Sizing of Electrical components

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • @SamboLindoh
    Junior Member
    • Jul 2015
    • 18

    #1

    [Question] Sizing of Electrical components

    Hey guys I have got a three phase drill presser here; on the name plate it written, Volt (400.), Ph(3), Pole (4), ,Hz (50),, kW (1.1), r.p.m. (1400), A(2.75), Cos (0.72), type (YS 90), Ins.Cl F, IP (54)& S6-60%. Now my 1st question what size 3 Phase C/B should I use?
  • AndyD
    Diamond Member

    • Jan 2010
    • 4951

    #2
    The circuit breaker is sized according to the circuit, not the appliance. Can you give details of the circuit? Is it on a plug and socket or will it be the only appliance on the circuit and hard wired into a t/pole isolator?
    _______________________________________________

    _______________________________________________

    Comment

    • @SamboLindoh
      Junior Member
      • Jul 2015
      • 18

      #3
      Sorry for the late response Andy, it will be the only appliance connected. It will be 5meters away from the DB that I'll use to power it up. The cable will be run on a cable tray.

      Comment

      • MullerR
        Full Member
        • Jan 2016
        • 44

        #4
        Does the drill press motor has its own overcurrent relay for in the case of an overcurrent? If so, it can be wired from the db with a 1 or 1.5sqmm surfix,protected by a 5A curve 1 mcb.
        Stupid questions are the ones never asked. Knowledge is power, so if you don't know, ask.

        Comment

        • @SamboLindoh
          Junior Member
          • Jul 2015
          • 18

          #5
          Thank you MullerR for your response, if I may ask what formular did you use to size the circurt breaker. If I calculate the current that my drill presser will draw (using P=root3*V*I) I get 1.59Amps.
          from there how do you size your breaker?

          Comment

          • AndyD
            Diamond Member

            • Jan 2010
            • 4951

            #6
            Your circuit breaker size is calculated from the cable size, the installation method, cable length etc etc. The circuit breaker protects the circuit, not the drill that's connected to it. The drill press motor should be protected by an appropriately sized thermal overload contained within the drill press itself.

            Also you can't calculate the run current of a motor from the kW rating of the motor. The kilowatt rating of a motor is an indication of its mechanical output, not its electrical input. In the good old days we sized motors in Horsepower and a 1 HP (Horsepower) motor meant it could lift the same weight at the same speed as an actual horse which is a measure of its output capabilities. Nowadays we use Kilowatts for the same measure and 1 horsepower is around 0.75kW. This has lead to endless confusion because electrical input is also measured in kilowatts but the electrical input will always be higher than the mechanical output because no motors are 100% efficient and free from losses.

            So basically you can't convert the kilowatt rating of a motor into a run current unless you also know its efficiency, it's power factor and any other losses including friction etc. If you want the run current rather refer to the data on the plate on the side of the motor or the loading graphs supplied by the manufacturer.
            _______________________________________________

            _______________________________________________

            Comment

            • Dave A
              Site Caretaker

              • May 2006
              • 22818

              #7
              i.e.

              Originally posted by @SamboLindoh
              Hey guys I have got a three phase drill presser here; on the name plate it written, Volt (400.), Ph(3), Pole (4), ,Hz (50),, kW (1.1), r.p.m. (1400), A(2.75), Cos (0.72),...
              Participation is voluntary.

              Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services

              Comment

              • Justloadit
                Diamond Member

                • Nov 2010
                • 3518

                #8
                A rule of thumb I use to calculate starting current for a motor is 8:1. So if the motor is a 1Amp motor, the starting current will peak approximately at 8Amps. The period that it remains at 8Amps is directly linked to the load.

                But as Andy says the circuit breaker in the DB is there to protect the wiring, not your load.
                Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
                Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

                Comment

                • @SamboLindoh
                  Junior Member
                  • Jul 2015
                  • 18

                  #9
                  The drill presser will be the only machinery connected to this circuit breaker there will be no other machinery or appliance connected. the drill presser will be "5m" away from the the DB and the cable will run on a cable rack.Please see the attached name plate for the drill presser.
                  Attached Files

                  Comment

                  • AndyD
                    Diamond Member

                    • Jan 2010
                    • 4951

                    #10
                    Originally posted by Justloadit
                    A rule of thumb I use to calculate starting current for a motor is 8:1. So if the motor is a 1Amp motor, the starting current will peak approximately at 8Amps. The period that it remains at 8Amps is directly linked to the load.

                    But as Andy says the circuit breaker in the DB is there to protect the wiring, not your load.
                    With small motors the start current would generally only affect the selection of the curve of the circuit breaker. In SA most MCB's are C curve as standard which means they'll tolerate 5-10 times their rated load current without instantaneous tripping which will tolerate most motor start currents. In some EU countries and the UK for example most MCB's are installed as B curve as standard so they would be more likely to nuisance trip with a motor load.

                    @Sambo, The fact it's such a small motor limits your circuit design options somewhat so I really wouldn't overthink this too much. Being a drill press it won't be started under any great load so I'd just go with MullerR's suggestion of a 1.5mm Surfix with a 5A C-curve MCB.
                    _______________________________________________

                    _______________________________________________

                    Comment

                    • @SamboLindoh
                      Junior Member
                      • Jul 2015
                      • 18

                      #11
                      C/B

                      Thank you very much guys, you have given me a fish (Answer) definetly sure I won't go hungry today but however please teach me how to fish now (how did you get about to that 5Amp C-curve MCB ..."METHOD/FORMULAR) THANK YOU ONCE MORE.

                      Comment

                      • MullerR
                        Full Member
                        • Jan 2016
                        • 44

                        #12
                        @sambo. If you read the previous comments from Andy,Dave and Justlaodit, you will see theres no formula here. The drill press has its own overcurrent protection device (supposed to). On the ID plate it states the drill will draw a current of 2.75A. Thus you go and check what wire size can draw those amps on that lenght. Refer to sans 10142-1 for volt drop calculations etc. If you determined the wire size, you must now select the protection device (mcb) to protect the wire (circuit). In this case, if you use a 1.5sqmm Surfix, a 5A mcb is more than sufficient. If you want more info on cables etc, check if you can download the aberdare catalogs. If you cant get hold of them,let me know, i can upload it.
                        Stupid questions are the ones never asked. Knowledge is power, so if you don't know, ask.

                        Comment

                        • @SamboLindoh
                          Junior Member
                          • Jul 2015
                          • 18

                          #13
                          I couldn't please forward it to me MullerR my email is "lindoh.sambo@gmail.com"

                          Thank you in advance.

                          Comment

                          Working...