P2 change over switch diagram pg344 Sans10142-1:2020 edition 3

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • melvinbrucepaton
    New Member
    • Nov 2011
    • 6

    #1

    P2 change over switch diagram pg344 Sans10142-1:2020 edition 3

    Hi

    Who actually installs a change over switch as per P2 change over switch diagram pg344 Sans10142-1:2020 edition 3.
    I never come across a installation like the diagram.
    I usually find the change over switch installed below the mains above the earth leakage.

    So my question is this legal? As far as i can see it still provides all the necessary protection.

    your thoughts?
  • melvinbrucepaton
    New Member
    • Nov 2011
    • 6

    #2

    Comment

    • Rifrug
      Full Member

      • Nov 2019
      • 70

      #3
      I have installed very similar as to the SANS drawing, I did not realize it until I had a closer look, only difference on mine is, an extra changeover switch for a third section called : Non-essential. Thereby I have three split neutrals with three earth leakages.
      1.- Normal section for Eskom only-geyser, dishwasher, stove etc. (no battery backup)
      2.- Non-essential for tv’s, kettle, fridges and all small power plugs (battery backup option if battery capacity is ok, these are load-shed if battery’s are running low)
      3.- Essential for CCTV, Alarms, gate motor, Wifi, lights, 1xTV only (Always on backup)
      Very few people wire their DB’s this way but I find it very convenient and it functions very well.
      Regards Rifrug

      Comment

      • Rifrug
        Full Member

        • Nov 2019
        • 70

        #4
        The only unclear part is the earthing, SANS show the bonding of alternate supply earth and consumers earth. They do not show a earth spike which I would think is necessarily if you were taught that all conductors should originate from the same point. That would mean creating a alternative earth with a good earth resistance as close as possible to the generator or solar inverter and not relying on a utility earth that might be hundreds of meters away. Please correct me if I’m not seeing something as I’m always learning something.

        Comment

        • ians
          Diamond Member

          • Apr 2010
          • 3943

          #5
          Originally posted by melvinbrucepaton
          It is exactly the same as page 359 SANS 10142-1:2017 edition 2
          Comments are based on opinion...not always facts....that's why people use an alias.