    Auto-Star Delta circuit

    Hi Guys.

    I built an AUTO-STAR DELTA circuit with a Grease Pump. All my 3 Contactors are 400V coils and the 4th contactor for the grease pump has got a 230V coil. The operation should be as follows: As soon as you you start the panel your grease pump should also start as the its coil is wired under the start button and neutral. The problem is that as soon as I switch the main breaker on the 4th contactor(grease pump) gets energized even before I can press the start button. What might be causing this problem members?
  • bergie
    Email problem

    • Sep 2010
    • 308

    #2
    is your grease pump coil wired on the wrong side of the start button? or maybe its getting feed back from something else. post the wiring diagram

    Comment

    • Popo
      New Member
      • Jul 2013
      • 7

      #3
      NO and thanks Bergie,the grease pump coil is connected right after the start buttton and I even tried removing it from the bridge(loop) that comes after the start button to coil of the main contactor by connecting it from the gease pump coil to the other side of the start button but it gives the same story. I will attach the wiring diagram.

      Comment

      • ians
        Diamond Member

        • Apr 2010
        • 3943

        #4
        They should both be n/ o contacts
        Comments are based on opinion...not always facts....that's why people use an alias.