    Section 7.12 Alternate supplies

    It seems the way forward is going to be solar instalations ... if you are not on the band wagon ... it might be a good idea to climb on.

    Which brings me to why i started this thread ... section 7.12

    I have been in discussion with other electricians ... about the specs ... it seems there are a few challenges they face when more than one installer/electrician completes and installtion

    So lets go through 7.12 and see why everyone cant just be happy.

    "Note 2 this part of SANS 1042 does not cover the supply to an installtion that functions in parrallel with the main supply (co generation)"

    Do I understand this correctly ... solar panels using a grid tied inverter would be regarded as working in parralel?

    by the way this thread is not to point fingers ... but rather create an understanding of the regs.
    Comments are based on opinion...not always facts....that's why people use an alias.
  • ians
    Diamond Member

    • Apr 2010
    • 3943

    #2
    7.12.2.1 - Notices and audible or visible power on indicators.

    A very important part of an alternate source of supply ... something I believe people dont pay enough attention to ... the details and correct location of the notice.
    Comments are based on opinion...not always facts....that's why people use an alias.

    Comment

    • GCE
      Platinum Member
      • Jun 2017
      • 1495

      #3
      Originally posted by ians
      "Note 2 this part of SANS 1042 does not cover the supply to an installtion that functions in parrallel with the main supply (co generation)"

      Do I understand this correctly ... solar panels using a grid tied inverter would be regarded as working in parralel?
      Grid tie would be parallel to the supply - The regulations covering co generation are published by NERSA and there are also municipal bylaws based on NERSA regulations.

      The Grid tie inverters are manufactured to specific requirements as per SANS regulations

      Sans 10142 is making you aware that there are other regulations to go look at - There is still talk of having a separate 10142 part 3 for solar

      Comment

      • ians
        Diamond Member

        • Apr 2010
        • 3943

        #4
        "Supplier" ... the day you switch on the solar system ...you the installer have now beome the "supplier" what does this mean to joe soap who installed the solar panel ? The first question i always ask ... is your insurance company happy with the documentation provided with the SANS approval for the product installed and the test results carried out by the suitably qualified installer ?

        It seems that some feel that if you go "off grid" no rules and regulations apply to the off grid system on the property ... this is something people need to be aware of ... the implications if something goes wrong.

        The days of installing a UPS next to a PC or a plug and play inverter on wheels are long gone ... and so have the regulations related to those units ... alternate supplies have become the new must have ... not only to save on your electricity bill but to generate your own elelctricity ... unfortunately with it comes the DIY enthusiast ...the people who know just enough to mount a panel and run a cable from the panel to a box and connect and configue the software ... like gate installers ... aircon techs ... alarm techs etc. Some of these installers and technicians have specialised in that field and know their stuf ... so credit to them.

        My concern with alternate supplies is the danger ... anyone can fit a socket outlet ... connect a motor ... install a generator or solar panel and inverter ... however the reason there is an SANS 10142-1 code is for the protection of people, animals and property.

        I believe alternate supplies should be an entire section on its own with additional requirements ... for example an additional section or attachment to a COC which requires training and certification. A single phase or installation tester will not be able to sign off a COC unless they have passed a test and been certified ... this includes master elctricians like myself ... new technology requires new training ... like an engineer ...we should have to get credits ... to ensure we keep up to date with technology and new regulations.

        Alternate supplies are growing fast and this industry requires urgent attention.
        Comments are based on opinion...not always facts....that's why people use an alias.

        Comment

        • ians
          Diamond Member

          • Apr 2010
          • 3943

          #5
          I find the easiest way to educate people is to share installations already completed run through how the installtion was done and some of the challenges or sketch up something and ask questions.
          Comments are based on opinion...not always facts....that's why people use an alias.

          Comment

          • ians
            Diamond Member

            • Apr 2010
            • 3943

            #6
            neutral bar earthing :

            "operation of protection devices shal not rely upon the connection to the earth point"

            Taking a copper coated steel rod ... hitting it into the ground and bolting it to the metal frame of the generator does NOT mean you have an earth elctrode installed ... it has to be done in accrodance with SANS 10199.

            Look at me getting all technical ...Where is Andy with his detailed technical responses?

            What makes you think i am heading in this direction ... the alternate supplies industry is the way forward... I even heard a comment about giving pensioners solar power to help them reduce their electricity bills ... maybe this the route forward with my new venture ... offer reduced rates and or free installations for old people ...people enjoy a feel good story.
            Comments are based on opinion...not always facts....that's why people use an alias.

            Comment

            • Justloadit
              Diamond Member
              • Nov 2010
              • 3517

              #7
              I have had a few pensioners telling me that you can not use a solar PV panel to heat water, only the thermal works.
              Go figure this one out.
              My system has been working for the last 5 years heating up water electrically using PV panels.

              With the reduced cost of PV panels today this is the way to go. Once you heated your water, you could divert the available energy to charge batteries or run grid tied inverters.
              Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
              Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

              Comment

              • ians
                Diamond Member

                • Apr 2010
                • 3943

                #8
                Originally posted by Justloadit
                I have had a few pensioners telling me that you can not use a solar PV panel to heat water, only the thermal works.
                Go figure this one out.
                My system has been working for the last 5 years heating up water electrically using PV panels.

                With the reduced cost of PV panels today this is the way to go. Once you heated your water, you could divert the available energy to charge batteries or run grid tied inverters.
                I am thinking about going this route ... i was going to look at installing gas ... but them you still have to buy gas .. solar is free ... setup the system to be super efficient and the running cost should be a low.

                I have been spending a lot of time researching solar ... my goal is to create a method to start off with the basics and expand as the budget allows ... i am not big on debt ...and to install a basic system with batteries is gona cost around R30k ... which i dont have floating around ... panels are the cheap part ... so it looks like we are going to star twith a few panels and a grid tied inverter ... then as it grows add a hybrid and lithium batteries ... hopefully batteries will also start dropping in price as the demand increases and technology advances.

                Solar start becoming an cost saving option when you run your bussines from home ... which i do ... and we have a small baking operation ... which requires drying product in the oven for hours... a little smart planning and the drying could be done between 9 am and 3 pm.
                Comments are based on opinion...not always facts....that's why people use an alias.

                Comment

                • Rifrug
                  Full Member

                  • Nov 2019
                  • 70

                  #9
                  Solar used to be a luxury but for me it has become more of a necessity, because being switched off at any moment and running the security risk of alarm system failure or gate motor failure that can cost dearly is no joke, so when considering the problems associated with not having electricity it becomes a gamble to not install backup, and considering the different types of backup solar comes out very expensive but might be the cheapest on the long run when it is utilized as much as possible to try and recover some cost.
                  I did my own install and must admit I had to read allot about solar and try to incorporate my electrical knowledge as I could not find the basic regulations for solar and I even had to redo certain parts of my solar installation as I learn and gain more knowledge. Solar is probably the future especially when it comes to new buildings and homes, I think it makes more sense to design to be off-grid as the utility supplier is in deep trouble and we are now starting to pay even for their darkness.

                  Comment

                  • ians
                    Diamond Member

                    • Apr 2010
                    • 3943

                    #10
                    An example: Share your thoughts on how you would tackle it... with a smuch detail as possible.

                    A standard 3 bedroom house with single phase DB (to keep it simple)

                    24 way din DB

                    60 amp single phase main switch
                    60 amp single phase earth leakage
                    2 x 30 amp single phase mcb (hob and ELO)
                    20 amp geyser combo
                    2 x 20 amp (plugs)
                    2 x 10 amp (lights)

                    A 5 kva petrol generator with an ATS (generator checked and not V-O-V)

                    1 plug and 1 light circuit to connect via the ATS

                    This is how i would do it.

                    I would fit the ATS as close to the main DB as possible.

                    Replace one of the plug circuit with a D curve mcb

                    Clip 2 blanks on the right of the mcbs ... then a din mount panel light (to indicate the power is on)... then an earth leakage unit ...then a 20 amp mcb ... then a 10 amp mcb.

                    make up a flexible cable with a female socket (coupler) and connect it directly to the generator (bypass the sockets provided)

                    make up another flexible cable with male socket (coupler) connected to a double isolator mounted next to the generator.

                    Run a cable from the isolator to the ATS

                    Run a 4 core + e cable from the DB to the ATS 2 cores used for supply and 2 for return to the DB and the earth connected the the ground on the ATS.

                    Labels

                    generator - for the D cuve breaker.

                    Alternate supply fed from the generator - above the generator circuits.

                    generator power on - above the din mounted light.

                    earth leakage unit - for the e/l

                    plugs - plugs.

                    lights for lights.

                    The neutral and earth linked in the ATS panel.

                    A spike next to the genrator (using a 6 mm wire)
                    Comments are based on opinion...not always facts....that's why people use an alias.

                    Comment

                    • Rifrug
                      Full Member

                      • Nov 2019
                      • 70

                      #11
                      7.12.2.1 - Notices and audible or visible power on indicators.
                      I did not install visible power on indicators because my prepaid meter is right next to my DB with a light display when “Eskom is on” it is light up and also an inverter keypad right next to the prepaid with a light display when inverter is on. I did not see the need to install more lights due to these visible displays but am wondering if the displays could be regarded as visible indicators. I did then label the DB to warn of “Alternate solar supply “ any advise on my scenario?

                      Comment

                      • Rifrug
                        Full Member

                        • Nov 2019
                        • 70

                        #12
                        Alternate supplies are growing fast and this industry requires urgent attention.

                        I have came across installers doing complete solar installations with very little knoledge of the SANS wiring code. They then get an installation electrician to come and install just the change over switch. The electrician than issue a C.O.C. for that C/O switch and the installer switch on the solar as if all is compliant. This to me is a gray area as to what regulations were followed doing the dc wiring, circuits and fuse ratings on batteries and pv panels.

                        Comment

                        • ians
                          Diamond Member

                          • Apr 2010
                          • 3943

                          #13
                          Originally posted by Rifrug
                          Alternate supplies are growing fast and this industry requires urgent attention.

                          I have came across installers doing complete solar installations with very little knoledge of the SANS wiring code. They then get an installation electrician to come and install just the change over switch. The electrician than issue a C.O.C. for that C/O switch and the installer switch on the solar as if all is compliant. This to me is a gray area as to what regulations were followed doing the dc wiring, circuits and fuse ratings on batteries and pv panels.
                          There is an even better way to do it ... you do the full installation ...install an electric fence ... fit a gas oven a ... do all those alterations around the house ... then tell everyone you are putting the house up for sale ... contact a company which specialises in COC's ... get them to do a full inspection report and COC for the entire installation
                          Comments are based on opinion...not always facts....that's why people use an alias.

                          Comment

                          • ians
                            Diamond Member

                            • Apr 2010
                            • 3943

                            #14
                            As per image on pg 359 of the sans book ... do you install physical barriers between the normal and eseential supply or do you just leave a gap between the breakers?

                            or do you install a 2 level DB one for normal and one for essential?
                            Comments are based on opinion...not always facts....that's why people use an alias.

                            Comment

                            • Rifrug
                              Full Member

                              • Nov 2019
                              • 70

                              #15
                              Originally posted by ians
                              As per image on pg 359 of the sans book ... do you install physical barriers between the normal and eseential supply or do you just leave a gap between the breakers?

                              or do you install a 2 level DB one for normal and one for essential?
                              To my understanding there should be a physical barrier between the different supplies, It would be even better if they could be in different DB’s but the aesthetics become a factor when the DB is inside a main living room or undesired area, who appreciates clusters of DB’s in a home. Also to install a separate DB for four little switches become uneconomical so my preference in a home would be towards installing a physical barrier between supplies if it has adequate space, and ensure that it is clearly labelled with warning signs.