The most important part of the installation ... the COC (I know I bash COC's all the time) ... without it ... legit or not ... at least you have a claim against the insurance or the contractor who installed it and a case can be opened with the AIA.
The very first investigation ... done by a person who apparently comes highly recommended and is installing systems faster than Eskom can load shed.
First thing before I even started the investigation ... no COC ... I should shut the system down until at least an inspection report is carried to very it is not a dangerous installation.
I walked up to the panel and the very first thing I noted was the exposed wires below the inverter ... pushed neatly up against the inverter.
The installation looks neat ... just because the installation look neat ... it doesn’t make it safe or legal ... it only gives a max of 5 point of the 100 required to pass.
I pull the covers off the trunking ... PVC ...I don’t see an issue with PVC trunking.
next issue ... battery wires and house wiring running in the same compartment ... we have discussed this issue in the past and if the cabling is rated at 450 - 1000 V ... can you run 48 VDC and 230 VAC in the same trunking ... even for short distances?
The next issue was earth wires twisted together using skrewits ... some people will say its illegal ... personally I feel the fact that the earth wires are connected in the trunking and not the DB above the trunking is not right.
Then I opened the DB ... well this is where I see things that make me realise that it is going to be a proper full investigation ...not just a quick over view of the installation.
The metal DB has a cut out at the bottom for the wiring ... it looks like a hammer and chisel was used to make the cut out and there is the first fail ... one of the wires is already penetrated by the sharp piece of steel.
It just got worse.
Some advice for people using a solar/inverter installer ... the most important part is that the installer has the correct certification to carry out the installation ... can issue a COC on completion ... not get it checked by a buddy or the inspector who signs them off a dime a dozen from his house up north.
Installations are costing R100 000 plus ... don’t be f%^&*n stupid ... just because Molly ... Pete and dick said on the group that Joe Soap is the man to use for your new installation ... there are people out there who know there stuff and are suitably qualified to perform the task ... just make sure you verify their credentials ... check they have the correct qualifications and licenses to do the job.
It is also very important that staff working on your property wear the card indicating the level of competency. It an appy or semi-skilled is left to do the work he will have a card which he should be wearing indicating the level of competency ... if you don’t know what they can do ... then calling the DOL ... ECB or ECA will clarify the tasks they can perform.
If a person doesn’t have a semi-skilled card ... they cant do much other than dig holes and carry stuff ... certainly not be installing and connecting cables.
Beware people ... load shedding is bring out all the rats and mice willing to do anything for a quick buck ... a couples hours of googling and YouTube will could make you a specialist before the sun sets ... people are desperate and willing to piss hundreds of thousands of rands against the wall ... hence my decision to start getting a piece of the pie.
The very first investigation ... done by a person who apparently comes highly recommended and is installing systems faster than Eskom can load shed.
First thing before I even started the investigation ... no COC ... I should shut the system down until at least an inspection report is carried to very it is not a dangerous installation.
I walked up to the panel and the very first thing I noted was the exposed wires below the inverter ... pushed neatly up against the inverter.
The installation looks neat ... just because the installation look neat ... it doesn’t make it safe or legal ... it only gives a max of 5 point of the 100 required to pass.
I pull the covers off the trunking ... PVC ...I don’t see an issue with PVC trunking.
next issue ... battery wires and house wiring running in the same compartment ... we have discussed this issue in the past and if the cabling is rated at 450 - 1000 V ... can you run 48 VDC and 230 VAC in the same trunking ... even for short distances?
The next issue was earth wires twisted together using skrewits ... some people will say its illegal ... personally I feel the fact that the earth wires are connected in the trunking and not the DB above the trunking is not right.
Then I opened the DB ... well this is where I see things that make me realise that it is going to be a proper full investigation ...not just a quick over view of the installation.
The metal DB has a cut out at the bottom for the wiring ... it looks like a hammer and chisel was used to make the cut out and there is the first fail ... one of the wires is already penetrated by the sharp piece of steel.
It just got worse.
Some advice for people using a solar/inverter installer ... the most important part is that the installer has the correct certification to carry out the installation ... can issue a COC on completion ... not get it checked by a buddy or the inspector who signs them off a dime a dozen from his house up north.
Installations are costing R100 000 plus ... don’t be f%^&*n stupid ... just because Molly ... Pete and dick said on the group that Joe Soap is the man to use for your new installation ... there are people out there who know there stuff and are suitably qualified to perform the task ... just make sure you verify their credentials ... check they have the correct qualifications and licenses to do the job.
It is also very important that staff working on your property wear the card indicating the level of competency. It an appy or semi-skilled is left to do the work he will have a card which he should be wearing indicating the level of competency ... if you don’t know what they can do ... then calling the DOL ... ECB or ECA will clarify the tasks they can perform.
If a person doesn’t have a semi-skilled card ... they cant do much other than dig holes and carry stuff ... certainly not be installing and connecting cables.
Beware people ... load shedding is bring out all the rats and mice willing to do anything for a quick buck ... a couples hours of googling and YouTube will could make you a specialist before the sun sets ... people are desperate and willing to piss hundreds of thousands of rands against the wall ... hence my decision to start getting a piece of the pie.