    3 phase earth leakage protection

    A trick question for all you smart fellas.

    When installing a 3 phase socket outlet in a shop which is only going to feed 1 appliance with a cord not longer than 3 meters, is earth leakage protection required?
    Comments are based on opinion...not always facts....that's why people use an alias.
  • Dave A
    Site Caretaker

    • May 2006
    • 22810

    #2
    It's certainly possible in terms of 6.7.5.5.

    In fact there's a high possibility for 6.7.5.5 b) to be applicable.

    6.7.5.5 The following do not need earth leakage protection:

    b) a socket outlet that complies with SANS 164-4 and that is intended only for the connection of an appliance for critical application (such as emergency lighting, a deep freeze, a burglar alarm, data processing equipment, or life-supporting equipment);
    Participation is voluntary.

    Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services

    Comment

    • AndyD
      Diamond Member

      • Jan 2010
      • 4946

      #3
      I'd also say it was a possible yes. Lots of variables though, if the socket was fed from a control panel then it could fall outside the general installation regs.
      _______________________________________________

      _______________________________________________

      Comment

      • ians
        Diamond Member

        • Apr 2010
        • 3943

        #4
        Will be fed from a standard 3 phase DB. It will be the supply for stationary appliances used for heating and cooking
        Comments are based on opinion...not always facts....that's why people use an alias.

        Comment

        • bergie
          Email problem

          • Sep 2010
          • 308

          #5
          i would say it has to be on earth leakage relay. if the socket outlet was dedicated for 1 particular appliance that shouldnt be on earth leakage ,such as alarms,etc then only can it be left off.

          Comment

          • ians
            Diamond Member

            • Apr 2010
            • 3943

            #6
            It all starts at the design of the electrical installations.

            A little while back i got into a dispute with a clever person (electrician) who knew everything and tried to make a fool of me in front of his customer, not a wise move. I may act like a fool most of the time but I do that to protect myself.

            My point is when you design an electrical installations there are a lot of factors which need to be taken into account. One of the reasons i very seldom respond to electrical questions on public forums.

            I have been doing some research into this issue with regards to 3 phase sockets and earth leakage protection and there is some interesting things popping up. For now all i am going to say is not all 3 phase sockets have to be on earth leakage. I need to finish my research before i say anymore.

            The project i am busy with will be hugely affected by earth leakage and i have noted that none of the other installations use earth leakage protection. The meeting with the engineer is going to be rather interesting.
            Comments are based on opinion...not always facts....that's why people use an alias.

            Comment

            • AndyD
              Diamond Member

              • Jan 2010
              • 4946

              #7
              I think the simple answer would be that yes, all 3phase sockets would require E/L protection unless they somehow qualify as an exemption. If it's cooking equipment in a commercial kitchen then I'd say it would be a good idea to RCD protect them anyway given the type of abuse they'd usually suffer in that environment. Under normal circumstances I don't see the point of having kitchen equipment on plugs and sockets, it just provides another place where faults can occur.