How many of you still install earth conductors as we have in the old days?
I have been spending time reading the SANS book to find ways to cut costs.
6.12.1.1 An earth continuity conductor
Do you install a 6 mm wire if you run a red and black 6mm or do you use a 4 mm wire.
If you look at table 6.28 ... protective device 40 amp ... so long as the cable is not longer than 80 m a 4 mm earth wire is fine.
If you look at twin+e or armoured cable ... those little earth conductors used are a fraction of the size in comparison to the live conductors.
I have been spending time reading the SANS book to find ways to cut costs.
6.12.1.1 An earth continuity conductor
Do you install a 6 mm wire if you run a red and black 6mm or do you use a 4 mm wire.
If you look at table 6.28 ... protective device 40 amp ... so long as the cable is not longer than 80 m a 4 mm earth wire is fine.
If you look at twin+e or armoured cable ... those little earth conductors used are a fraction of the size in comparison to the live conductors.

... if it was safe enough for ed 2 ... I am sure it will be fine ... It seems I am going to have to purchase ed 3 ... anyone know if there are any changes ... upgrades or modification in the next few months ... I dont want to go waste money buying ANOTHER BOOK to add to my already full shelf of SANS books?