Mastech 5908C Multifunction Tester (Lite)

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • AndyD
    Diamond Member

    • Jan 2010
    • 4951

    #1

    Mastech 5908C Multifunction Tester (Lite)

    Mastech 5908C 'Circuit Analyzer'

    Price; Under a grand ZAR.

    Looks like this;

    Click image for larger version

Name:	02.jpg
Views:	1
Size:	25.0 KB
ID:	269702

    Tests performed;

    • True RMS
    • Ground to Neutral Voltage
    • Peak Voltage
    • Frequency
    • 5A/8A/10A load for volt
    drop test
    • Socket test function
    • RCD / GFCI test
    Line Volts: 85 - 265V
    Neutral/Ground: 0 - 10V
    Peak: 121 - 374V
    Freq: 45 - 65Hz
    Volt Drop: 0.1 - 99.9%
    RCD trip time: 1ms - 6.5s
    RCD trip Amp 30mA
    GFCI trip time: 1ms - 6.5s
    GFCI trip Amp: 6mA

    Has anyone got any first hand experience of this tester? I have a Mastech multimeter with logging that I use on my repair bench, it's a couple of years old, always been accurate and recently passed a calibration. The input stage on the multimeter isn't as well protected as a Fluke for example, it's classed as CATIII but lacks in physical separation and fuse quality. That said I'm aware of its limitations and only use it for electronics benchwork.

    The 5908C does an impressive array of tests and given the price it would be rude not to buy one if it does what it says. Just wondered if anyone had any advice about whether it's fit for purpose.

    MS5908C.pdf
    _______________________________________________

    _______________________________________________
  • Dave A
    Site Caretaker

    • May 2006
    • 22818

    #2
    It looks like you'll have to be our tester, Andy.

    I have to say it does look interesting...
    Participation is voluntary.

    Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services

    Comment

    • AndyD
      Diamond Member

      • Jan 2010
      • 4951

      #3
      Already ordered last week, will keep you posted.
      _______________________________________________

      _______________________________________________

      Comment

      • AndyD
        Diamond Member

        • Jan 2010
        • 4951

        #4
        Okay, as of this afternoon I'm the proud owner of a brand new Mastech 5908C 'Circuit Analyzer'.

        Contained in the box is;
        1x Zip pouch
        1x Instruction booklet (identical to the pdf in the post above)
        1x Mastech 5908C tester
        6x AAA batteries
        1x Test lead with a 10Amp IEC 60320 plug on one end (computer type plug) and a 16Amp Schuko plug on the other end.

        Why it comes with a Schuko plug on the lead I can't imagine, as far as I know schuko sockets aren't even legal in South Africa.


        Click image for larger version

Name:	a.jpg
Views:	1
Size:	31.0 KB
ID:	265549
        _______________________________________________

        _______________________________________________

        Comment

        • AndyD
          Diamond Member

          • Jan 2010
          • 4951

          #5
          Removing the battery cover and another 4 screws on the reverse side of the tester the entire back easily separates to reveal the single circuit board inside.

          Click image for larger version

Name:	b.jpg
Views:	1
Size:	69.2 KB
ID:	265550

          A considerable spiral of plactic came out with two of the back panel screws which appear to just self-tap into the posts on the front panel and on later reassembly one of the screws didn't tighten fully.

          The internal circuit board looks fairly neat at first glance, all the components are SMD with no through-hole components that I've seen in abundance on cheaper testers in the past. There's numerous empty solder pads scattered around the board along with a solid plastic blanking plug on the LHS of the tester where a button might go which suggests there's at least one more model available in this form factor with extra components and probably extra tests it can do.

          The soldering on the input pins is borderline passable at best and there's no slots cut into the circuit board to create safety separation between the input area and the logic area of the board. The input fuse looks like it might be silica filled but it's small and of poorer quality than the HRC fuses you get in more expensive testers. Also there's only a single fuse and a very small surge arrestor by the looks of it and there's no containment panels molded into the back panel to surround the fuse and the MOV to contain any flash that might occur should they ever blow.

          According to the literature the rating of the tester is IEC 601010-1, 300v, CAT III. I'd probably be happy to use the tester on single phase domestic circuits but the safety of the input stage doesn't instill much confidence and I'd be loathed to use it anywhere with higher than average PFC, anywhere where there may be high voltage transients or where there could be any chance the 300v limit might be accidentally exceeded.
          _______________________________________________

          _______________________________________________

          Comment

          • AndyD
            Diamond Member

            • Jan 2010
            • 4951

            #6
            The input stage of the tester also has a large 5 Watt resistor which is mounted on top of a small chip. I'd guess the resistor is for performing the voltage test with a 5A, 8A and 10A load and the chip underneath it is for sensing over-temperature of the resistor which is going to heat up pretty quickly during this type of test. The resistor is sitting at an angle above the chip and there's a gap of a couple of milimeters between them. I'm not convinced about the effectiveness of this arrangement as protection against overheating, a thermal fuse would have been a nice addition here.

            Click image for larger version

Name:	c.jpg
Views:	1
Size:	59.8 KB
ID:	265552


            Under the microscope it's easier to see the angle and distance of the components relative to each other;

            Click image for larger version

Name:	5.jpg
Views:	1
Size:	45.9 KB
ID:	265551
            _______________________________________________

            _______________________________________________

            Comment

            • AndyD
              Diamond Member

              • Jan 2010
              • 4951

              #7
              A closer look at the board shows that there's several areas where the components were soldered on by hand. The quality of the soldering and the amount of residual flux and contamination is very poor.

              This is the MOV surge arrestor on the input stage;

              Click image for larger version

Name:	7.jpg
Views:	1
Size:	87.2 KB
ID:	265553



              This is some of the SMD soldering under a microscope showing large amounts of contamination;

              Click image for larger version

Name:	6.jpg
Views:	1
Size:	77.9 KB
ID:	265554 Gawd knows what all the black bits are...


              Click image for larger version

Name:	1.jpg
Views:	1
Size:	101.0 KB
ID:	265555 I'd be interested to know if R16 is supposed to be there....


              Click image for larger version

Name:	2.jpg
Views:	1
Size:	100.8 KB
ID:	265556
              _______________________________________________

              _______________________________________________

              Comment

              • AndyD
                Diamond Member

                • Jan 2010
                • 4951

                #8
                So.....to sum up so far, I guess you get what you pay for.

                On the down side it's got minimal, probably borderline passable user protection. The general build quality and ruggedness is average until you get down to component level on the board when it becomes unacceptably poor and it comes with a plug that's not relevant in this country.

                On the up side is it's low price and wide range of tests it can apparently do.

                I'll get around to doing some tests with it this weekend and report back again.
                _______________________________________________

                _______________________________________________

                Comment

                • SeanM
                  Bronze Member

                  • Mar 2018
                  • 120

                  #9
                  Morning Andy

                  Thank you for the on depth feedback so far. Very interested in the update on the testing.

                  Comment

                  • Dave A
                    Site Caretaker

                    • May 2006
                    • 22818

                    #10
                    Originally posted by AndyD
                    Gawd knows what all the black bits are...
                    Flux?
                    (Kinda reminds me of my early soldering days )
                    Participation is voluntary.

                    Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services

                    Comment

                    • AndyD
                      Diamond Member

                      • Jan 2010
                      • 4951

                      #11
                      The photos were taken at around 20X magnification and the black bits aren't really visible to the naked eye.

                      The whole area is covered in residual flux and flux usually comes out of a syringe so it's clean, the black bits are something else entirely. Looking at the board they haven't reflowed using a hot air station so I'd guess it's a build up of burned crap that was on the soldering teezers or pencil iron they used. Maybe they scraped the shellac of the solder pads on the board using the iron or hot tweezers and that resulted in bits of blackened and burned varnish.

                      If it survives the testing regime I have planned for it and I end up keeping the tester I'll probably give the board an hour in the ultrasonic bath.
                      _______________________________________________

                      _______________________________________________

                      Comment

                      • AndyD
                        Diamond Member

                        • Jan 2010
                        • 4951

                        #12
                        Just a note to let you know I haven't forgotten I promised to post some test results. I made some initial tests and all did not go well. I'm in the process of some further investigations which are taking longer than I anticipated.
                        _______________________________________________

                        _______________________________________________

                        Comment

                        • AndyD
                          Diamond Member

                          • Jan 2010
                          • 4951

                          #13
                          Okay, a late update with this unit.

                          All didn't go well. The main reason I was interested in this particular tester was its ability to do 5Amp, 8Amp and 10Amp on-load tests. The tester I bought did none, or rather it did the tests and gave results with dubious accuracy but it didn't introduce a 5, 8 or 10 Amp load whilst it did them. I even tested it it using a high sample rate on an oscilloscope in case it was so fast it was outside the sample rate of my Fluke bench meter but alas nothing.

                          I returned the unit and exchanged it as faulty for another new one. The build quality of the new one was marginally better, it didn't have the black particulates on the board and considerably less residual flux but it still yielded exactly the same results.....or lack of results. I kinda lost interest at this point because I couldn't find any board-view schematics online and I don't have time to start from scratch reverse engineering the circuit to localise the problem(s).

                          This one was a bust unfortunately.
                          _______________________________________________

                          _______________________________________________

                          Comment

                          • Sparks
                            Gold Member

                            • Dec 2009
                            • 909

                            #14
                            Thank you Andy, your contributions are much appreciated.

                            Comment

                            • BobZA
                              Email problem
                              • Oct 2018
                              • 20

                              #15
                              Thanks Andy. Was going to post a question on the build quality of Mastech … but I think you have covered that well. As you say I guess what you pay is what you get ...

                              Comment