    [Question] One of the weirdest faults I have found

    Friend of mine mentions that the place he is staying in has a earth leakage that he thinks is not working right. So I am there but have no tools and he at least has a semi decent multi meter. I press the test button as he has done and it trips. Reset it and try again - nothing. Ok. Easiest way to test earth leakage undo everything at the bottom and take a piece of wire and touch from neutral to earth. Doesn’t trip but creates a small arc. I think to myself ok thats not right. Take the multimeter and test. I get the full 230v between the neutral and earth after the earth leakage but before the earth leakage its round about 10v. Not knowing if his tester is ok or not I get a normal cfl bulb and touch one point to the metal casing and the other one to my wire. It lights up but flickers. I then disconnect the neutral at the top of the earth leakage and connect a wire from the earth bar to the top of the earth leakage and do the same touching the cable from the bottom (which now should be a earth) to the one point of the lamp and the other point to the metal of the db which i did check was connected to the earth bar. It lit up ! What is going on here ? How can I get a voltage thats strong enough to light up a lamp between earth and earth by just passing it trough the earth leakage ? I reconnected everything as I found and told him to be very careful until I can have a decent look at just what is causing this strange fault.
  • Justloadit
    Diamond Member

    • Nov 2010
    • 3518

    #2
    I have had a similar situation, but not with earth leakage, but a three phase motor starter and screw on overload, the type where you have to screw the overload to the base plate, as it was a large contactor & overload.

    There was a small current flowing between the phases and earth, not through the contactor, but through the overload.
    Not sure the reason this was occurring, but took a while to figure out. Once I replaced the overload, problem went away.
    I must say that I never broke open the overload, too busy at the time to inspect.

    There could be a number of explanations.
    This was on a golf course who are always watering the turf using sprinklers, so humidity could have gotten into the DB board, and finally settled with in the Overload enclosure.
    There could have been insects with in the overload, which eventual got electrocuted and remained in the position causing a carbon track. Seen a number of these on PCBs I repaired.
    There could have been overload trips over time, which created a carbon path, which eventually lead to the base and earth.
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

    Comment

    • AndyD
      Diamond Member

      • Jan 2010
      • 4946

      #3
      Originally posted by JustJohann
      Friend of mine mentions that the place he is staying in has a earth leakage that he thinks is not working right. So I am there but have no tools and he at least has a semi decent multi meter. I press the test button as he has done and it trips. Reset it and try again - nothing. Ok. Easiest way to test earth leakage undo everything at the bottom and take a piece of wire and touch from neutral to earth. Doesn’t trip but creates a small arc. I think to myself ok thats not right. Take the multimeter and test. I get the full 230v between the neutral and earth after the earth leakage but before the earth leakage its round about 10v. Not knowing if his tester is ok or not I get a normal cfl bulb and touch one point to the metal casing and the other one to my wire. It lights up but flickers.
      Shorting the neutral on the load side of the earth leakage to earth only usually causes tripping if there's current flow through the earth leakage.

      Some earth leakage units have internal electronics that draw a few microamps so it's possible when you disconnect the neutral on the load side it will appear to be at 230 volts on the empty neutral terminal to a digital tester that has an input impedance somewhere in the megaohm range. This would also probable be enough current to charge up the input capacitor on the CFL ballast to the point where it discharges intermittantly causing the tube to strike momentarily whils it drains....hence the flicker.

      The 10 volts on the supply side of the earth leakage is probably just the neutral-earth voltage of the installation.

      Originally posted by JustJohann
      I then disconnect the neutral at the top of the earth leakage and connect a wire from the earth bar to the top of the earth leakage and do the same touching the cable from the bottom (which now should be a earth) to the one point of the lamp and the other point to the metal of the db which i did check was connected to the earth bar. It lit up ! What is going on here ? How can I get a voltage thats strong enough to light up a lamp between earth and earth by just passing it trough the earth leakage ? I reconnected everything as I found and told him to be very careful until I can have a decent look at just what is causing this strange fault.
      Again, the 10v neutral earth voltage might have been sufficient to charge up the input capacitor on the CFL ballast.

      The tests you're doing are highly unorthodox and the results are misleading. I'd advise against doing these kinds of tests because they'll run you around in circles chasing faults that don't exist. Bottom line is if the earth leakage has a supply connected to it and it doesn't trip when the test button is pressed then just replace it with a new one.
      _______________________________________________

      _______________________________________________

      Comment

      • Derlyn
        Platinum Member

        • Mar 2019
        • 1748

        #4
        Originally posted by AndyD
        Shorting the neutral on the load side of the earth leakage to earth only usually causes tripping if there's current flow through the earth leakage.
        Hell, am I glad there is at least one person who agrees with me. Said the same thing a couple of months back on this same forum and was basically told that I'm talking rubbish.

        Peace out .. Derek

        Comment

        • Dave A
          Site Caretaker

          • May 2006
          • 22812

          #5
          Originally posted by Derlyn
          Hell, am I glad there is at least one person who agrees with me. Said the same thing a couple of months back on this same forum and was basically told that I'm talking rubbish.
          And I had considered quoting your point on that one
          But thought I would leave it to you...

          Don't worry - I had taken notice when you raised the issue. Not all seed falls on stony ground.
          Participation is voluntary.

          Alcocks Electrical Services | Alcocks Pest Control & Entomological Services | Alcocks Hygiene Services

          Comment

          • ians
            Diamond Member

            • Apr 2010
            • 3943

            #6
            Originally posted by AndyD
            Shorting the neutral on the load side of the earth leakage to earth only usually causes tripping if there's current flow through the earth leakage.
            Excuse my ignorance ... when you touch a neutral wire and earth wire .... doesnt it generate a small current due to the circuit/wire resistance etc ?

            I have a nother one of these issues i am trying to understand ... I have a transformer which has only terminals 0 - 230 - 380 ... used for the control circuit in a machine and to run a cooling fan ... dont want to hijack this thread ... so i will start another thread ... someone mentioned an autotransfomer.
            Comments are based on opinion...not always facts....that's why people use an alias.

            Comment

            • AndyD
              Diamond Member

              • Jan 2010
              • 4946

              #7
              An earth leakage works very similar to using a clamp meter around the live and the neutral wires of a circuit simultaneously, what it sees is the difference in current flowing in the two wires. If there's no load on the circuits there would be zero Amps flowing in the live wire and (assuming an ideal world) if there's no voltage difference between the neutral and earth then shorting the neutral to earth won't result in any current flowing. So there's no current on the live, no current on the neutral, the difference in current between the live and neutral is zero as well hence the earth leakage shouldn't trip.
              _______________________________________________

              _______________________________________________

              Comment

              • Justloadit
                Diamond Member

                • Nov 2010
                • 3518

                #8
                Originally posted by AndyD
                An earth leakage works very similar to using a clamp meter around the live and the neutral wires of a circuit simultaneously, what it sees is the difference in current flowing in the two wires. If there's no load on the circuits there would be zero Amps flowing in the live wire and (assuming an ideal world) if there's no voltage difference between the neutral and earth then shorting the neutral to earth won't result in any current flowing. So there's no current on the live, no current on the neutral, the difference in current between the live and neutral is zero as well hence the earth leakage shouldn't trip.
                True, however if there are some big loads running, then shorting the Neutral to Earth may cause another smaller current path to the Neutral of the transformer supply through Earth, unbalancing the L/N current that the Earth Leakage is sensing and may trip the ELU if greater than 20mA.
                Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
                Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

                Comment

                • ians
                  Diamond Member

                  • Apr 2010
                  • 3943

                  #9
                  Originally posted by AndyD
                  An earth leakage works very similar to using a clamp meter around the live and the neutral wires of a circuit simultaneously, what it sees is the difference in current flowing in the two wires. If there's no load on the circuits there would be zero Amps flowing in the live wire and (assuming an ideal world) if there's no voltage difference between the neutral and earth then shorting the neutral to earth won't result in any current flowing. So there's no current on the live, no current on the neutral, the difference in current between the live and neutral is zero as well hence the earth leakage shouldn't trip.

                  So i went into my workshop and found 4 earth leakage units CBI and clipsal connected 1 at a time.

                  No wires out the bottom ... no load (current) ... no resistance ... "ideal world" ... imagine that every single earth leakage unit trips as i touch the neutral to earth.

                  Derek or anyone else for that matter please prove me wrong by posting a video of you touching a neutral wire to earth that doesnt trip ... still waiting for the video promised months ago.

                  We all understand the theory behind earth leakages and ohms law.
                  Comments are based on opinion...not always facts....that's why people use an alias.

                  Comment

                  • ians
                    Diamond Member

                    • Apr 2010
                    • 3943

                    #10
                    Originally posted by Dave A
                    And I had considered quoting your point on that one
                    But thought I would leave it to you...

                    Don't worry - I had taken notice when you raised the issue. Not all seed falls on stony ground.
                    Have you got your "sparkies" to try it yet ... Hopefully you can post a video for us ? I will even drive to your workshop to see it in the flesh
                    Comments are based on opinion...not always facts....that's why people use an alias.

                    Comment

                    • Derlyn
                      Platinum Member

                      • Mar 2019
                      • 1748

                      #11
                      Hi Ian. Made the video as promised. I am a man of my word.

                      Only then did I find out how long it takes to upload to youtube.

                      If anyone is interested, Ian you too, I will whattsapp it to you if you send me a number.

                      Or if there is anyone who can advise me of a quicker way of sharing it, I would appreciate it.

                      I can be contacted on derlyn700@gmail.com or 082 557 4099.
                      Nothing to hide, brother.

                      Peace out .. Derek.
                      Last edited by Derlyn; 13-Oct-20, 05:09 PM.

                      Comment

                      • ians
                        Diamond Member

                        • Apr 2010
                        • 3943

                        #12
                        I connected my leakage current clamp to the wire to the earth wire and touched the neutral with no other wires connected ... it displays 14 mA and trips ( i do beleive this reading would be higher if the meater had a faster response time) ... which indicates that it creates a current large enough to trip the earth leakage (by the way i used a really short lead to reduce resistance) ...so back to drawing board.

                        I could post 2 videos of earth leakage units not tripping ... both ... the test button didnt trip the units nor did the earth leakage tester.
                        Comments are based on opinion...not always facts....that's why people use an alias.

                        Comment

                        • Derlyn
                          Platinum Member

                          • Mar 2019
                          • 1748

                          #13
                          Sorry email is derlyn700@gmail.com

                          Comment

                          • ians
                            Diamond Member

                            • Apr 2010
                            • 3943

                            #14
                            Someething else which has got me thinking ... M&G earth leakage units ...I wish I had a spare one ... had to use it for a job which had a complicated earth leakage issue ... on that site the earth leakage units I installed would just trip randomly ... it could take a day or 2 months ... eventually i took the M&G unit and installed it on site ... as i switched on it tripped ... tried again ...just tripped .. eventually i found the cause and repiared it.

                            I need to setup a plug and connect the fluke 1650 ... to see the trip current and response time of the units i tested.

                            Derek ... take my comments with a pinch of salt ... if there is one thing i have learnt on social media ... I dont take anything to heart and dont attack anyone in person.

                            The reason I waste my time here is to learn from everyone ... this earth leakage topic has got my attention ... if I can learn something from it ... you have got my attention.
                            Comments are based on opinion...not always facts....that's why people use an alias.

                            Comment

                            • Dave A
                              Site Caretaker

                              • May 2006
                              • 22812

                              #15
                              If you recall the discussion, part of the issue was Derlyn is from East London and the supply authority doesn't supply a separate earth from the star point of the transformer...