Welcome to The Forum SA. As a visitor you have read only access to the public content areas of this website. You will have to register as a member to access all content, post messages and network with our members. Membership is free and registering is quick and easy. You can click here to register now and become a member within minutes.
Good day. I read a few threads back but can't find a related one.
How many plug circuits may be connected to a 20A breaker?. In other words, may you have two 2.5mm wires connected to the bottom of a breaker that feeds plugs? What does regulation say. Thanks in advance.
On 20 Amp and 2,5sqmm I would say max 3 - You still need to watch that you circuit will not exceed the 5Kw load state somewhere in the code and there is also a restriction on neutrals and earths .
Pasted the 2 relevant regs below
6.1.5 A maximum of three conductors may be connected to any one
terminal provided that the terminal has the correct rating.
6.6.1.11 If a conductor of cross-sectional area exceeding 4 mm2 is used, it
shall be so installed to allow any one neutral conductor to be disconnected
without disturbing the connection of any other neutral conductor
We process personal data about users of our site, through the use of cookies and other technologies, to deliver our services, personalize advertising, and to analyze site activity. We may share certain information about our users with our advertising and analytics partners. For additional details, refer to our Privacy Policy.
By clicking "I AGREE" below, you agree to our Privacy Policy and our personal data processing and cookie practices as described therein. You also acknowledge that this forum may be hosted outside your country and you consent to the collection, storage, and processing of your data in the country where this forum is hosted.