ABC cable suspended from beef wood trees

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • Thys LOW Elektries
    Silver Member

    • Jan 2021
    • 269

    #1

    ABC cable suspended from beef wood trees

    Good day

    Out on the farm farmers can make good plans
    Can one use a couple of beefwood trees to run your cable from one structure to another??

    I can think of a number of reasons why it is unsafe but can't find any legal reason to stop a person from doing it

    Hope their is someone with more knowledge and experience out there that might point me in the right direction

    Have fun
  • adrianh
    Diamond Member

    • Mar 2010
    • 6320

    #2
    Telkom inadvertently did that with the telephone lines in my area - the trees grew and the lines failed!

    Comment

    • GCE
      Platinum Member
      • Jun 2017
      • 1495

      #3
      If I am struggling to find a definite regulations to fail a part of the installation because it looks and feels wrong , I have a go to clause, 5.1

      5 Fundamental requirements
      5.1 General
      All commodities in an electrical installation shall be installed in accordance
      with the requirements in this part of SANS 10142 and with the manufacturer's
      instructions, where applicable.

      NOTE 1 This clause contains the general safety principles applicable to electrical
      installations.
      NOTE 2 The manufacturer's instructions may contain more stringent requirements.


      An existing "live" tree would not pass and could put some kids life at risk when he decides to climb it , and as the tree grows so the strain on the cable will change

      You could also use 6.2.14.4 + 6.3.4.2 + 6.4.1e

      6.2.14.4 ABC cables are intended to be suspended between structures and
      shall not be buried directly in the ground.

      6.3.4 Aerial conductors
      6.3.4.1 An aerial conductor shall be of
      a) hard-drawn copper,
      b) stranded aluminium, or
      c) composite construction, such as steel-cored aluminium.
      6.3.4.2 A surge protective device should be installed at each end of each
      aerial conductor circuit in an installation (see 6.7.6).
      The arrangement, support and, where required, insulation of an aerial
      conductor shall comply with the relevant statutory requirements
      .


      6.4 Positioning and fixing of cables
      6.4.1 Positioning
      A cable shall not be run
      a) in the same trench or wireway as a supplier's cable, except with the
      supplier's permission,
      b) in the same wireway as the cables or wires of telecommunication, radio
      and signalling circuits that are not covered by this part of SANS 10142,
      c) where it is likely to be damaged by liquids such as oil, acid, acetone and
      alkali or by gases such as sulfur dioxide,
      d) within 150 mm of hot services such as hot pipes and flues if the heat is
      likely to damage the cable, unless the cable is cooled or shielded from
      heat, or
      e) in a position where it is likely to be damaged, unless it is mechanically
      protected.

      Comment

      • GCE
        Platinum Member
        • Jun 2017
        • 1495

        #4
        Power lines are also covered under the OHSA , Electrical Machinery regulations



        Overhead power lines
        19. (1) A supplier, employer or user shall cause the supports, clearances,
        insulators and fittings and conductors for power lines to be designed, installed
        and maintained in accordance with the relevant health and safety standard
        incorporated into these Regulations under section 44 of the Act.

        (7) The employer or user shall ensure that all supports of the lattice type
        which are used to carry overhead conductors or live parts of other ~lectrical
        equipment are adequately protected in order to prevent any unauthorized person
        from coming into dangerous proximity of the conductors by climbing such
        supports, and an inspector may require an employer or user similarly to protect a
        support of any other type.

        Comment