What is the regulations saying with regards to three phase and single phase cooking appliances used in take away stores for example that is feed from a welding socket? The socket can also be classified as an isolator cause it serves the same perpose, but should it be on earth leakage or not? A fixed alliance don't need earth leakage protection cause its on an isolator but in this case its equipment thst s on wheels that can be moved for cleaning purposes due to the oil etc. I struggle to come to a solid point regarding this as there's so many points that almost sounds contradictory in sans 10142:1. And some equipment works on two phases and neutral but I haven't seen a 2 phase c\b except for live and neutral 2 pole circuit breakers and then the normal 3 pole circuit breakers. What's your opinion about this and issuing a coc for this kind of installation?
Fixed appliances
Collapse
X
-
Tags: None
-
When it comes to socket-outlets, section 6.15 must be taken into account.
6.15.1.2.4 contains this -
Then 6.15.1.2.6 contains this -NOTE 1 Dedicated socket-outlets are the only socket-outlets that need not be protected by earth leakage.
The use of the term "stove coupler" may cause some confusion (as it did during the interview of one of the candidates for a technical advisor post of the ECA(SA) last week), so for clarity -NOTE 1 Earth leakage protection is not required for the stove circuit when a stove coupler is used.
6.15.1.2.5 specifies -
A stove coupler shall comply with the requirements of SANS 60309-1 and shall be of dimensions as given in SANS 337.Participation is voluntary.