If there is an isolating transformer, COC apply?

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • Justloadit
    Diamond Member

    • Nov 2010
    • 3518

    #1

    If there is an isolating transformer, COC apply?

    A question to my learned friends.

    We wish to place some lights on a very long fence, the connection between lights is made using silicon cabtyre wire, to handle the elements. The lights are connected to the secondary of an isolating transformer, and the isolating transformer is connected to the DB box, does the light circuit require to have a COC?

    Under the same scenario as above, the isolating transformer is swopped out to a low voltage AC transformer, what are the requirements for the secondary light circuit?
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za
  • AndyD
    Diamond Member

    • Jan 2010
    • 4946

    #2
    Unless the system is on a plug and socket I'd say it would require a certificate.
    Why are you using an isolating transformer? Are the lights installed in a zone that requires it?
    I'd also look at other options rather than silicon cabtyre. There's hybrid PVC cables that are UV stable such as 'mastlight', these will be cheaper.
    _______________________________________________

    _______________________________________________

    Comment

    • Justloadit
      Diamond Member

      • Nov 2010
      • 3518

      #3
      Its on a high fenced sports field, apprximately 250 meters long. Being a very very old school, the complete electrical system would then have to be evaluated and possibly upgraded to get the COC. All that we would be contracted to do is the lighting the sports field. If we have to contract out the COC process, the upgrade of the current system would force the school to abandon the project due to the financial implication, and we will lose a very lucrative order.

      So I am looking for acceptable safe ways to do the lighting circuit. Our original idea was to use 12V LED flood lights. Some clever wiring must be done, as the total current from the transformer on the 12V side will be 183Amps. By spliting the cables to the respective lights, they could switch banks of lights from a control panel depending on what they were doing that specific night.
      Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
      Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

      Comment

      • AndyD
        Diamond Member

        • Jan 2010
        • 4946

        #4
        With lighting systems of this size you need to steer clear of ELV distribution. When you're talking about a total load of nearly 200Amps the cable sizes become immense and that's just the start of it. The size of any switchgear (contactors, isolators, relays etc) also becomes very large, the transformer to produce a secondary current of 200A will also be enormous, the distances involved of 250 meters also mean you're going to have to upsize cabling to reduce volt drop, the cost will be astronomical. My advice is to keep as much of the distribution network as possible in 230 or even 380v. If the fittings are 12 volt then install a transformer or driver in each fitting.

        With this kind of installation I don't see how you're going to get away without issuing a COC, I think you'll be taking a large risk if you don't.
        _______________________________________________

        _______________________________________________

        Comment

        • Justloadit
          Diamond Member

          • Nov 2010
          • 3518

          #5
          The total consumption is just over 2Kwatts when all the lights are on, but at 12V it is 183 Amps, or lets say 24v will be 90 odd amps. Each light only draws 50 watts or 4.2amps at 12v but will draw 2.1Amps at 24V. The LEDs use switch mode supplies which ensure that only 50watts of power are consumed, irrespective of the supply voltage, so if I go for 24V, there can be a 12V drop in the cable with out affecting the LED output performance. If I bundle 9 cables so that each cable carries 10 amps, then there is no real issue with the cable required. The silicon cable can carry a far higher current than normal cable, due to the higher temperature rating of the silicon insulation with out degradation, plus it is UV resistant and weather resistant.
          Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
          Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

          Comment

          • Dave A
            Site Caretaker

            • May 2006
            • 22810

            #6
            Originally posted by Justloadit
            Being a very very old school, the complete electrical system would then have to be evaluated and possibly upgraded to get the COC. All that we would be contracted to do is the lighting the sports field. If we have to contract out the COC process, the upgrade of the current system would force the school to abandon the project due to the financial implication, and we will lose a very lucrative order.
            I suggest the professional thing to do is point out this inconvenient fact of life anyway.

            Who knows, maybe they have already got a COC on the rest of the installation. And if they haven't:
            • They can't even add a plug or light point without going through the rigmarole
            • The user or lessor is responsible for ensuring a COC is available when legally required to have one
            • A school should be very concerned about safety issues anyway (especially old ones).



            What are the odds that they've added to the installation since 1994 already? There's every chance they're already on the hook and might not even know it.

            Watch CYA kick in and be the hero that saved the day.
            Participation is voluntary.

            Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services

            Comment

            • Justloadit
              Diamond Member

              • Nov 2010
              • 3518

              #7
              Hi Dave I hear you.
              An interesting question, you have R150K. Do you spend it to get a COC on the school electrical system, or do you help underpreviliged kids to have a place train soccer, rugby , tennis and cricket in the evenings under lights, who will not be there if there is noone. The reason for this project is to give the kids something to aspire too.
              Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
              Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

              Comment

              • AndyD
                Diamond Member

                • Jan 2010
                • 4946

                #8
                Forget 12v distribution and even forget 24v distribution; do the design, work out the cable sizes and lengths then find a comfy chair, take a deep breath and work out the price. Then when you've recovered sufficiently phone for a price for a transformer that can acommodate 183A at 12v or 90+ Amps at 24v PLUS INRUSH CURRENT, PLUS POOR POWER FACTOR (add approx 30% to the expected running load depending on efficiency of PSU's).

                Originally posted by Justloadit
                The total consumption is just over 2Kwatts when all the lights are on, but at 12V it is 183 Amps, or lets say 24v will be 90 odd amps.
                You can't take the lamp wattage and work backward to size your supply, it doesn't work that way when there's a transformer or constant current driver (SMPS) involved. Use the stated current on the driver/transformer because this will allow for PF and efficiency losses. See SANS 0142 for correction factors according to presence of 3rd harmonic. With switch mode supplies you should accomodate all harmonics in the triplen range.

                Originally posted by Justloadit
                Each light only draws 50 watts or 4.2amps at 12v but will draw 2.1Amps at 24V. The LEDs use switch mode supplies which ensure that only 50watts of power are consumed, irrespective of the supply voltage, so if I go for 24V, there can be a 12V drop in the cable with out affecting the LED output performance.
                This is not legal, not safe and not compliant. The short answer is refer to the tables in SANS0142 and the clauses stating the volt drop across the cable will be maximun 5%. Don't forget the wire length of the supply wiring is effectively double the distance between the supply point and the load, this is because the live wire and the neutral wire have resistance (ZL AND ZN).

                Originally posted by Justloadit
                If I bundle 9 cables so that each cable carries 10 amps, then there is no real issue with the cable required. The silicon cable can carry a far higher current than normal cable, due to the higher temperature rating of the silicon insulation with out degradation, plus it is UV resistant and weather resistant.
                Yes silicon cable can carry a higher current, refer to the tables again in 0142. Problem with silicon (apart from expense) is it's lack of durability, I would never use silicon cable for general installation especially if it's accessible by hand or open to the kind of impact it might receive on a sports field fence. Running cables in general on fences in public or semi-public areas isa bad idea because of the theft issue.

                As for the COC, I would say you don't have a choice.
                _______________________________________________

                _______________________________________________

                Comment

                • Justloadit
                  Diamond Member

                  • Nov 2010
                  • 3518

                  #9
                  Originally posted by AndyD
                  Forget 12v distribution and even forget 24v distribution; do the design, work out the cable sizes and lengths then find a comfy chair, take a deep breath and work out the price. Then when you've recovered sufficiently phone for a price for a transformer that can acommodate 183A at 12v or 90+ Amps at 24v PLUS INRUSH CURRENT, PLUS POOR POWER FACTOR (add approx 30% to the expected running load depending on efficiency of PSU's).
                  There is a lot of merit in 12v and 24V systems. Battery backup is one advantage. The other advantage is the safety issue against shock or faults is negligible, a simple fuse will suffice for protection. Humidity does not influence the supply voltage.
                  The transformer cost is about R4000.00. Whilst 183 amps sounds fantastically large, it is really not a n issue. The starter in your car draws a 1000 amps when initially cranked and then drops down to a couple of hundred amps when turning. A slow rise in voltage is not an issue for the LED supplies as the internal electronics has a built in low voltage detector which waits for the supply to be above 12V.


                  Originally posted by AndyD
                  You can't take the lamp wattage and work backward to size your supply, it doesn't work that way when there's a transformer or constant current driver (SMPS) involved. Use the stated current on the driver/transformer because this will allow for PF and efficiency losses. See SANS 0142 for correction factors according to presence of 3rd harmonic. With switch mode supplies you should accomodate all harmonics in the triplen range.
                  The lamps are 12V DC with an internal DC constant current SMPS, running at over 100Khz, the power factor is not even measureable because the SMPS act both as buck and boost supply, ensuring a constant current draw from the supply irrespectivce of where the sine wave is. It does not behave as in the old days with an inductive dimmer. The power factor is negligible because the total amount of power draw from the mains system is 2Kw. Far less than a unloaded squirel cage motor. Adding a few micro farads of power factor capacitor on the primary side of the transformer would correct that at minimal cost of a couple of hundered Rands.


                  Originally posted by AndyD
                  This is not legal, not safe and not compliant. The short answer is refer to the tables in SANS0142 and the clauses stating the volt drop across the cable will be maximun 5%. Don't forget the wire length of the supply wiring is effectively double the distance between the supply point and the load, this is because the live wire and the neutral wire have resistance (ZL AND ZN).
                  I would agree if the system is on a 220V system connected to the grid, it will then fall under the SANS0142, but if the system does not require a COC because it is low voltage then one practically ignore the SANS0142.

                  Originally posted by AndyD
                  Yes silicon cable can carry a higher current, refer to the tables again in 0142. Problem with silicon (apart from expense) is it's lack of durability, I would never use silicon cable for general installation especially if it's accessible by hand or open to the kind of impact it might receive on a sports field fence. Running cables in general on fences in public or semi-public areas isa bad idea because of the theft issue.
                  Point noted, but the fence is approximately 6 meters high.

                  Originally posted by AndyD
                  As for the COC, I would say you don't have a choice.
                  The situation that has a arisen is that there is limited donor money available to install the lights for the benefits of underprivilidged kids, who do not attend the particular school, but have been offered the use of the fields and sports facilities. If the money is to be routed to do the COC, and no lights installed or inadaquatly installed lights, there will be no more future donour money to help the underprivilidged kids, as the money will have been deeemed to have been used for othere uses than what it was intended for. A no win situation for all. We are simply trying to find a solution that will accomodate everyone.
                  Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
                  Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

                  Comment

                  • bergie
                    Email problem

                    • Sep 2010
                    • 308

                    #10
                    +1 for andy. listen to his advice. long 12 volt runs are bad news .

                    Comment

                    • AndyD
                      Diamond Member

                      • Jan 2010
                      • 4946

                      #11
                      Originally posted by Justloadit
                      There is a lot of merit in 12v and 24V systems. Battery backup is one advantage. The other advantage is the safety issue against shock or faults is negligible, a simple fuse will suffice for protection.
                      The safety issues for ELV systems are as critical if not more so than 230v systems. ELV systems are highly prone to fires because of the high currents involved. Most of the vehicals on the road that catch fire are due to 12vdc faults. It's a common misconception that with ELV it's much safer but in the days when 12v halogen lighting was becoming fashionable there were many fires caused by these systems which lead to several changes to the installation codes.
                      Originally posted by Justloadit
                      The transformer cost is about R4000.00. Whilst 183 amps sounds fantastically large, it is really not a n issue. The starter in your car draws a 1000 amps when initially cranked and then drops down to a couple of hundred amps when turning.
                      True but look at the size of the wires that supply a starter motor on a car. This is going to be the size of wiring you'll need around your transformer and the reason you'll need 10 or more circuits of 2.5mmsq cable to carry the power to the lights whereas if it's 220v distribution a single cable would suffice.


                      Originally posted by Justloadit
                      The lamps are 12V DC with an internal DC constant current SMPS, running at over 100Khz, the power factor is not even measureable because the SMPS act both as buck and boost supply, ensuring a constant current draw from the supply irrespectivce of where the sine wave is. It does not behave as in the old days with an inductive dimmer. The power factor is negligible because the total amount of power draw from the mains system is 2Kw. Far less than a unloaded squirel cage motor. Adding a few micro farads of power factor capacitor on the primary side of the transformer would correct that at minimal cost of a couple of hundered Rands.
                      SMPS's in their basic form have notoriously poor PF. Depending on the individual item and the mode of its operation it may have internal correction installed so whilst PF is always a consideration it may not be an issue.
                      Last edited by AndyD; 05-Aug-13, 07:13 PM. Reason: corrected typo's
                      _______________________________________________

                      _______________________________________________

                      Comment

                      • Justloadit
                        Diamond Member

                        • Nov 2010
                        • 3518

                        #12
                        PF's are only issue on large currents, a single circuit drawing 5 amps and over at the 230/400V level, not when you are pulling 220mA from the mains. A simple 1uF 400V capacitor on the DC side of the bridge rectifier eliminates the PF caused by the SMPS, which costs around R3.00. Typical high PFs in this case would be speed drives, and banks and banks of flourescent lighting, where power factors are in the magnitude of 0.82, attempting to compensate for this yields capacitors costing more than the drive itself.

                        This is where power electronics are comming into play where you boost the voltage during the rising and falling parts of the rectified sine wave, and you buck on the peaks, attempting to maintain a constant current draw from the supply. I have been succesfull with a prototype driving a 1.1Kwatt motor achieving PFs over 0.92 at full load, and unloaded, which is when the PF really is bad.The inductor required is hefty as it has to content with a constant DC current flow in the same direction into the load. If you have an understanding of electronics, here is a typical IC from MOTOROLA MC33262 which will do the task. If you open the data sheet, on page 12 they print a table of volatges in which the application design was tested, yielding efficiencies above 99% which is close to a power factor of 1.

                        I have succesfully replaced flourescent fittings with equivalent brighter LED retrofits, in which the power consumed has reduce by more than 65%, and simultaneously improving the power factor. There is much to be said about proper LED circuits, mind you not the cheap rubbish many stores are selling.

                        Your explanation of the halogen lamps is very true, the installers were using incorrectly sized wire for one, and bad joints for the other part due to incorrectly crimped cheap rubbish connectors, causing hot joints and burning of cables as you have suggested. The silicon cable does not burn for one, and if you place a suitably rated fuse on each of the cables as protection, any shorts that may occur will be protected by the fuse. There is also no requirement of an earth conductor for the detection of ground faults.

                        I understand where you are comming from with the high standards required in the 230/400V arena, but on the LV side, simple common sense is more than sufficient to ensure that the sytem works.
                        Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
                        Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

                        Comment

                        • AndyD
                          Diamond Member

                          • Jan 2010
                          • 4946

                          #13
                          I agree PF may or may not be an issue depending on the driver design but like I say it's always a consideration that needs quantifying when designing the supply network even if it's found that no improvement or derating of cable sizes is necessary.

                          The cause of fires with ELV is often undersized cabling or inadequate connections. Silicon insulation doesn't support combustion admittedly but it's the terminations and connections come under far more strain because of the high currents involved and many connections that do give problems at 12 volts wouldn't give problems with the same power at 230v. The terminations tend to overheat and arc causing combustion at or around the lug, connector block or whatever the connection is and fuses aren't protection against this as an arcing connection will actually increase the circuit resistance so reduce the current flow.

                          More for the benefit of others reading I'd say it's a common trap thinking that ELV, in this case 12 or 24V distribution is safer. In some respects maybe but in other respects definately not, they may be safer with regard to the user receiving a fatal shock but they're far more of a fire hazard. I would also expect the overall cost of an ELV system to be several times higher than the cost of the same system design in 230v.

                          Rereading the thread from the start I realise we're arguing the same technicalities from two completely different viewpoints. I'm basing my recommendations primarily on standard system design considerations and you appear to be basing yours primarily on avoiding the necessity of issuing a compliance certificate. As such we're always going to be short on common ground or agreement.

                          As for the COC problem, to this end I would suggest you investigate going with a 230v distributed system using 3 OR 4 circuits of floodlights with staggered switching to lessen inrush current on startup. From the figures you've given (circa 9Amps @ 230v) you could run the entire system on a 2.5mm trailing lead (or even 2 x 2.5mm leads) plugged into a standard EXISTING wall socket. Even if you upsize the long distribution cables to reduce voltdrop this will still be a fraction of the cost of your 9 or ten ELV circuits in silicon and an additional transformer. Maybe also investigate using black surfix which is UV stable and can be clipped direct to the top of the fence.

                          I assume your prospective installation is in the JHB area. If on the off chance it's in Cape Town you can give me a shout and I'll do a survey and your design for gratis if you're also working on a not-for-profit basis and it's for a good cause.
                          _______________________________________________

                          _______________________________________________

                          Comment

                          • Justloadit
                            Diamond Member

                            • Nov 2010
                            • 3518

                            #14
                            AndyD, I thank you for your invaluable information that you have provided in your posts.
                            The installation if it materializes will be in the Johannesburg area.
                            Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
                            Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

                            Comment

                            • skatingsparks
                              Silver Member

                              • Mar 2008
                              • 375

                              #15
                              If its Joburg, you're working on a not-for-profit basis, it's for a good cause and if you need help - private message me. All for the pay it forward thing.