    Cabtyre cabling not allowed in electrical installation

    Good day

    My name is Munnik an i am a installation electrician

    Can someone explain to me why you not allowed to use cabtyre cabling in an electrical installation.

    I have ask many other electrician but no one give me answer that makes sense.

    Thanks in advance
  • GCE
    Platinum Member

    • Jun 2017
    • 1473

    #2
    The SANS 10142 regulation 6.1.11(pasted below ) does not allow you to use flexible cords in an installation would be the easy answer

    The reason behind it I have always understood the insulation is not the same standard as T&E .
    There are flexible cords that are made to higher standards and could be acceptable in the future.But for the time being 6.1.11 applies


    6.1.11 Flexible cords shall not be used as part of the electrical installation,
    except where
    a) required by the relevant product solely for termination or connection of
    moving parts,
    b) specified in the product standard,
    c) used as single cores in conduits,
    d) used in an authorized wiring system (see 3.5), or
    e) needed for the connection of luminaires, provided that each connection is
    limited to one luminaire and to a maximum length of 3 m.

    Comment

    • AndyD
      Diamond Member

      • Jan 2010
      • 4946

      #3
      Flexible cords can be manufactured to far higher specifications than installation cable such as twin and earth, I think the big problem with flexible cords is that they're fine stranded wiring which requires some type of ferrule when it's terminated. Most terminations in electrical accessories and in DB's are designed for the solid type conductors or coarse stranded type conductors which are found in installation cables and aren't suitable for fine stranded wiring.
      _______________________________________________

      _______________________________________________

      Comment

      • bergie
        Email problem

        • Sep 2010
        • 308

        #4
        i wouldnt say db boards are not suited for fine stranded wire. a bootlace ferrule works well.
        maybe its to do with the greater chances of it being abused in an installation. the green yellow earth wire being used as live conductors. i think from 6mm up you can use flexible cable anywhere in an installation.

        Comment

        • Nieuwfam
          New Member
          • Dec 2020
          • 4

          #5
          An old thread, but I note that flexible cord is apparently now allowed in an electrical installation provided colour standards are adhered to and one uses ferrules for terminations.

          6.1.11 Where flexible cords are used as part of the electrical installation, the
          selection, installation and colour identification (see 6.3.3) shall be done in
          accordance with this part of the standard.
          6.1.12 Where flexible cords are used, the strands of the conductors shall be
          mechanically protected with ferrules to prevent the strands from being cut off
          in terminations.

          No mention of maximum length. So you only need to mark the blue wire with black tape / sleeve and use ferrules for terminations?

          I quoted the draft regulations, so apologies if this was not applied in the published version and please correct me if I have the wrong end of the stick.

          Keep safe

          Comment

          • Dave A
            Site Caretaker

            • May 2006
            • 22810

            #6
            Originally posted by Nieuwfam
            An old thread, but I note that flexible cord is apparently now allowed in an electrical installation provided colour standards are adhered to and one uses ferrules for terminations.

            6.1.11 Where flexible cords are used as part of the electrical installation, the
            selection, installation and colour identification (see 6.3.3) shall be done in
            accordance with this part of the standard.
            6.1.12 Where flexible cords are used, the strands of the conductors shall be
            mechanically protected with ferrules to prevent the strands from being cut off
            in terminations.

            No mention of maximum length. So you only need to mark the blue wire with black tape / sleeve and use ferrules for terminations?

            I quoted the draft regulations, so apologies if this was not applied in the published version and please correct me if I have the wrong end of the stick.

            Keep safe
            You are correct. The change was introduced in Edition 3. Effective date of publication appears to be 27th July 2020.