Welcome to The Forum SA. As a visitor you have read only access to the public content areas of this website. You will have to register as a member to access all content, post messages and network with our members. Membership is free and registering is quick and easy. You can click here to register now and become a member within minutes.
I would just like some clarity on installing an earth leakage for welding plugs. Most manufacturers only make 2 pole and 4 pole earth leakages so how would a 3phase plus earth welding socket need to be connected as there is no neutral
You can usually use a 4-pole earth leakage breaker on a 3 phase circuit that has no neutral. One issue may be that the test button is using the neutral to create the imbalance to trip when it's pressed in which case it's not a suitable.
Just as a side note, RCD's and welders are a notoriously problematic and can result in bad nuisance tripping due to the type of load a welder presents to the supply with harmonics , high inrush currents and spikes. What do the manufacturers instructions say about the supply requirements? Sometimes they recommend that no RCD is fitted. Can the circuit be installed without an RCD and still meet compliance requirements? If it can ie dedicated sockets etc I'd suggest a risk assessment and see if the RCD is necessary.
We process personal data about users of our site, through the use of cookies and other technologies, to deliver our services, personalize advertising, and to analyze site activity. We may share certain information about our users with our advertising and analytics partners. For additional details, refer to our Privacy Policy.
By clicking "I AGREE" below, you agree to our Privacy Policy and our personal data processing and cookie practices as described therein. You also acknowledge that this forum may be hosted outside your country and you consent to the collection, storage, and processing of your data in the country where this forum is hosted.
Comment