Electrical certificate of Compliance where there is no supply from municipality
  • Tamao1035
    • May 2019
    Hi all, there's a project where they are building low cost houses but there is no electrical network or no supply to to the houses, can one issue a COC for the houses?
    • 1495
    In theory you cannot issue a coc for work that does not have power as you will not be able to carry out all the tests .Any COC with generator is only valid with that generator connected , the minute a different generator is connected your power source has changed and you need to retest.
    Being a government type project - In practice you need to do a coc with generator power so that you can submit with your invoice and get paid. Also make sure that you have a witness from the builder or client that signs off that all the electrical was working. I am assuming they have a practical completion at some stage on a block of houses. State on the COC the make and serial number of the generator to prevent problems later
    If you have a witness then at least later if everything is stolen they cannot turn around and say that they never saw it operational and then try and force you to redo at your own cost.
    The generator may be able to be claimed as a separate cost depending on the contract data and information at tender stage .
    We went through a similar situation at a service center for a municipality - Tested with generator , got consultants out there at night to ensure that everybody witness the exterior lighting was operational around the building etc.
    Years later when they finally got power to site there was not a wire left and they had to pay to have it redone
    Use the COC to cover yourself
    • eugene mhlongo
      • Jan 2017
      • 4
      In this case where the generator is used for a coc, how to get loop impedence and pscc
        • 1495
        Your loop can be measure but should basically be zero as your neutral earth bridge point will be on the genset
        PSCC - will not be more than 1,5 times the rating of the generator unless the motor is to big for the alternator - Generally if you go over the 1,5 times of a generator rated current the generator will stall which will be the max prospective short circuit current.
        Likewise for inverters etc , they all have electronic cut offs