    Ceiling fan tripping earth leakage.

    Hi All

    Maybe someone can explain theoretically why the following occurs.

    First time I've experienced the following:

    A ceiling fan is tripping the earth leakage relay only the moment it is switched off.
    It can run for hours on end without a problem, but the moment you switch it off, the earth leakage trips.

    Maybe someone can explain what is happening here.

    Regards ... Derek
  • adrianh
    Diamond Member

    • Mar 2010
    • 6328

    #2
    I would think that when the circuit is broken a couple of things might happen:
    1. There would be a spark in the switch causing a transient into the motor coil.
    2. That transient may be high enough to to cause a short in a moist or already compromised environment.

    Maybe one of your motor coils has failed.

    I had a similar thing with one of my CNC machines. It would run happily for hours on end and only trip when I turn the main power off. After much stuffing about and replacing many components did it come to light that the coolant pump had failed and I suppose the excessive magnetic field built up in the motor coil with the addition of the switch opening transient field was enough to short the pump to ground.

    Dunno - may be I am talking rubbish but it seems to be the only thing that makes sense.

    Comment

    • AndyD
      Diamond Member

      • Jan 2010
      • 4951

      #3
      There may be high standing leakage from other circuits and the arc caused when you switch the ceiling fan off is enough to cause tripping.
      _______________________________________________

      _______________________________________________

      Comment

      • Derlyn
        Platinum Member
        • Mar 2019
        • 1761

        #4
        Bit of feedback.

        Definately a fault with the fan.

        There are another 5 fans on the same circuit and it's only this one causing the earth leakage to trip.

        Have megger tested it ok. infinity .

        Have removed the fan and replaced it with another ( same make and model ) ..... problem solved, but it still remains a mystery why.

        Will start playing around with it in the workshop when time permits.

        Regards ... Derek

        Comment

        • ians
          Diamond Member

          • Apr 2010
          • 3943

          #5
          IF you have done an insulation resistance test and it is clear ...my guess would be one of the capacitors are faulty... (without actually checking the fan it would be just that ...a wild guess) or a pinched wire...this is why i have a current leakage tester.
          Comments are based on opinion...not always facts....that's why people use an alias.

          Comment

          • AndyD
            Diamond Member

            • Jan 2010
            • 4951

            #6
            Earth leakage breakers can be a bit skittish. I had issues with one that used to trip every evening when the council street lights switched on. They can be a bit sensitive to phase angle fluctuations upstream as well as downstream especially with switching of highly capacitive or highly inductive loads. Usually a different brand of earth leakage breaker sorts it out but in your case it was probably just easier to replace the fan.
            _______________________________________________

            _______________________________________________

            Comment

            • adrianh
              Diamond Member

              • Mar 2010
              • 6328

              #7
              Originally posted by AndyD
              Earth leakage breakers can be a bit skittish. I had issues with one that used to trip every evening when the council street lights switched on. They can be a bit sensitive to phase angle fluctuations upstream as well as downstream especially with switching of highly capacitive or highly inductive loads. Usually a different brand of earth leakage breaker sorts it out but in your case it was probably just easier to replace the fan.
              Next time I will ask you first before speaking a lot of $h1T :-)

              Comment

              • ians
                Diamond Member

                • Apr 2010
                • 3943

                #8
                Originally posted by adrianh
                Next time I will ask you first before speaking a lot of $h1T :-)
                Actually your statement is not total bullshyte...nobody really knows the real answer unless a variety of tests are done using the correct equipment.

                Comments made on a social media platform are merely suggestions.

                Andy is also correct in what he stated... i wouldnt total agree with his statement ...but as i mentioned they merely suggestions.
                Comments are based on opinion...not always facts....that's why people use an alias.

                Comment

                • adrianh
                  Diamond Member

                  • Mar 2010
                  • 6328

                  #9
                  Originally posted by ians
                  Actually your statement is not total bullshyte...nobody really knows the real answer unless a variety of tests are done using the correct equipment.

                  Comments made on a social media platform are merely suggestions.

                  Andy is also correct in what he stated... i wouldnt total agree with his statement ...but as i mentioned they merely suggestions.
                  Well I can tell you, sometimes the answer that solves a problem is really odd. I did a roughing toolpath on a cnc job last week and it was perfect. So I saved the file to a new revision today and made some alterations to the part. (made it a bit longer and added some elements) The CAM sotfware refused point blank to create the roughing path correctly. It would simply ignore large parts of the geometry. I spent many hours faffing with it - making al the parts nurbs, then nubs and meshes, then just a big mesh and and and.... I compared to the old revision and everything is correct (stock, bounding geometry etc). Then I turned the entire thing 90 degrees....Now the damn thing works perfectly. I have absolutely no idea why the stupid thing likes the drawing better landscape than portrait. It doesn't matter because I will place the stock accordingly. The point that I am trying to make is that the solution to the problem is totally irrational though it seems to be the only thing that works.

                  Comment

                  • Derlyn
                    Platinum Member
                    • Mar 2019
                    • 1761

                    #10
                    Hi All

                    A bit of feedback.

                    Meggered the motor. Result infinity.

                    Connected the fan in my workshop and tested.

                    Turned it on and off a couple of times ..... no problem.
                    Left it running for an hour. When I turned it off, the earth leakage tripped.

                    While the motor was still warm, I meggered it again and found the reading to be lower than when the motor was cold. 1,5 megs.

                    The insulation resistance is reducing with an increase in temperature.

                    I am aware that the earth leakage should only start tripping when the insulation resistance is approx 8k or lower, but I suppose the reduction in insulation resistance combined with the arc from the switch does something that causes enough current to earth to trip the earth leakage.

                    I still don't fully understand the theory behind it, but I now know that it's the fan that's faulty.

                    Derek

                    Comment

                    • ians
                      Diamond Member

                      • Apr 2010
                      • 3943

                      #11
                      Originally posted by Derlyn
                      Hi All

                      A bit of feedback.

                      Meggered the motor. Result infinity.

                      Connected the fan in my workshop and tested.

                      Turned it on and off a couple of times ..... no problem.
                      Left it running for an hour. When I turned it off, the earth leakage tripped.

                      While the motor was still warm, I meggered it again and found the reading to be lower than when the motor was cold. 1,5 megs.

                      The insulation resistance is reducing with an increase in temperature.

                      I am aware that the earth leakage should only start tripping when the insulation resistance is approx 8k or lower, but I suppose the reduction in insulation resistance combined with the arc from the switch does something that causes enough current to earth to trip the earth leakage.

                      I still don't fully understand the theory behind it, but I now know that it's the fan that's faulty.

                      Derek
                      Until you actually find the fault... you will never know....how does the saying go... clutching at straws.

                      something to consider...the motor turns...its hanging on a shaft... wiring gets warm (even if it doesnt get warm)...as the motor stops...the wiring shorts on the frame ...e/l trips...i would bet money on the neutral being the cause of problem.

                      The wires are always squashed through the tubes and out through a hole into a connector block... do you have a leakage current clamp?

                      if not...hang the fan ...connect the insulation resistance tester set to 1000 volts ...shake the bottom of the fan and see if the reading drops while doing this.
                      Comments are based on opinion...not always facts....that's why people use an alias.

                      Comment

                      • natal21
                        Email problem
                        • Oct 2011
                        • 12

                        #12
                        Originally posted by Derlyn
                        Hi All

                        A bit of feedback.

                        Meggered the motor. Result infinity.

                        Connected the fan in my workshop and tested.

                        Turned it on and off a couple of times ..... no problem.
                        Left it running for an hour. When I turned it off, the earth leakage tripped.

                        While the motor was still warm, I meggered it again and found the reading to be lower than when the motor was cold. 1,5 megs.

                        The insulation resistance is reducing with an increase in temperature.

                        I am aware that the earth leakage should only start tripping when the insulation resistance is approx 8k or lower, but I suppose the reduction in insulation resistance combined with the arc from the switch does something that causes enough current to earth to trip the earth leakage.

                        I still don't fully understand the theory behind it, but I now know that it's the fan that's faulty.

                        Derek
                        This is why i always said , "electricity is a mix of science and magic"

                        Comment

                        • Polycab
                          New Member
                          • Feb 2021
                          • 1

                          #13
                          Hello, There

                          Ceiling fan tripping earth leakage may be it is happen due to the poor wiring or also due to the earthing problem in house. One of the simplest grounding problems to fix is making sure that all ground connections are correct.