    Earth leakage tripping when plug in snake rack

    Hi guys

    I recently built a snake rack which uses 2 x 30watt heat cable. No matter where I plug it in my flat the earth leakage keeps tripping after about 30mins or so or as the wire heats up. With this happening I decided to plug it into a plug where I disconnected everything else and it ran fine for the night but when switched kettle on in morning it tripped. Would this be due to overloading the breaker ?
  • AndyD
    Diamond Member

    • Jan 2010
    • 4946

    #2
    It's much more likely the snake heater or whatever it is has got an insulation fault which is causing the earth leakage to trip. You'll need to get an electrician in or someone who has a megger tester to test it and replace the faulty part.
    _______________________________________________

    _______________________________________________

    Comment

    • MattyN
      New Member
      • Aug 2015
      • 4

      #3
      I decided to change the plug last night and ran it whole night without a trip. Hoping a faulty plug was the issue. Time will tell.

      Comment

      • AndyD
        Diamond Member

        • Jan 2010
        • 4946

        #4
        Plug? I'm not sure how the plug could be the culprit, highly unlikely.
        _______________________________________________

        _______________________________________________

        Comment

        • MattyN
          New Member
          • Aug 2015
          • 4

          #5
          Only thing I have really changed and had 2 days with no trouble at all. Usually it takes 30 mins and trips

          Comment

          • AndyD
            Diamond Member

            • Jan 2010
            • 4946

            #6
            You occasionally get heating elements that cause earth leakage tripping if they're either new or if they haven't been used in a long time. The mica filling in an element tube is hygroscopic and when the element is hot for some time it sometimes dries out any moisture that's been absorbed and the tripping fault miraculously disappears.
            _______________________________________________

            _______________________________________________

            Comment

            • MattyN
              New Member
              • Aug 2015
              • 4

              #7
              Awesome. Thanks for the help.

              Comment

              • Sparks
                Gold Member

                • Dec 2009
                • 909

                #8
                Could also be the cable was being pinched at the plug entry to the point where the insulation might not have been what it should be. This could also be the cause, especially if the end of the cable was cut off before fitting a new plug which applied less pressure. If this is the case I would consider a thicker cable on the appliance.