Is it law that an E/L/Unit must be installed on a domestic (house) installation or can all circuits be individually protected.
Earth Leakage Unit Question
Collapse
X
-
You certainly don't have to have ELU protection for the entire installation, just the portions that are required to have ELU protection per SANS 10124-1
If the entire installation is on a single ELU, and you intend to only have a portion of the installation on ELU, just watch out the ELU is not also serving as the main switch.Participation is voluntary.
Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services -
You can individually protect circuits that require it using 30mA RCBO's. (if you can find a supplier). This won't really be an option if the main switch is an earth leakage unit because you won't be able to achieve discrimination._______________________________________________
_______________________________________________Comment
-
The section has been amended a number of times, including amendment 8 - so make sure your copy is totally up to date (Edition 1.8).
I see amendments from the original code arising in amendments 1, 3, 5, 6 & 8.
There are also other instances where ELU's are required or material to compliance, for example s6.16.1.4 and s6.16.3.2.3
Not to mention s6.15 - but that should be pretty obviousLast edited by Dave A; 18-Mar-14, 11:51 AM.Participation is voluntary.
Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene ServicesComment
-
All I know is that Earth Leakage is only on sockets, not on light circuits. But I have no idea why and would like to know.
Why would one not want a Earth Leakage?Houses4Rent
"We treat your investment as we treat our own"
marc@houses4rent.co.za www.houses4rent.co.za
083-3115551
Global Residential Property Investor / Specialized Letting Agent & Property ManagerComment
-
Hi Houses4Rent a lot of people, I would go so far as to say that the majority of people [I]electricians [I]included do not understand the purpose of a earth leakage unit and consider it unecessary and causes nuisance tripping. Unknown to them the tripping function is there as a protective device and by functioning properly is indicating that there is a fault on the circuits or part of the circuits that are being supplied by the E.L.U. So basically an E.L.U. is a essential safety device designed to protect life and property. Lighting circuits in some installations are not covered by E.L.U. as a safety precaution (make sense, you must have illumination)
Comment
-
Thanks mikilianis. I understood it to be a safety device. As an enginer i believe that everything must have a purpose and I need to understadn its purpose first before I believe anybody claiming that it has not purpose and can simply be ommited. But I am not so sure about the lighting. I rather have no light than not triggering the E/L when accidentally touching a live light circuit wire. Anyway, so far that did not happen to often. I am not a great competancy of electricity and stay away from things which are beyond basic connections.
Something else: I was quoted 5 hours labour (excl materials) to replace a main breaker and put a surge arrestor next to it. Am I right in saying that its a matter of making a few cable connections at the board which - lets be generous - should not take more than an hour maybe?Houses4Rent
"We treat your investment as we treat our own"
marc@houses4rent.co.za www.houses4rent.co.za
083-3115551
Global Residential Property Investor / Specialized Letting Agent & Property ManagerComment
-
Thanks mikilianis. I understood it to be a safety device. As an enginer i believe that everything must have a purpose and I need to understadn its purpose first before I believe anybody claiming that it has not purpose and can simply be ommited. But I am not so sure about the lighting. I rather have no light than not triggering the E/L when accidentally touching a live light circuit wire. Anyway, so far that did not happen to often. I am not a great competancy of electricity and stay away from things which are beyond basic connections.
Something else: I was quoted 5 hours labour (excl materials) to replace a main breaker and put a surge arrestor next to it. Am I right in saying that its a matter of making a few cable connections at the board which - lets be generous - should not take more than an hour maybe?
Also some guys can rip you off as well.Comment
-
I will get a second quote or simply watch them the 5 hours to see whether they ripped me off. Its worth the fun. I am giving them quite some work from my managed portfolio and I challanged them on a number of times and they could not justify their actions very well or eventually admitted their fault. On soem occassions of course I agreed to their reasoning. This might be a good test to decide to carry on with them or kick them out, but I thought I would be able to get a rough feasibity of 5h labour on this sparky infested thread :-) I actually asked them what is planed to fill 5 hours and I had no response... Maybe that alone says it all.
I also asked around to veryfy their material costs. I simple got a quote from an electrciacal wholesaler without having an account whith them. So anybody can get those prices and it was cheaper by factor 4-5 or so. That is too much of a markup for my liking.Houses4Rent
"We treat your investment as we treat our own"
marc@houses4rent.co.za www.houses4rent.co.za
083-3115551
Global Residential Property Investor / Specialized Letting Agent & Property ManagerComment
-
Thanks mikilianis. I understood it to be a safety device. As an enginer i believe that everything must have a purpose and I need to understadn its purpose first before I believe anybody claiming that it has not purpose and can simply be ommited. But I am not so sure about the lighting. I rather have no light than not triggering the E/L when accidentally touching a live light circuit wire. Anyway, so far that did not happen to often. I am not a great competancy of electricity and stay away from things which are beyond basic connections.
Something else: I was quoted 5 hours labour (excl materials) to replace a main breaker and put a surge arrestor next to it. Am I right in saying that its a matter of making a few cable connections at the board which - lets be generous - should not take more than an hour maybe?
Got a call out to a restaurant yesterday, 3 phase E/L/Unit not working (will not trip) I was quoted R1,700.00 by the wholesaler for a new one, the client decided he could live without one, you can't force people to install them, that is until one of the staff gets zapped, then there is k@k of note.Apparently there is nothing that cannot happen today.Comment
-
And did they not charge for eTolls
I know you in CT
That's what they are now doing in Jhb as part of their call out feeVictor - Knowledge is a blessing or a curse, your current circumstances make you decide!
Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.zaComment