    7.12 Alternative supplies

    Time to sit down put plug in the airpods with background sounds and review section 7.12

    What are the requirements .. .the way I read it.

    Labels labels labels and as many more labels and notices on each DB.

    Indicator - A din mount light next to the main switch is my preference.

    Change over switch as per requirements.

    As per requirements - earth leakage protection for plugs ... I am still trying to understand why people insist on installing earth leakage on the supply to the inverter ... I can understand samll plug in UPS ... but not a 5 kva inverter connected directly to a DB.

    V-O-V type generators not to be connected to the "fixed" electrical installation.
    Comments are based on opinion...not always facts....that's why people use an alias.
  • ians
    Diamond Member

    • Apr 2010
    • 3943

    #2
    Earthing requirements...

    Where there is no earth spike already installed ... a suitable one must be installed and bonded to the consumer earth terminal with a wire at least half the thickness of the phase conductor ... but not less than 6 mm.

    But this note is rather interesting ... deosnt his mean that if you install a spike you dont need an SPD ... or if you install an SPD you dont need the spike.

    NOTE 2 Protection of photovoltaics can be by means of or surge protective device
    (SPD).

    This section is one that seems to be a little confusing for many.

    7.12.3.1.2 In an installation that is supplied from a combination of
    transformers and alternative supplies located near to each other, the neutral
    points of each of these items shall be connected to a single earthed neutral
    bar (see P.1). This earthed neutral bar shall be the only point at which the
    neutral of the installation is earthed. Any earth leakage device shall be
    positioned in such a way as to avoid incorrect operation due to the existence
    of any parallel neutral/earth path.
    7.12.3.1.3 Where alternative supplies are installed remotely from the
    installation, or from one another, and where it is not possible to make use of
    a single neutral bar or neutral conductor which is earthed, the neutral of each
    unit shall be earthed at the unit and these points shall be bonded to the
    consumer's earth terminal (see 6.12.4). The supply from each unit which
    supplies the installation or part of the installation, shall be switched by means
    of a switch that breaks all live conductors operating substantially together (see
    figures P.2 and P.4), to disconnect the earthed neutral point from the
    installation neutral when the alternative supply is not connected (see also
    6.1.6).
    NOTE Where four pole switching is implemented, consideration should be given to use
    overlapping neutral switching devices.
    7.12.3.1.4 Where only part of an installation is switched to the alternative
    supply in the same distribution board, the neutral bar shall be split (see
    figures P.2 and P.3).
    Comments are based on opinion...not always facts....that's why people use an alias.

    Comment

    • Derlyn
      Platinum Member
      • Mar 2019
      • 1765

      #3
      Originally posted by ians
      Time to sit down put plug in the airpods with background sounds and review section 7.12

      What are the requirements .. .the way I read it.

      Labels labels labels and as many more labels and notices on each DB.

      Indicator - A din mount light next to the main switch is my preference.

      Change over switch as per requirements.

      As per requirements - earth leakage protection for plugs ... I am still trying to understand why people insist on installing earth leakage on the supply to the inverter ... I can understand samll plug in UPS ... but not a 5 kva inverter connected directly to a DB.

      V-O-V type generators not to be connected to the "fixed" electrical installation.
      Another question.

      Why is it not a requirement that a generator have a built in earth leakage ?
      I mean, after all there are socket outlets on a genny where all sorts of appliances are plugged in.

      Derek

      Comment

      • Dylboy
        Gold Member

        • Jun 2020
        • 777

        #4
        The last bit is where I get muddled up. It may be a case of someone sitting me down and explaining and then answering all my questions I have to then understand.

        The whole neutral earth bar bit is tricky. I have seen inverters that output need an "earthing box" so as when it kicks in the alt supply the N and E are bonded but when grid is back then it dissconects and the N is now floating... why can it all not be joined to incoming E and then joined to the N to all be the same.??

        I may be missing something very simple but it seems very complex for no reason..

        They say the N and E shall (i think its a shall)be joined on the supplier side only so if that's the case for not perm joining the inveter output N to E I think they must rethink or at least I must be taught why it must be so.



        Sent from my SM-N960F using Tapatalk

        Comment

        • ians
          Diamond Member

          • Apr 2010
          • 3943

          #5
          I am trying to figue out why you would feed a changeover over switch from an earth leakage unit ... then fit an earth leakage unit from the alternate supply ... why not just fit the earth leakage P.2/P.3/P.4 on the essential side ... its like saying you can have an earth leakage and you can have and earth leakage while we giving away earth leakage units just add one to the UPS ... it not the show where every one gets something just because they have lots of them
          Comments are based on opinion...not always facts....that's why people use an alias.

          Comment

          • Dylboy
            Gold Member

            • Jun 2020
            • 777

            #6
            Hahahah I see what you saying.
            My only guess is to have additional protection if it is a long cable run or likely to be damaged But then discrimination needs to happen. Otherwise its an ELU ping pong match



            Sent from my SM-N960F using Tapatalk

            Comment

            • Derlyn
              Platinum Member
              • Mar 2019
              • 1765

              #7
              Originally posted by ians
              I am trying to figue out why you would feed a changeover over switch from an earth leakage unit ... then fit an earth leakage unit from the alternate supply ... why not just fit the earth leakage P.2/P.3/P.4 on the essential side ... its like saying you can have an earth leakage and you can have and earth leakage while we giving away earth leakage units just add one to the UPS ... it not the show where every one gets something just because they have lots of them
              @ Ians

              I am talking about a portable generator, not a standby one that's connected to the installation.

              I'm thinking now, how many people have been shocked while using an appliance plugged into a portable genny ?

              Derek.

              Comment

              • ians
                Diamond Member

                • Apr 2010
                • 3943

                #8
                Originally posted by Derlyn
                @ Ians

                I am talking about a portable generator, not a standby one that's connected to the installation.

                I'm thinking now, how many people have been shocked while using an appliance plugged into a portable genny ?

                Derek.
                I would assume (never heard of one myself) there have been cases because if you look at the UK for example they use 110 VAC generators for site work ... I used a 5 kva generator for about 10 years ... and boy did that thing get abused and the cables would be in the rain ... hammering away with a jackhammer ... cant say I ever recall a shocking experience ... the only shocking experiences where when we put a pickhead through a 11 kv or HT cables ... the smaller power just made a puff of smoke ... the 11 kv cables would melt the pick head with a pretty spray.

                It became a ghost story about the devil rising ... one of the stronger guys in our team pegged an HT cable the thing blew up ... melted the pick head ... he shat himself ... but the reason he never came back to work ... when system closed again ... that spray made him think the devil was coming out the ground ... he was one of my best strongest team members ... hasnt seen his since that day
                Comments are based on opinion...not always facts....that's why people use an alias.

                Comment

                • ians
                  Diamond Member

                  • Apr 2010
                  • 3943

                  #9
                  back to the regs.

                  brain is too cluttered with crap by 9 pm ... so I decided to get up early this morning and continue with the revision ... which reminded me that I have the latest draft (wish I had 2 big screens in my office ... looks like I ma going shopping today).

                  Reading through the draft ... what I was looking for in the ed 3 is there in the draft ... the actual labels required and a lot of info with regards to alternate suppliers ... its looks like my weekend is going to be spent reading SANS regs ... havent done that in a few years (maybe 15 years) I might learn something new (and shopping for 2 big screens ... cant work without the "right" equipment )
                  Comments are based on opinion...not always facts....that's why people use an alias.

                  Comment

                  • ians
                    Diamond Member

                    • Apr 2010
                    • 3943

                    #10
                    The new draft refers to SSEG's which should be used in with other specifications like the NRS specs.

                    I see a lot more information with regards to labels (a good thing) ... I have noticed some of the installers are already using these labels referenced in the draft.
                    Comments are based on opinion...not always facts....that's why people use an alias.

                    Comment

                    • ians
                      Diamond Member

                      • Apr 2010
                      • 3943

                      #11
                      Every EGI must have a single line diagram as a minimum ... yes please ... with a copy attached to the COC and secured in the main DB or next to the main DB ... this is just as important as the labeling.

                      There should also be a diagram of the PV layout with all the relevant information ... especially the voltage and current produced by the panels.
                      Comments are based on opinion...not always facts....that's why people use an alias.

                      Comment

                      • ians
                        Diamond Member

                        • Apr 2010
                        • 3943

                        #12
                        AC and DC must be mechanically separated and labeled.

                        The single line diagram must be displayed at the DB.
                        Comments are based on opinion...not always facts....that's why people use an alias.

                        Comment

                        • ians
                          Diamond Member

                          • Apr 2010
                          • 3943

                          #13
                          The use of screw type and not compression type metal conduit ... so no bosal conduit on the roof top ?

                          the job I am watching being installed on the roof of a garage ... I wonder if PVC piping and trunking is allowed ... let see as we dig deeper.
                          Comments are based on opinion...not always facts....that's why people use an alias.

                          Comment

                          • ians
                            Diamond Member

                            • Apr 2010
                            • 3943

                            #14
                            functional earthing requirements ... this is gonna required more attention ... need to wrap my head around this.
                            Comments are based on opinion...not always facts....that's why people use an alias.

                            Comment

                            • Dylboy
                              Gold Member

                              • Jun 2020
                              • 777

                              #15
                              Originally posted by ians
                              That an interesting one 5.4.4.6

                              The use of screw type and not compression type metal conduit ... so no bosal conduit on the roof top ?

                              the job I am watching being installed on the roof of a garage ... I wonder if PVC piping and trunking is allowed ... let see as we dig deeper.
                              Is that in Ed 3?

                              And then the AC DC mechanically separated is an intresting one as well!

                              Sent from my SM-N960F using Tapatalk