Hi All
Need some help please.
I have a large customer that has had most of his earthing stolen.
The building has various 11kv substations that feed LV rooms that feed sub DB’s that feed consumer DB’s
The layout out does not allow for complete new copper earthing and neither does the budget. We have installed various earth bonding straps and used all the armouring strands that we can get our hands on. We have managed to get the Ze of the sub DBs down to 0.11 Ohms. (Main breaker off and new earth strap disconnected)
Now if we follow SANS
I have a Main breaker of 1250Amps
So calculate Ze = 240V/2(1250) = 0.096 Ohms.
I have tried many things including new copper earthing and I can NOT get it below the 0.1 Ohm mark.
Many thanks
Neal
Need some help please.
I have a large customer that has had most of his earthing stolen.
The building has various 11kv substations that feed LV rooms that feed sub DB’s that feed consumer DB’s
The layout out does not allow for complete new copper earthing and neither does the budget. We have installed various earth bonding straps and used all the armouring strands that we can get our hands on. We have managed to get the Ze of the sub DBs down to 0.11 Ohms. (Main breaker off and new earth strap disconnected)
Now if we follow SANS
I have a Main breaker of 1250Amps
So calculate Ze = 240V/2(1250) = 0.096 Ohms.
I have tried many things including new copper earthing and I can NOT get it below the 0.1 Ohm mark.
Many thanks
Neal
Comment