    Yesterday, i went to look at a piece of land, because i want to start a small "farm" it is a startup i have been planning on doing for some time. Now the owner got the land from "a successful land claim" and all his animals are all but gone... Now due to this epic fail he is looking to rent the land out and since my roots go back to that type of thing, i figured to give it a go.

    When I was on the property i noticed that most of the pumps where down and basically there is no water running. Now the history of the land and "if you know where to look" i found lots of water, it is there and tests say it is safe. But my word! there is not a single trip switch to be found on the property... "everything is live" and it is scary!" most of the wiring is insulation tape and block connectors... That is it... Now I will put up some photos when i start "renting" the land will get a electrician out. But damn... it is just nuts...

    Now what p!$$es me of frankly is that home owners must jump through hoops! And we must pay fines and penalties and all kinds of crap... But this is ok somehow? I phone the municipality they will come and to a inspection and if it is going to cost to much to get it up to code i will terminate our lease agreement. The agreement states outright POWER and WATER will be functioning and maintained by the LAND-LORD. Now if this guy thinks i will be happy with how things are now... He is about the have a rude awakening...
    peace is a state of mind
    Disclaimer: everything written by me can be considered as fictional.

    Comment

    • Dave A
      Site Caretaker

      • May 2006
      • 22811

      #17
      Originally posted by Leecatt
      Nice picture, I assume that you do realise that the use of "twist ties" is also illegal.
      Sometimes a picture says so much -

      Click image for larger version

Name:	can_of_worms_ahead.jpg
Views:	1
Size:	25.3 KB
ID:	264750
      Participation is voluntary.

      Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services

      Comment

      • tec0
        Diamond Member

        • Jun 2009
        • 4624

        #18
        Nice picture, I assume that you do realise that the use of "twist ties" is also illegal
        Care to elaborate on that? I am just asking because when i got the contractor in to replace all the lights in my home, "twist ties" was the norm" They are all gone now but somehow the guy that did the first COC didn't mention it and he cost me a lot of money to date and I would love to know more because this will be yet another thing he overlooked.

        My home is up to code now but it cost me a small fortune....
        peace is a state of mind
        Disclaimer: everything written by me can be considered as fictional.

        Comment

        • kosmonooit
          Full Member
          • Jul 2015
          • 40

          #19
          Originally posted by AndyD
          The regs don't permit luminaires or light fittings not to be earthed, the only mention the lamp holders.
          I was under the impression a lamp holder / light fitting was a luminaire?

          (as defined)

          3.48
          luminaire
          appliance that distributes, filters or transforms the light transmitted from
          one or more lamps and that includes all the parts necessary
          supporting, fixing and protecting the lamps but not the lamps themselves,
          and, when necessary, circuit auxiliaries together with the means for
          connecting them to the supply.

          NOTE A batten lamp holder or a lamp holder suspended by a flexible cord is a
          luminaire.


          Also the regs says fitting don't have to be earthed if they meet certain conditions, as I posted above, its the same applied for light fittings surely I dont see anywhere where it says all luminaires must be earthed.

          Comment

          • DieterT
            Bronze Member

            • Oct 2014
            • 126

            #20
            The regs don't permit luminaires or light fittings not to be earthed, the only mention the lamp holders.
            Andy, is it possible you are maybe getting confused with discharge luminaries?

            i will probably get myself in trouble by making statements like that. if the regulations say " do not earth it" ,it is different to "there is no need to earth it"
            i'm not going to earth something that is double insulated , but i always earth steel lightswitches with plastic covers and plastic screws or light fittings out of arms reach.
            Begie, +1 to that. Even if it is a plastic box with a plastic switch and I used GP wires and not a 2core + earth I would pull in an earth wire. Reason for this, what happens if that client has a steel switch installed. He'd be cursing your name for a while to come. Just thinking ahead some.

            Kosmonooit, I completely understand where you coming from.
            Unfortunately we live in an economy where everyone is trying to save a few rather than thinking ahead at the consciences and making more long term investments. Maybe it's just the hazardous locations training that made me more paranoid, but one has to look beyond the basic installation. I would rather offer a defense in court saying I did more than I was suppose to than saying I did the bare minimum, because you will always be questioned on your choices you made.

            But all and all, earth continuity should always be considered as with where an earth conductor is cut off/back or wrapped not properly connected also with metallic objects with live conductors. Remember, the earth is the main form of protection. When doing the earth resistance and continuity of bonding tests, that includes light fittings, light switches, conductive surfaces (which could become live due to a fault) that the resistance should be withing the required limit as to enable protection.

            Comment

            • kosmonooit
              Full Member
              • Jul 2015
              • 40

              #21
              Thanks Dieter I am just quoting 'the book' having made an attempt to memorise it, and the subject of earthing lights did come up for discussion in our classes at P&T.

              I have been doing domestic LED conversions using those GU10 fittings from those horrible 12V transformers that sit it the roof. Those things are a real fire / safety hazard, the get so hot the melt wires and fittings (see pic). Have seen some that are earthed, others not, but never the fittings as such. One does get a GU10 adapter with provision for earth, but if the fitting is non-conductive, there is no point really?
              Attached Files

              Comment

              • AndyD
                Diamond Member

                • Jan 2010
                • 4946

                #22
                I'm not getting confused with discharge luminaires....well not as far as I know at least.

                My understanding is that generally a 'lamp holder' is not a 'luminaire', it's a part of the luminaire that the lamp actually inserts into. These are lamp holders;Click image for larger version

Name:	Lampholders.jpg
Views:	1
Size:	32.4 KB
ID:	264753

                The only time a lamp holder on its own would qualify as a luminaire would be if it would fall under the note in the luminaire definition in 3.48.

                NOTE A batten lamp holder or a lamp holder suspended by a flexible cord is a
                luminaire.


                I don't see that reg 6.14.4.1 would extend to the entire 'luminaire' or 'light fitting' unless it was a batten lamp holder suspended by flex. Therefore there's no way a luminaire or light fitting would be exempt from earthing.

                Reg 6.14.4.1 A lamp holder shall be shrouded in insulating material or shall
                be earthed, unless it is simultaneously
                a) out of arm's reach from the floor or walkway level,
                b) out of arm's reach from a structure that is bonded to earth,
                c) protected from the weather and the splashing, dripping, or accumulation
                of water, and
                d) not touching a conductive surface.


                A luminaire or light fitting is the complete lighting assembly including the lampholder inside obviously. Luminaires;
                Click image for larger version

Name:	Luminaires.jpg
Views:	1
Size:	25.8 KB
ID:	264754
                According to the regs the definition is;
                3.48 luminaire
                appliance that distributes, filters or transforms the light transmitted from
                one or more lamps and that includes all the parts necessary
                supporting, fixing and protecting the lamps but not the lamps themselves,
                and, when necessary, circuit auxiliaries together with the means for
                connecting them to the supply.


                To address the exception made for an 'exposed conductive part' in 6.12.3.2. I'd suggest 'exposed conductive part' would apply to exposed cover screws for example. Any part likely to introduce any potential, including earth potential, would be classed as 'extraneous conductive' and not 'exposed conductive'. For the part to qualify as exposed conductive it would need to have a resistance of at least 1kΩ @ a 250v IR test in dry conditions otherwise it would be classed as extraneous conductive in which case it should be earth bonded.
                _______________________________________________

                _______________________________________________

                Comment

                • bergie
                  Email problem

                  • Sep 2010
                  • 308

                  #23
                  6.12.3.2 The following conductive parts do not need to be earthed:

                  b) exposed conductive parts of fixed electrical equipment that are
                  1) out of arm's reach from the floor (or walking) level,
                  2) out of arm's reach from a structure that is bonded to earth, and
                  3) not exposed to the weather or to the condensation, dripping,
                  splashing or accumulation of water, and
                  4) not touching a conductive surface;

                  and/or

                  6.14.4 Lamp holders


                  fixed electrical equipment : would a luminaire not be considered fixed electrical equipment?

                  Comment

                  • Dave A
                    Site Caretaker

                    • May 2006
                    • 22811

                    #24
                    Here's one I got presented with this morning.

                    It is a low hanging Radiant light fitting with metal ceiling cup and reflector/shade over a kitchen counter top -

                    Click image for larger version

Name:	unearthed-metal-reflectors.jpg
Views:	1
Size:	27.9 KB
ID:	264756

                    The bottom of the metal reflector is 1.8m above floor level. It's a 220v luminaire. Our test for earth on the metal reflector revealed no continuity back to the main earth point of the installation. Closer examination reveals there is an installation earth conductor available at the point of consumption, but no earth connection point provided to connect to within the luminaire, and the cable between the two metal parts is twin flex with no earth conductor.

                    Ultimately the luminaire seems to be installed and connected as designed...

                    Thoughts, anyone?
                    Participation is voluntary.

                    Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services

                    Comment

                    • Leecatt
                      Silver Member

                      • Jul 2008
                      • 404

                      #25
                      Well now I can't find the sentence in the regs.
                      It used to say that a tool must be used to separate connections, or something to that effect. Of course, undoing a twist tie is not using a tool. I will keep looking when I get more time.
                      To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

                      Comment

                      • Dave A
                        Site Caretaker

                        • May 2006
                        • 22811

                        #26
                        Originally posted by Leecatt
                        Nice picture, I assume that you do realise that the use of "twist ties" is also illegal.
                        Originally posted by tec0
                        Care to elaborate on that? I am just asking because when i got the contractor in to replace all the lights in my home, "twist ties" was the norm" They are all gone now but somehow the guy that did the first COC didn't mention it and he cost me a lot of money to date and I would love to know more because this will be yet another thing he overlooked.
                        Originally posted by Leecatt
                        Well now I can't find the sentence in the regs.
                        It used to say that a tool must be used to separate connections, or something to that effect. Of course, undoing a twist tie is not using a tool. I will keep looking when I get more time.
                        I'd also be curious as to the section that makes the twist tie illegal on all phase conductors and neutrals.

                        When it comes to the earth conductor,
                        6.12.1.5 - Connections of earth continuity conductors shall not rely only on twisting of the conductor or strands of the conductor
                        and
                        6.12.1.6 - A fuse or switching device shall not be fitted in an earth continuity conductor (joints which can only be disconnected by means of a tool may be provided for test purposes).
                        apply.
                        Participation is voluntary.

                        Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services

                        Comment

                        • SilverNodashi
                          Platinum Member

                          • May 2007
                          • 1197

                          #27
                          Originally posted by Dave A
                          Here's one I got presented with this morning.

                          It is a low hanging Radiant light fitting with metal ceiling cup and reflector/shade over a kitchen counter top -

                          [ATTACH=CONFIG]5888[/ATTACH]

                          The bottom of the metal reflector is 1.8m above floor level. It's a 220v luminaire. Our test for earth on the metal reflector revealed no continuity back to the main earth point of the installation. Closer examination reveals there is an installation earth conductor available at the point of consumption, but no earth connection point provided to connect to within the luminaire, and the cable between the two metal parts is twin flex with no earth conductor.

                          Ultimately the luminaire seems to be installed and connected as designed...

                          Thoughts, anyone?
                          So it shouldn't be earthed?
                          Get superfast South African Hosting at WebHostingZone

                          Comment

                          • hartdev@hotmail.com
                            Full Member
                            • Jul 2015
                            • 46

                            #28
                            I struggle to understand why any light fitting out of arms reach should not be earthed. If someone is on eg. a metal ladder and gets a shock while changing a bulb or doing a repair then that person could fall from a height as a result, making it more dangerous than something that is at arms reach.
                            It's not like it's a big deal to connect an earth wire...