"AC fusing parallel strings
For units in parallel it is advised to use one AC fuse for all units on that phase. Both on the input, and on the
output. Multiple fuses which are mechanically connected are okay to be used, this is counted as one fuse"
If 3 x 5 kva units in parallel are used ... consideration if the units are 4000w (17 amps) or 5000w (21 amps) units
If I understand this correctly ...
Either 1 x single 50(4000 w) /60 (5000w) amp circuit breaker must be used wired from the breaker to the first unit looped to the second and then the third.
or
1 x triple pole 32/40 circuit breaker ... wired using 4mm or 6 mm wire ...each wire from the breaker to the inverter.
The apext installer manual (5 kva) recommends using 10 mm square wire (but that would be if you use 1 x circuit breaker.)
or