I must still disagree here, installing an earth wire from the DB because of a breakdown in continuity has not changed the installation. It has merely brought the existing circuitry up to standard with requirements. Neither the amount of circuits nor the amount of points have changed. The circuit has only been made safe. If there is an earth from the DB available and it is too short to connect you must extend it with a pigtail, without having to certify it.
Regarding the obligation to certify, well your point 3 states certification must be refused where a fault is detected and point 4 states that your work be certified.
When you are called out to change a socket outlet, you do not inspect the whole house to see if there are faults, you are shown to the faulty socket outlet and you work on that point. If you discover something like the earth is a problem you inform the client of what it could mean for the rest of the installation, but it remains his choice as to when and by whom it be attended. This is where you get the opportunity to sell your business and could end up with a nice commission if handled properly. Should the client be under financial constraints there is no reason why any corrective work cannot be done in stages as a gradual upgrade. You would still however be expected to repair the faulty socket outlet as requested.
Regarding the obligation to certify, well your point 3 states certification must be refused where a fault is detected and point 4 states that your work be certified.
When you are called out to change a socket outlet, you do not inspect the whole house to see if there are faults, you are shown to the faulty socket outlet and you work on that point. If you discover something like the earth is a problem you inform the client of what it could mean for the rest of the installation, but it remains his choice as to when and by whom it be attended. This is where you get the opportunity to sell your business and could end up with a nice commission if handled properly. Should the client be under financial constraints there is no reason why any corrective work cannot be done in stages as a gradual upgrade. You would still however be expected to repair the faulty socket outlet as requested.
Comment