Earth leakage trip 7 min past the hour every hour. How do I locate the problem? This started after I replaced the old Earth leakage. Driving me mad. The problem is on one of about 7 circuit breakers or combination of them. This tends to happen only at night, but does happen here and there during day hours.
Earth leakage trip 7 min past the hour every hour
Collapse
X
-
Maybe disable the timer switch....
Meant as a joke, but it seems there may be sense in the madness?
BOVER Technologies - computer sales and TeamViewer support
Elmine Botha Freelance Photographer - Photographer/ Videographer -
I had this problem about a year ago. In the end, I have put the old earth leakage unit back. I forgot about it and replaced it now again. So this condition is around for a long time now. Only timer around, is the one at the pool pump.
Why would it be hourly at night and only once or twice during the day?~Expenses will eat you alive! - My first Boss~Comment
-
The geysers have no effect on the tripping of the ELCB. Neither the lights. Just the plugs. It seems to be random, or building up something, that makes it trip in exactly 60 min at night! Exactly 7 min past the hour!~Expenses will eat you alive! - My first Boss~Comment
-
Alternatively, get another ELB, and connect one circuit through it every couple of days, until you find the one that trips the ELB. It is a bit of work, as you need to find the neutral as well of the circuit you pushing through the ELB. This way you will find it, with out the inconvenience of not having power on all the circuits at the most inoprtune times, like when you are away for the week end/holiday.Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.zaComment
-
This is what I am doing. What makes it difficult, I cannot do it during the day, as I can leave all the ELB's on during the day and nothing will trip. I left everything on today again, the whole day and had my first trip at 18h07.
I have figured out, it is at night, with 6 breakers switched off, that I do not get trip's. However, if I go on any combination, smaller than these 6, I get trips.
Yes, it is a CBI. But it is the second brand new one. The first was a 63amp 3ka, the second new one is 63amp 6ka.
I am still testing....~Expenses will eat you alive! - My first Boss~Comment
-
OK, the six off produced no trip at 19h07. I am now leaving them like that to confirm 'no trip' at 20h07.
The bottom row of CB's is 13 is total.
0111100001110
How do I check if they have something in common, that will cause a trip, even if it is not the guilty CB? I suspect that if I switch any of those 0's to 1, I will get a trip! Only at night though!~Expenses will eat you alive! - My first Boss~Comment
-
What has altered recently? Any electrical additions or new appliances or even Christmas lights?
Do you have access to a Mega tester and an RCD ramp tester? If not it's going to be difficult to find the fault(s) unless it's something obvious. The problem is that global earth leakage is a cumulative fault so you might be looking for several smaller leakage faults and it may be that none of them on their own are large enough to cause the RCD (earth leakage breaker) to trip.
*Edit*
0111100001110 is actually a binary message and translates as 'you'll never find me without a Mega tester'.
_______________________________________________
_______________________________________________Comment
-
hehe, good one!
No, I have the normal hosehold multi-meters, AMP meter, ELCB polarity tester.
Our electritian should be back from holiday tomorrow. He should be able to borrough me what I need. How does Mega and RCD ramp tester work?
Might have surge protection scattered around. Why?~Expenses will eat you alive! - My first Boss~Comment
-
AndyD there is your binary quote!01111001011011110111010100100111011011000110110000 10000001101110011001010111011001100101011100100010 00000110011001101001011011100110010000100000011011 01011001010010000001110111011010010111010001101000 01101111011101010111010000100000011000010010000001 00110101100101011001110110000100100000011101000110 010101110011011101000110010101110010~Expenses will eat you alive! - My first Boss~Comment



Comment