Hi guys. Is there anything restricting me to use a 20A orange toggle for a plug circuit. Circuit is generaly pulling 18A but when fridge or freezer start it goes over 20A and trip the mcb
Orange toggle
Collapse
X
-
Tags: None
-
Orange lever switches have a slow tripping curve. Therefore it would take longer to trip than a normal white lever switch especially under fault conditions.
If your MCB (that should have a higher rating) trips before the 20A CB for the plug circuit trips you might have a faulty MCB or the total load on the MCB is too much.Last edited by Lourens.dL; 12-Jan-20, 12:02 AM. -
If your circuit is wired with 2,5mm sq wire, you can use a 25A mcb.
Cheers and peace out ... DerekComment
-
Participation is voluntary.
Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene ServicesComment
-
Comment
-
Hi guys. I still do not see the reg. stating that orange toggles are not allowed to protect plug circuits. My problem is a plug circuit witch were wired with twin and earth(chased directly in wall) and drawing to close to mcb max. I know that 2,5mm cables can draw more then 20A depending on installation method and the mcb rating of a plug circuit may not exceed 125% of the socket rating. So a 20A orange toggle can go up to 25A for a very limited time. I have seen aircons feeding from plug circuits witch are protected with orange toggle mcb's. I do not want to install the orange toggle(witch will solve my problem) if it is ileagal.Comment
-
Orange...curve 1...D curve breakers are designed specifically for this type of application.
Do some research into circuit breakers and you will find that curve 1 ...2 and 3 have specific applications.
All boils down to design and application.Comments are based on opinion...not always facts....that's why people use an alias.Comment