    surfix in hazardous areas

    i have always used surfix for lighting in zoned areas. theres very little chance of damage high up. the inspection authority in kuilsriver accept it. however today another master sparky says its illegal as in hazardous areas the earth wire must be the same size as the live conductors.
    any clarification? andy?
  • AndyD
    Diamond Member

    • Jan 2010
    • 4946

    #2
    Can you calrify what the zoned areas are ie what Division/Zone? I'm guessing you're meaning Ex?
    _______________________________________________

    _______________________________________________

    Comment

    • AndyD
      Diamond Member

      • Jan 2010
      • 4946

      #3
      From SANS60079
      15.3 Apparatus not requiring earthing
      Where there is no requirement for earthing or bonding, for example, in some types of
      electrical apparatus having double or reinforced insulation, or for which supplementary
      earthing is not necessary, an internal or external earthing or bonding facility need not be
      provided.
      NOTE Double insulated apparatus, while not presenting a risk of electrical shock, may need to be earthed or
      bonded to reduce the risk of ignition.
      15.4 Size of conductor connection
      Earthing or equipotential bonding connection facilities shall allow for the effective connection
      of at least one conductor with a cross-sectional area given in Table 5.

      [ATTACH=CONFIG]3296[/ATTACH]

      In addition, earthing or bonding connection facilities on the outside of electrical apparatus
      shall provide effective connection of a conductor with a cross-sectional area of at least
      4 mm2.
      So if the CSA of your live is <16mmsq then the earth must be the same size. This would rule out all domestic installation cables as the earth is invariably one or two CSA sizes smaller than the live and neutral.
      Attached Files
      _______________________________________________

      _______________________________________________

      Comment

      • bergie
        Email problem

        • Sep 2010
        • 308

        #4
        ex zones yes .
        mmmm, i also see in sans 10086 ,something about "if the required earth conductor size cannot be achieved,the main circuit must be on an earth fault protection system."
        the lights i am doing are on 300 ma earth leakage. all metal equipment are bonded with a 10mm external earth. the lights are plastic of course.

        Comment