Welcome to The Forum SA. As a visitor you have read only access to the public content areas of this website. You will have to register as a member to access all content, post messages and network with our members. Membership is free and registering is quick and easy. You can click here to register now and become a member within minutes.
I am re-designing a shop in a mall. The current geyser is in the ceiling space, and I have to re-position the DB to a position directly underneath the geyser. The ceiling will be removed, and the top of the DB will be approximately 2 m below the drip tray.
Is this allowed? If not, how far and in what direction away from the geyser must I re-position the DB?
I would say that is a no - DB cannot be under the geyser because the chances of the geyser leaking are good even with a drip tray .
The regulations ask you to consider the enviroment in which you are installing and I feel that 5.2.4 basically allows the electrical contractor to say , Not putting it there as I am exposing the DB to possible water damage.
5.3.8 helps even more
6.6.1.2 A distribution board shall comply with the requirements of clause 5.
6.6.1.4 The distribution board shall be suitable for the environmental
conditions in which it operates
6.6.1.7 A distribution board shall not be mounted
c) within a radius of 1 m from a water tap or valve (in the same room),
unless the enclosure provides a degree of protection of at least IP44
5.2.4 Positioning of equipment
Electrical equipment which, under normal conditions will be
a) exposed to flammable or explosive gas, vapour, dust or liquid, or to
external influences such as direct sunlight, corrosive vapour or oil, or
b) in a hazardous location,
shall be so selected or enclosed that it is protected against harmful effects or
it shall comply with the requirements of an applicable standard (or both).
5.3.8 Positioning and accessibility of electrical equipment
d) it is not likely to be physically damaged,
e) dust or moisture is not likely to accumulate on live or other parts and
cause flashover, and
We process personal data about users of our site, through the use of cookies and other technologies, to deliver our services, personalize advertising, and to analyze site activity. We may share certain information about our users with our advertising and analytics partners. For additional details, refer to our Privacy Policy.
By clicking "I AGREE" below, you agree to our Privacy Policy and our personal data processing and cookie practices as described therein. You also acknowledge that this forum may be hosted outside your country and you consent to the collection, storage, and processing of your data in the country where this forum is hosted.