Issuing electrical COCs - On a hiding to nothing!

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • 1reniernel
    Email problem
    • Jan 2012
    • 6

    #16
    Selling of a factory premises

    Originally posted by Sparks
    Not quite. The integral wiring of appliances, depending on the length thereof, just may form part of the COC.
    Can you perhaps give me an example of an appliance of which integral wiring must be included in the CoC?

    Comment

    • Sparks
      Gold Member

      • Dec 2009
      • 909

      #17
      An eyelevel oven with a hob connected to it more than 1m away, the interconnecting cables form part of the COC. The COC does not end at the first point of termination. The actual oven and hob however are still not part of the COC.

      The connecting cables of a split unit aircon unless mounted back to back will also qualify.
      Last edited by Sparks; 12-Feb-12, 12:56 AM. Reason: Addition

      Comment

      • Leecatt
        Silver Member

        • Jul 2008
        • 404

        #18
        Originally posted by murdock
        dave
        what you should have done...what everyone else is doing is just fitted a plug top to the cable feeding the outbuiding and you are no longer responsible...it no longer forms part of the installation...time and money saved..
        Ive heard of this before and actually seen it about 8 years ago. However I read in an electrical Magazine, could have been Sparks, that it would be contested and the electrician would be found responsible for the alienated circuitry. I can no longer find the relevant article but the following portion of the Electrical Regulations seem to back this up, unless I am reading it wrong. Comments more than welcome to clear this up.


        "electrical installation" means any machinery, in or on any premises, used for the transmission of electricity from a point of control to a point of consumption anywhere on the premises, including any article forming part of such an electrical installation irrespective of whether or not it is part of the electrical circuit, but excluding..........(not relevant)

        Full regulations here
        To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

        Comment

        • Sparks
          Gold Member

          • Dec 2009
          • 909

          #19
          Spot on Leecatt

          Comment

          • murdock
            Suspended

            • Oct 2007
            • 2346

            #20
            so tell me how a ready board works...in low cost housing...1 db...3 plugs and you know the rest...

            please show me typical cases where the AIA or DOL have enforced this ruling.

            Comment

            • Dave A
              Site Caretaker

              • May 2006
              • 22810

              #21
              Originally posted by Sparks
              An eyelevel oven with a hob connected to it more than 1m away, the interconnecting cables form part of the COC. The COC does not end at the first point of termination. The actual oven and hob however are still not part of the COC.

              The connecting cables of a split unit aircon unless mounted back to back will also qualify.
              Does this mean it can't be done in cabtyre exceeding a certain length?
              (3 metres)?
              Participation is voluntary.

              Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services

              Comment

              • Sparks
                Gold Member

                • Dec 2009
                • 909

                #22
                It means that where integral wiring exceeds 1m in length, that integral wiring also forms part of the certifiable installation and must comply with the applicable regs.

                Comment

                • murdock
                  Suspended

                  • Oct 2007
                  • 2346

                  #23
                  aircons are a good example...they use to only use cabtyre...but inoticed on the project we are busy with they are using 2.5 x 4 core surfix

                  Comment

                  • Dave A
                    Site Caretaker

                    • May 2006
                    • 22810

                    #24
                    Originally posted by Sparks
                    It means that where integral wiring exceeds 1m in length, that integral wiring also forms part of the certifiable installation and must comply with the applicable regs.
                    I've just raised this with my wireman and he's scratching his head - there's nothing about this in the airconditioning section of fixed appliances.
                    What is the applicable reg?
                    Participation is voluntary.

                    Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services

                    Comment

                    • Leecatt
                      Silver Member

                      • Jul 2008
                      • 404

                      #25
                      Originally posted by Dave A
                      I've just raised this with my wireman and he's scratching his head - there's nothing about this in the airconditioning section of fixed appliances.
                      What is the applicable reg?
                      1./ I understand the following to mean that the wiring between different parts of the same appliance that exceed 1,5 meters are to be considered as part of the electrical installation and subject to SANS requirements:

                      6.16.1.1 Fixed appliances do not form part of the electrical installation other than their positioning in relation to the supply and the wiring carried out between different parts of the appliances.

                      6.16.1.11 The wiring between different parts of a fixed appliance that are installed separately is part of the fixed installation, even where it is supplied from a socket-outlet, unless such wiring is less than 1,5 m in length.


                      2./ I understand the following to mean that 2.5mm and 1.5 mm cables should be solid copper type. Ie Surfix or Norsk cable.

                      6.3.2 Construction
                      6.3.2.1 Conductors of nominal cross-sectional area exceeding 2,5 mm2 shall be stranded, except in the following cases, where solid conductors may be used:
                      a) conductors of mineral-insulated metal-sheathed cables;
                      b) internal connections of distribution boards, switchgear and industrial
                      controlgear;
                      c) busbars;
                      d) aerial conductors;
                      e) aluminium conductors of nominal cross-sectional area 16 mm2 or
                      more; and
                      f) copper conductors of nominal cross


                      3./ I understand the following to exclude the use of Cabtyre cables entirely

                      6.3.1 Materials
                      All conductors of nominal cross-sectional area less than 16 mm2 shall be of annealed copper. In the following cases alternative material may also be used:
                      a) earth continuity conductors (see 6.12.1.9);
                      b) bonding conductors (see 6.13.1); and
                      c) aerial conductors (see 6.3.4).


                      4./ I hope that I have understood the above quotes correctly.
                      The reason I am here is to learn and not to teach, please criticize if necessary.
                      To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

                      Comment

                      • Dave A
                        Site Caretaker

                        • May 2006
                        • 22810

                        #26
                        Thanks Leecatt. At least I can now point to the relevant section that drives the point raised.

                        While I was looking at the section myself, it struck me how easy it is to take stuff out of context. As example:

                        6.16.1.6: A socket-outlet shall supply only one fixed appliance. The use of flexible cords of length exceeding 3 m is not recommended.

                        It's clearly pretty important to pay attention to the whole section to get the right interpretation (in this case 6.16.1.1 to 6.16.1.13 in full by the looks of things).
                        Participation is voluntary.

                        Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services

                        Comment

                        • murdock
                          Suspended

                          • Oct 2007
                          • 2346

                          #27
                          and you need to understand the different between cabtyre flexible cords and and flexible cables...i went to a site where the cabling between the floors...where wired with flexible cables...which was not illegal because unless you understand the definition of cords and cable you could make a noise for nothing.

                          Comment

                          • Leecatt
                            Silver Member

                            • Jul 2008
                            • 404

                            #28
                            Originally posted by Dave A
                            Thanks Leecatt. At least I can now point to the relevant section that drives the point raised.

                            While I was looking at the section myself, it struck me how easy it is to take stuff out of context. As example:

                            6.16.1.6: A socket-outlet shall supply only one fixed appliance. The use of flexible cords of length exceeding 3 m is not recommended.

                            It's clearly pretty important to pay attention to the whole section to get the right interpretation (in this case 6.16.1.1 to 6.16.1.13 in full by the looks of things).
                            Thats right, you literally have to know the whole book - in context as well.
                            I must be honest and say that I enjoy the rules and regs, quirky but that's me.
                            I find that the older I get the more slips away and its not that easy any more so this forum is something of great value to me.
                            If I go on too much about SANS feel free to shit me out

                            By the way, the name is Lee (i dont know how to change the LEECATT?)
                            Last edited by Leecatt; 13-Feb-12, 09:05 PM. Reason: additional info
                            To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

                            Comment

                            • AndyD
                              Diamond Member

                              • Jan 2010
                              • 4946

                              #29
                              Originally posted by Leecatt
                              3./ I understand the following to exclude the use of Cabtyre cables entirely

                              6.3.1 Materials
                              All conductors of nominal cross-sectional area less than 16 mm2 shall be of annealed copper. In the following cases alternative material may also be used:
                              a) earth continuity conductors (see 6.12.1.9);
                              b) bonding conductors (see 6.13.1); and
                              c) aerial conductors (see 6.3.4).

                              I don't think that 6.3.1 excludes the use of cabtyre. Cabtyre has stranded annealed copper conductors. I think section 'a' allows earthing continuity conductors to be galvanised steel conduit for example. Section 'b' allows bonding conductors to be hard-drawn copper bar (not annealed) or aluminium.

                              I completely agree that interconnecting cables for an oven/hob or an airconditioner may fall under the COC and simple running these appliances from a plug wouldn't exclude them.
                              _______________________________________________

                              _______________________________________________

                              Comment

                              • Dave A
                                Site Caretaker

                                • May 2006
                                • 22810

                                #30
                                Yet another opportunity to be slagged off as money-grubbing rip-off artists by the the looks of things.

                                But as I keep saying to clients in our defence - we don't make the rules, we just apply them.

                                Originally posted by Leecatt
                                By the way, the name is Lee (i dont know how to change the LEECATT?)
                                I just checked - I regret the username Lee is already taken.
                                Participation is voluntary.