    Separation of AC and DC wiring in backup systems

    It seems there are rules with regards to AC and DC separation ... it seems the attitude is the same as my attitude to euro plugs in my house.

    What are the facts with regards to installing AC and Dc wiring for backup systems ... in the same wireways ...

    is there a specific distance

    types of barriers required

    crossing over of AC and DC wires in wireways.

    What happens when you get to the inverter and you have a whole lots of AC and DC wires you need to now get into the inverter?
    Comments are based on opinion...not always facts....that's why people use an alias.
  • Dylboy
    Gold Member

    • Jun 2020
    • 777

    #2
    I have the exact same thoughts! It irritates me to no end! We need the definition of separation.

    Is a single layer of PVC considered suitable separation... is it a 5mm gap... is it a PVC trunking plastic thickness fine like in those Dual power trunkings...

    What about if they cross wires at 90° or run parallel....


    What about having some 12V DC relays in a AC DB board... how far apart must they be to AC breakers, can the wires touch or just there be a 10mm gap or mist DC be 100% jn its own enclosure...? Smaft home stuff is real and there is DC components that will control AC so we need clarification.

    There may be some somewhere but I can't find it yet


    Sent from my SM-N960F using Tapatalk

    Comment

    • GCE
      Platinum Member
      • Jun 2017
      • 1495

      #3
      Hi

      I find the regulation clear with regards to separation
      We tend to run a U shape trunking when it comes to inverters and DC cabling and use a split trunking if need be .
      We have also run cable tray with a P8000 in the tray for Data cables to keep separate

      Have attached reg below that I feel is relevant and a pic of the latest install.



      6.1.7 If conductors that operate at different voltages run in the same wireway,
      the insulation of each conductor shall be able to withstand the highest
      conductor voltage in the wireway. Alternatively, the conductors shall be
      separated by a continuous barrier of insulating material or earthed metal.

      6.1.10 Conductors that form part of a d.c. installation shall not be run in the
      same wireway as conductors that form part of an a.c. installation.

      3.85
      wireway
      open or enclosed route or support such as a rack, tray, ladder, ducting,
      trunking, sleeving or conduit that is intended to contain conductors or cables
      NOTE A wireway can consist of one or more separate wireway channels, each of
      which is intended for different services such as installation wiring and
      telecommunication wiring.



      Click image for larger version

Name:	1.jpg
Views:	1
Size:	23.6 KB
ID:	266098

      Comment

      • Dylboy
        Gold Member

        • Jun 2020
        • 777

        #4
        That is well and good for wireways but I am more asking about in a DB, apologies i was not specific but that is more where my mind is.


        Sent from my SM-N960F using Tapatalk

        Comment

        • BobZA
          Email problem
          • Oct 2018
          • 20

          #5
          Hi,

          I think GCE covered it all pretty nicely from a regs point of view for wireways

          For me the remainder is down to good practice and best effort. Wherever possible run AC and DC wires separately. Where paths cross ... try cross at 90 degrees.

          In some panels/DB's it is virtually impossible ... but perhaps a strategically placed piece of trunking / tubing can help separate some of the "delicate" wires.

          Comment

          • ians
            Diamond Member

            • Apr 2010
            • 3943

            #6
            When you run the P8000 ... do you put short pieces of earth wire with a lug or do you just use the pop rivetted joiner for the P8000 as the earth continuity.
            Comments are based on opinion...not always facts....that's why people use an alias.

            Comment

            • ians
              Diamond Member

              • Apr 2010
              • 3943

              #7
              Originally posted by BobZA
              Hi,

              I think GCE covered it all pretty nicely from a regs point of view for wireways

              For me the remainder is down to good practice and best effort. Wherever possible run AC and DC wires separately. Where paths cross ... try cross at 90 degrees.

              In some panels/DB's it is virtually impossible ... but perhaps a strategically placed piece of trunking / tubing can help separate some of the "delicate" wires.
              The 90 % cross over is more for data applications ... when it comes to AC/DC and voltage variations ... its more about the highest voltage insulation protection.
              Comments are based on opinion...not always facts....that's why people use an alias.

              Comment

              • GCE
                Platinum Member
                • Jun 2017
                • 1495

                #8
                Originally posted by ians
                When you run the P8000 ... do you put short pieces of earth wire with a lug or do you just use the pop rivetted joiner for the P8000 as the earth continuity.
                use the pop rivet or tek screw for bonding and if not joined to the DB then an earth at the beginning
                I have never seen any consultant insist on a bonding strap on each piece besides Transnet

                Comment

                • Weable
                  Email problem
                  • Nov 2021
                  • 9

                  #9
                  GCE covered the answer perfectly. I would not recommend to any one at all to ever run DC and AC in the same wire ways. Always keep them separated and clearly marked. If in the same enclosure be it trunking or DB and if there had to be a problem and these currents mingle together for an evening drink. It will be a totally off the chat show

                  Comment

                  • GCE
                    Platinum Member
                    • Jun 2017
                    • 1495

                    #10
                    Originally posted by Dylboy
                    That is well and good for wireways but I am more asking about in a DB, apologies i was not specific but that is more where my mind is.


                    Sent from my SM-N960F using Tapatalk
                    Been thinking on this one and specifically to home automation type systems .

                    Technically a DB is not a wireway .
                    The home auto system use extremely low DC and generally with low current limiting capabilities to prevent damage to the components.
                    The home automation relays would generally be built into there own separate enclosure and I would term the "DB" as a motor control center or machine

                    I would say " each conductor shall be able to withstand the highest conductor voltage" as per 6.1.7 and as mentioned above , keep the control wiring in a separate trunking within the DB.
                    I would also use clause 5.1 note 2

                    5 Fundamental requirements
                    5.1 General
                    All commodities in an electrical installation shall be installed in accordance
                    with the requirements in this part of SANS 10142 and with the manufacturer's
                    instructions, where applicable.
                    NOTE 1 This clause contains the general safety principles applicable to electrical
                    installations.
                    NOTE 2 The manufacturer's instructions may contain more stringent requirements.


                    To me the regulations are written around DC wiring having a high short circuit ratings and the prevention of arching like experienced on PV , inverters ,Battery banks and telecommunication equipment.
                    I cannot think of anywhere that home automation systems would be mentioned in SANS 10142-1

                    Comment

                    • Dylboy
                      Gold Member

                      • Jun 2020
                      • 777

                      #11
                      Yes ya I agree. Interesting subject none the less and good to know.

                      I know a guy who had almost the whole DB with home auto stuff (12V DC) and is currently taking it out and separating to get it compliant. This is where my dive into DC and all is coming from mostly. When we do solar or inverter its all separate amd fairly easy to do so.

                      Either way separation with conduit or trunking helps and then the double insulated cable i feel is similar as it has a second protective covering but not sold on that yet.

                      Just good to chat about all this and learn, get opinions and grow. I tried the ECA on a number of occasions for all sorts and I get nothing... perhaps because not a member hahah.

                      Sent from my SM-N960F using Tapatalk

                      Comment

                      • ians
                        Diamond Member

                        • Apr 2010
                        • 3943

                        #12
                        Just a note for anyone reading these posts ... its not about being the brightest crayon in the box or Harvard degree bright spark ... at the end of the day what happens in these threads is more important ... when you are seated in the box and every one is waiting for your response ... what they want to hear is ... what steps did you take to prevent an incident.

                        Being the smartest lad in the room is not always the best ... they going to pin you for being the person who should have know better ... thats what it all boils to.

                        Ask a lot of question and make an effort to do it right ... and generally you will be ok ... nobody is perfect ... and beware of people who think they know everything.
                        Comments are based on opinion...not always facts....that's why people use an alias.

                        Comment

                        Working...