008
            • 404

            #6
            Originally posted by ians
            also on page 279

            8.7.8.2 The insulation resistance, measured as follows, shall be at least
            1,0 MΩ:
            a) to measure the insulation resistance to earth, apply the test voltage
            between the earth continuity conductor and the whole system of live
            conductors, or any section of it; and
            b) to measure the insulation resistance between the conductors, apply
            the test voltage
            1) between the phase conductors, and, when relevant,
            2) between the phase conductors and the neutral conductor.
            8.7.8.3 When there are sub-distribution boards and the total insulation
            resistance is less than 1,0 MΩ, the insulation-resistance test may be
            carried out by
            a) isolating and testing the wiring between the main supply and the subdistribution
            boards, and
            b) testing, as a separate section, each sub-distribution board connected
            to all the circuits that it feeds, but the insulation resistance in each
            section shall be at least 1,0 MΩ.


            Now you see thats what i also thought until i read the new amendment no.8 carefully.

            you will find this note...

            8.7.8 Insulation resistance
            NOTE 1 Before power is connected to any new or altered circuit, the test for
            insulation resistance should be carried out to ensure there is no short-circuit or
            high impedance faults in the installation, and that it is safe to energize. Amdt 8

            NOTE 2 In the case of existing installations where the power may not be switched
            off from certain circuits in order to carry out this test, the fact that the circuits are
            subject to the supply voltage can be regarded as evident that the insulation
            resistance is compliant. Amdt
            This is very interesting and has gone straight over my head and I am tempted to agree with Dave, only in the case where power may not be switched off
            To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

            Comment

            • ians
              Diamond Member

              • Apr 2010
              • 3943

              #7
              It depends on what you are testing, if you are only doing domestic inspections, then there should be no reason why you cannot switch off. However, if you do factories and commercial inspections this could prove to be a bit tricky. I was involved with an inspection at a sugar mill, switching off the plant to do insulation resistance tests could have been tricky.
              Comments are based on opinion...not always facts....that's why people use an alias.

              Comment

              • Dave A
                Site Caretaker

                • May 2006
                • 22810

                #8
                I suggest the reason why the power can't be switched off would have to be very well motivated. I certainly can't see us rolling over on this without a fight - and supporting documentation.

                Wouldn't you be nervous issuing a CoC without an insulation test?