Hi Guys
I need some advice from you guys about the proper way to install my 2.5kW Solis single phase grid-tie inverter into my DB board. As per the manual, the inverter should be connected in parallel with the mains (before the earth leakage) and through a disconnecting device and preferably current limit to 15A.

Attached is a photo of my current DB, but I've drawn it as a diagram as well (it's a small townhouse so it's a tiny DB and all circuits are protected by EL, including the geyser).

Is my understanding correct:
- Label existing half of DB "GRID" and label new breaker(s) with "Alternate Supply"
- Add a new mains-rated breaker (63A 2P). 10mm2 Neutral and Live tapped from Earth Leakage input. Label "Alternate Supply"
- Add new 16A MCB. 10mm2 live tapped from new 63A breaker bottom. Label "Inverter"
- Connect inverter using live from bottom of new 16 MCB. Neutral from neutral bar. Earth from earth bar. Surfix with 2.5mm2 conductors.
- CT Clamp in seperate conduit to DB clamped around live from prepaid meter before mains breaker.
Here is the diagram of what I mean:

Lastly, instead of using both a isolator and MCB, can I use just a 16A double-pole MCB to function as over-current and isolator (the poles connected being live and neutral)?
I need some advice from you guys about the proper way to install my 2.5kW Solis single phase grid-tie inverter into my DB board. As per the manual, the inverter should be connected in parallel with the mains (before the earth leakage) and through a disconnecting device and preferably current limit to 15A.
Attached is a photo of my current DB, but I've drawn it as a diagram as well (it's a small townhouse so it's a tiny DB and all circuits are protected by EL, including the geyser).
Is my understanding correct:
- Label existing half of DB "GRID" and label new breaker(s) with "Alternate Supply"
- Add a new mains-rated breaker (63A 2P). 10mm2 Neutral and Live tapped from Earth Leakage input. Label "Alternate Supply"
- Add new 16A MCB. 10mm2 live tapped from new 63A breaker bottom. Label "Inverter"
- Connect inverter using live from bottom of new 16 MCB. Neutral from neutral bar. Earth from earth bar. Surfix with 2.5mm2 conductors.
- CT Clamp in seperate conduit to DB clamped around live from prepaid meter before mains breaker.
Here is the diagram of what I mean:
Lastly, instead of using both a isolator and MCB, can I use just a 16A double-pole MCB to function as over-current and isolator (the poles connected being live and neutral)?