House DB main switch

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • Leecatt
    Silver Member

    • Jul 2008
    • 404

    #16
    Originally posted by Slow Blow
    Does the main switch on a single phase DB have to be single pole, single pole and neutral or double pole, I ask this as there seem to be some confusion amongst a lot of local electrical CoC providers in Cape Town.
    The db must be protected by a double pole disconnecting device that disconnects both the live and neutral.
    If there is no integrated overload protection in the disconnecting device then a circuit breaker may be installed on the load side of the disconnecting device.
    See SANS 10142-1:2009 section 6.9
    To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

    Comment

    • AndyD
      Diamond Member

      • Jan 2010
      • 4946

      #17
      Originally posted by Leecatt
      ........What is that above the circuit breakers?
      Originally posted by ians
      This would confuse the local sparkies. I assume this is a pic of a DB used in the USA not in SA.......
      It was just a picture showing RCBO'S for the benefit of anyone uncertain what they are. t's not my handywork (my panels are far neater than that ) the DB shown is actually a UK 17th Edition compliant one, each socket and light circuit MCB has two wires because they generally use 32A ring circuits.

      RCBO

      Click image for larger version

Name:	111.jpg
Views:	1
Size:	4.7 KB
ID:	262803
      _______________________________________________

      _______________________________________________

      Comment

      • Dave A
        Site Caretaker

        • May 2006
        • 22810

        #18
        A residual-current circuit breaker with overload protection (RCBO) combines the functions of overcurrent protection and leakage detection.
        With thanks to Wikipedia.
        Participation is voluntary.

        Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services

        Comment

        • AndyD
          Diamond Member

          • Jan 2010
          • 4946

          #19
          Thanks Dave, forgot about wikipedia momentarily. Basically they're the size of an MCB, well at least the more recent versions are, the older ones are quite a bit taller than an MCB but same width. You fit one for each circuit being supplied from the DB and they provide earth leakage protection as well as overload protection to each individual circuit. The bonus is that an earth leakage fault just causes tripping of the guilty circuit and not the entire premises.
          _______________________________________________

          _______________________________________________

          Comment

          • Slow Blow
            Full Member

            • Feb 2014
            • 55

            #20
            I have learned something new now, I have been using RCD's for years and always thought that they were expensive ELCB's
            Apparently there is nothing that cannot happen today.

            Comment

            • Mark_Spark
              New Member
              • Jun 2016
              • 5

              #21
              Mind if i ask for a quote comparing CBs and these RCBOs?

              Comment

              • AndyD
                Diamond Member

                • Jan 2010
                • 4946

                #22
                Well the good news is that RCBO's have come down in price and also now come in a form factor that's the same as an MCB which means they're not as tall as they were and can now directly replace an MCB without rearranging the other surrounding items to get them in.

                The bad news is that I'm still importing mine as I need them from the UK because unbelievably the local wholesalers still aren't supplying them.

                I also found out you can't get AFDD's here either yet
                _______________________________________________

                _______________________________________________