    Thanks for that info AndyD, very informative (even 5 years later). I have a question though, is there a limit on how many milliseconds the RCD should take to trip? I did a check across 37 installed RCD's and the time range from 9 to 203 milliseconds.

    Comment

    • Ippi591
      New Member
      • Oct 2017
      • 5

      #32
      I found a document, VC8035 From 1987, Compulsory Specification for Earth leakage protection units.

      It lists the following times:

      Click image for larger version

Name:	elu time.jpg
Views:	1
Size:	92.8 KB
ID:	265821

      Are they still relevant?

      Comment

      • MCP
        New Member
        • Jul 2023
        • 1

        #33
        Originally posted by AndyD
        If there's anything I missed, anything that's inaccurate or anything that doesn't read too well grammatically please let me know.
        Andy - that was an amazing summary that prompted me to sign up and congratulate you.
        This is my first ever post.
        And also to ask a question which I hope is not deemed too dumb.
        How many circuit breakers can one connect on a bank supplied by a single RCB/EL?
        Is there a limit or does one break it up for easier management in future fault-finding?
        The DBs I have seen mostly have only the plug circuits on EL. Typically 20A C/Bs.
        eg - I have seen DBs with 10x20A C/Bs on a single EL. Others with max of 5x20A C/Bs on EL and with 2 or 3 "banks" of these.
        Most are "old style" black Samite but some are "new style" DIN rail.
        Thx
        C

        Comment

        • GCE
          Platinum Member
          • Jun 2017
          • 1482

          #34
          Originally posted by MCP
          Andy - that was an amazing summary that prompted me to sign up and congratulate you.
          This is my first ever post.
          And also to ask a question which I hope is not deemed too dumb.
          How many circuit breakers can one connect on a bank supplied by a single RCB/EL?
          Is there a limit or does one break it up for easier management in future fault-finding?
          The DBs I have seen mostly have only the plug circuits on EL. Typically 20A C/Bs.
          eg - I have seen DBs with 10x20A C/Bs on a single EL. Others with max of 5x20A C/Bs on EL and with 2 or 3 "banks" of these.
          Most are "old style" black Samite but some are "new style" DIN rail.
          Thx
          C
          Per regulations you can put as many CB after the Earth leakage as you want to - The Earth leakage has to be overloaded protected so in a domestic situation usually 63Amp isolator type earth leakage an it would have a max of 63Amp CB protecting.

          Good practice is to install limited CB after the earth leakage and that is very dependent on usage - Every appliance has a leakage to earth so eventually an earth leakage will trip purely due to the qty of appliances leaking to earth , some worse than others

          In smaller house you would do 1 ELU and 3 plug circuits , In a bigger house maybe 2 earth leakages or 3

          My previous house I had 5 Earth Leakage units , where I squat now I have 3 and really only need 1 but I don't like struggling when I get home , I prefer drinking a beer in peace