Beware of PioLED lighting lamps

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • ians
    Diamond Member

    • Apr 2010
    • 3943

    #1

    Beware of PioLED lighting lamps

    I purchased a box of 5 ft LED lamps...Wired the fittings to suit and tested...works.

    So whats the problem...i start installing and connecting the light fittings and get my assistant to install the lamps...switch on and BOOOOM big bang.

    It turns out that you cannot install PioLED lamps in the opposite way...the catch is this company is selling this product directly to the public...who might not be aware of this issue...nor can i find any certification...indicating that they are certified anywhere else in the world.

    Checked a few PioLED light fittings for some for approval anywhere in the world...nothing...not even a country of origin...where they are manufactured etc...nothing.

    I stripped a fitting thinking i might find a stamp of sorts somewhere on the fitting.

    So the question...

    do these light fittings not need some form of approval to be sold in SA?

    Can you modify a fitting to suit these 230 volt LED lamps...which would change the integrity of the wiring...removing any form of certification for the fitting?
    Comments are based on opinion...not always facts....that's why people use an alias.
  • GCE
    Platinum Member

    • Jun 2017
    • 1473

    #2
    Hi Ians

    Besides the normal SANS 10142 instructing us to use SABS certified equipment only there are also Approved Recommended Practice ( ARP ) notes publish by SABS.

    There is an ARP 032:2014 publish in connection with retrofits of fluorescent fittings to LED tubes -

    We read the ARP and decided that the risks to carry out retrofits are to high vs the reward.

    The minute you change the wiring/design of a fitting you need to carry out an approval/verification process and ensure that the fitting would pass an end of line test complying with SANS 60598-1

    In short - You are allowed to rewire the fitting but you become the certification for the fitting , installation procedure , lighting designer ensuring that the modified fittings match the original lighting design for glare and lux levels

    Comment

    • Leecatt
      Silver Member

      • Jul 2008
      • 404

      #3
      Originally posted by GCE
      Hi Ians

      Besides the normal SANS 10142 instructing us to use SABS certified equipment only there are also Approved Recommended Practice ( ARP ) notes publish by SABS.

      There is an ARP 032:2014 publish in connection with retrofits of fluorescent fittings to LED tubes -

      We read the ARP and decided that the risks to carry out retrofits are to high vs the reward.

      The minute you change the wiring/design of a fitting you need to carry out an approval/verification process and ensure that the fitting would pass an end of line test complying with SANS 60598-1

      In short - You are allowed to rewire the fitting but you become the certification for the fitting , installation procedure , lighting designer ensuring that the modified fittings match the original lighting design for glare and lux levels
      Very interesting.
      Once you rewire the fitting it is no longer SABS certified and the installation no longer complies with the SANS 10142-1.
      To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

      Comment

      • ians
        Diamond Member

        • Apr 2010
        • 3943

        #4
        My concern is more for the man on the street...we as qualified electricians are aware of the dangers...and even we have blown a few of these Pioled lamps to pieces.

        A few things to note.

        A customer unaware of the modification...purchases a 230 volt led lamp...and tries to fit it into a "modified" fitting...however as some people are doing...wiring both ends 230 volts...if you fit a Pioled lamps there is going to be a big bang...if the lamp explodes in your hand...you gona end up with injuries to your face...could even damage your eyes...being so close to the lamp while installing it...you could cut hand...and we all know what happens when you that glass from these lamps break.

        An electrical company purchases a box of 230 lamps...and lets the semi skilled people replace the lamps...unaware that some of the lamps could be normal fittings with starters and ballasts...others could be 230 volt wired both sides.

        and many other dangers.

        My question is where is the policing...are we waiting for someone to get injured or killed before some form of standard is introduced.

        It seems buying from the China mall or the reputable electrical wholesaler is the same thing...all just out to make a quick buck...regardless of the public danger.

        I have contacted my electrical wholesaler and requested the required documents to add to my COC.



        Being the Pioneers of LED Lighting, it is our duty to set the industry standard for all LED advancements. We look forward to making an ever-lasting impression on you with our exceptional Quality and Service.
        Comments are based on opinion...not always facts....that's why people use an alias.

        Comment

        • ians
          Diamond Member

          • Apr 2010
          • 3943

          #5
          Pioled do have a 2 year warranty on their products...returning faulty products is another entire thread on its own. ..make sure you have the correct documentation and the date of purchase stamped on the product...it seems a common problem is products has a date of manufacture...not a date of purchase...the 2 year warranty is valid from the date of manufacture...it could be in transit...customs...and on the shelf you a lot longer than expected...as i have experienced.

          My biggest concern is the latest issue with a faulty fitting...if this fitting had burnt the office block down would the insurance pay out...if the fitting is not SABS approved or been modified.

          if i were in the insurance industry...risk management or a building manager responsible for tenants in the building...i would be checking products being installed...considering there is no policing of the sale of these products.
          Comments are based on opinion...not always facts....that's why people use an alias.

          Comment

          • Dave A
            Site Caretaker

            • May 2006
            • 22810

            #6
            Originally posted by ians
            ..make sure you have ... the date of purchase stamped on the product...
            Say what?
            Who is supposed to do that?
            Participation is voluntary.

            Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services

            Comment

            • ians
              Diamond Member

              • Apr 2010
              • 3943

              #7
              Originally posted by Dave A
              Say what?
              Who is supposed to do that?
              I do it with all equipment i install...The date of manufacture doesnt help when it takes a year plus for the product to get to the consumer...and the product has a 2 year warranty.

              I received the certification the light fittings...it is to certify that Pioled fittings have been tested and approved in China...i assume they dont need one for SA...as they see our SABS regulations as a joke like everyone else...the question is who is going to police it...so why bother.
              Comments are based on opinion...not always facts....that's why people use an alias.

              Comment

              • ians
                Diamond Member

                • Apr 2010
                • 3943

                #8
                As someone pointed out to me today...why bother with SABS approval or an RCC number...light fittings do not form part of a COC...so why waste the time worrying about it...its not my problem...even though i supply and fit the fitting.

                The only people who should be worried about it...insurance companies...or should they...a good excuse to deny a claim...so at the end of the day... once again...the only sucker is...yip you guessed it...the owner/customer.
                Comments are based on opinion...not always facts....that's why people use an alias.

                Comment

                • AndyD
                  Diamond Member

                  • Jan 2010
                  • 4946

                  #9
                  Retrofitted LED T8 tubes are a problem because there's 2 types availible. One type requires a live and neutral on the same end, the opposite end is a short circuit. The other type requires a live on one end and a neutral at the other of the tube and the pins on both ends are a short circuit.

                  If wired correctly both types are reversible without a problem but when the fitting is wired for one of the types you can't replace the tube with the other type without introducing a fault.
                  Last edited by AndyD; 01-Aug-18, 09:56 AM.
                  _______________________________________________

                  _______________________________________________

                  Comment

                  • AndyD
                    Diamond Member

                    • Jan 2010
                    • 4946

                    #10
                    The standard fluroscent wiring looks like this;

                    Click image for larger version

Name:	Standard Flouroscent Wiring.jpg
Views:	1
Size:	41.1 KB
ID:	265529
                    _______________________________________________

                    _______________________________________________

                    Comment

                    • AndyD
                      Diamond Member

                      • Jan 2010
                      • 4946

                      #11
                      The first type of LED retrofit tube requires that the ballast is bypassed/removed and a 1 Amp fuse is installed in place of the starter.

                      Click image for larger version

Name:	Fuse.jpg
Views:	1
Size:	39.5 KB
ID:	265530

                      The final conversion would be wired like this;

                      Click image for larger version

Name:	LED Tube Type 1.jpg
Views:	1
Size:	44.0 KB
ID:	265531
                      _______________________________________________

                      _______________________________________________

                      Comment

                      • AndyD
                        Diamond Member

                        • Jan 2010
                        • 4946

                        #12
                        The second type of LED tube requires a live and neutral on opposite ends so the converted wiring would look like this;

                        Click image for larger version

Name:	LED Tube Type 2.jpg
Views:	1
Size:	47.2 KB
ID:	265532
                        _______________________________________________

                        _______________________________________________

                        Comment

                        • AndyD
                          Diamond Member

                          • Jan 2010
                          • 4946

                          #13
                          In both of the LED wiring schemes above the tube is reversible without a problem but if the tube is replaced at a later date with one that's the other type there could be problems.

                          All retrofitted T8 fittings should have a warning sticker and a circuit diagram inside them after they've been converted.
                          _______________________________________________

                          _______________________________________________

                          Comment

                          • ians
                            Diamond Member

                            • Apr 2010
                            • 3943

                            #14
                            I had another mishad last week ...installed the Pioled 5 ft lamp lamp the wrong way again ... "BOOM" ...so what is the big deal ... i am a master electrician and i get it wrong ... how on earth is the customer with no electrical knwoledge expected to know that one side of the 5 ft lamp has a dead short.

                            Another issue with LED tube type fittings ... I am yet to come across a fitting with the lampholders labelled AC live side ... the tube might has it marked but if you dont know which side has the live and neutral ... the way i see it whoever authourised the cerification for these products to be sold in SA should be held responsible for the injury or damage to the infrasture.

                            Somebody need sto take this to the correct auhourities before someone is injured or killed.

                            DONT SAY YOU HAVENT BEEN WARNED.

                            With regards to the purchase date ... beware ...some product are dated 2019 and sold in 2020 (yip its already the middle of the year ... imagine trying to return a faulty product without the invoice) I know i tried ... i was told by Pioled to go bother someone else with my issues ... over a silly R200 light fitting ... it was a bad idea.
                            Comments are based on opinion...not always facts....that's why people use an alias.

                            Comment

                            • ians
                              Diamond Member

                              • Apr 2010
                              • 3943

                              #15
                              Some good news ... when purchasing Pioled lamps you get a strip of stickers in the box... which can be attached to the side of the fitting which has the terminals connected to 230 VAC.

                              This should be another annexure to the regs ... like solar etc ... there should be clear indication/labelling on the fitting with regards to the wiring configuration and the type on lamp to be used.

                              It is easy to say just cheack the lamp and replace it with the same lamp ... in practise not so easy and very dnagerous.