    [Question] Cable depth

    Good day,

    Is it correct that an armoured cable can be buried right below paving? The regulations only refer to unarmoured.

    Reg 6.4.4.2 (a)

    Thank you
  • ACEsterhuizen
    Bronze Member

    • Mar 2012
    • 165

    #2
    Page 114, Table 6.8 should help maybe? Standard Conditions Of Installation for: multicore pvc insulated armoured cables buried directly in the ground:: 0.5m Depth Of Burial. Also see SANS 1507. (as sans 10142 refers to it)

    Comment

    • ElectricalContractorGuy
      New Member
      • Oct 2015
      • 2

      #3
      Thank you Ace - understood. The regulations note 6.4.4.2 (a) - unarmoured cable may be buried 1) in less than .5m 2) in a conduit 3) under paving or concrete.

      My question however is does this apply to armoured cable also?