7.12 Alternative supplies

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • ians
    Diamond Member

    • Apr 2010
    • 3943

    #16
    I have removed any reference to the sans draft ... as this thread is for discussion only to help us understand what might become the new regs.

    Dave can we move this thread to a members only or closed group.
    Comments are based on opinion...not always facts....that's why people use an alias.

    Comment

    • ians
      Diamond Member

      • Apr 2010
      • 3943

      #17
      I need t find out if we can discuss this on this forum before I continue ... Dave or someone will know the legal implications ... I will wait for a response before I continue.
      Comments are based on opinion...not always facts....that's why people use an alias.

      Comment

      • ians
        Diamond Member

        • Apr 2010
        • 3943

        #18
        Ok so you just google draft and walla ... so I am sure it is fine to discuss this on a public forum ?

        Comments are based on opinion...not always facts....that's why people use an alias.

        Comment

        • ians
          Diamond Member

          • Apr 2010
          • 3943

          #19
          Comments are based on opinion...not always facts....that's why people use an alias.

          Comment

          • ians
            Diamond Member

            • Apr 2010
            • 3943

            #20
            Trying to understand the functional earth ... does this mean that if you connect lets say the negative conductor to the supplier earth ... you dont need to run separate earth wires with the DC cables ?
            Comments are based on opinion...not always facts....that's why people use an alias.

            Comment

            • Dylboy
              Gold Member

              • Jun 2020
              • 777

              #21
              That first PDF I really enjoy, even though its a draft it has decent info and good practices so I follow that in conjuction with 10142-1.

              Thanks for the second PDF, will read later on. Got a stuffy nose and not feeling well so retaing info is making my head explode haha.

              Sent from my SM-N960F using Tapatalk

              Comment

              • Dylboy
                Gold Member

                • Jun 2020
                • 777

                #22
                Originally posted by ians
                Trying to understand the functional earth ... does this mean that if you connect lets say the negative conductor to the supplier earth ... you dont need to run separate earth wires with the DC cables ?
                Also do we have to earth the dc side of things. Bt earth i mean for example join the Neutral of the DC battery bank to an earth spike or even the consumer installation MET or the CET ? Also then PV Negative lead must that be earthed like the battery bank ?

                Sent from my SM-N960F using Tapatalk

                Comment

                • GCE
                  Platinum Member
                  • Jun 2017
                  • 1495

                  #23
                  Originally posted by Derlyn
                  @ Ians

                  I am talking about a portable generator, not a standby one that's connected to the installation.

                  I'm thinking now, how many people have been shocked while using an appliance plugged into a portable genny ?

                  Derek.
                  One of the reasons for VOV gensets on site .
                  The voltage to earth if you pick up a shock is 110v not 220v
                  A genset is generally not referenced to earth , rubber vibration pads between genset and frame - If you measure from live to ground as in earth , sand , you should measure 0V , so you cannot become the earth path

                  Comment

                  • ians
                    Diamond Member

                    • Apr 2010
                    • 3943

                    #24
                    Originally posted by GCE
                    One of the reasons for VOV gensets on site .
                    The voltage to earth if you pick up a shock is 110v not 220v
                    A genset is generally not referenced to earth , rubber vibration pads between genset and frame - If you measure from live to ground as in earth , sand , you should measure 0V , so you cannot become the earth path
                    You must like in the Cape ... I have never in all the time of hiring purchasing or installing a 5 kva generator ever seen a generator with vibrating pads ... other than the bigger diesel floor standing units ... we install vibration pads.
                    Comments are based on opinion...not always facts....that's why people use an alias.

                    Comment

                    • GCE
                      Platinum Member
                      • Jun 2017
                      • 1495

                      #25
                      Originally posted by Dylboy
                      They say the N and E shall (i think its a shall)be joined on the supplier side only so if that's the case for not perm joining the inveter output N to E I think they must rethink or at least I must be taught why it must be so.



                      Sent from my SM-N960F using Tapatalk
                      Basically ,only the supplier may earth the neutral - You can become the supplier on the load side of a generator or inverter .

                      6.1.6 The neutral conductor shall not be connected direct to earth or to the
                      earth continuity conductor on the load side of the point of control except as
                      allowed in 7.16.4.


                      You will see that this is also stipulated in municipal bylaws and Eskom bylaws since the day dot.

                      The reason behind the reg is to prevent fires and I will take an extreme case as an example.

                      My house is fed from the municipal cable network and I take 80 Amp single phase supply.The neutral is earthed at the substation transformer, 800KVA
                      If I then install an inverter and bridge my inverter neutral to earth with a 6sqmm or 4sqmm wire as the inverter is only 1KVA, and that inverter neutral is direct connection to municipal neutral.

                      If for some reason the municipal earthed/neutral comes loose or is stolen my house neutral/earth now becomes the earth/neutral for the 800KVA transformer and all imbalanced load will flow through my 16sqmm mains cable and then through my 4sqmm neutral to my inverter which is earthed
                      That 4sqmm wire could be in my roof space , overheat due to the current flow and cause a fire .
                      That earth neutral current flow could be as high as 200Amp on an imbalanced load.

                      That is the though process for that particular regulation

                      Comment

                      • ians
                        Diamond Member

                        • Apr 2010
                        • 3943

                        #26
                        I am wondering if I should even waste my time to carry on reading the SANS ed 3 version of alternate supplies ... compared to the latest draft regs ... it is pretty useless.

                        The new drat makes a lot more sense the label description and everything is more up to date.
                        Comments are based on opinion...not always facts....that's why people use an alias.

                        Comment

                        • ians
                          Diamond Member

                          • Apr 2010
                          • 3943

                          #27
                          Originally posted by Dylboy
                          Also do we have to earth the dc side of things. Bt earth i mean for example join the Neutral of the DC battery bank to an earth spike or even the consumer installation MET or the CET ? Also then PV Negative lead must that be earthed like the battery bank ?

                          Sent from my SM-N960F using Tapatalk
                          Dont get mixed up with the AC and DC component of the installation ... refer to the AC side as the neutral and the DC is the negative.

                          I am still trying to understand the logic of what I am reading ... it sounds like one of the DC conductors can be bonded to earth which will mean you dont have to run an earth wire with the DC cabling ... but just beware I am trying to makes sense of it ... I am confused myself.
                          Comments are based on opinion...not always facts....that's why people use an alias.

                          Comment

                          • Justloadit
                            Diamond Member
                            • Nov 2010
                            • 3517

                            #28
                            Originally posted by Dylboy
                            Also do we have to earth the dc side of things. Bt earth i mean for example join the Neutral of the DC battery bank to an earth spike or even the consumer installation MET or the CET ? Also then PV Negative lead must that be earthed like the battery bank ?

                            Sent from my SM-N960F using Tapatalk
                            I would say No! Consult the battery or inverter manufacturer.
                            The Neutral of the AC side of the inverter is derived from the battery from a bridge type electronics, so in effect, the negative side of the battery and PV panels are effectively connected to the Neutral of the AC out via a Diode/FET.

                            Joining this to earth would damage the inverter.

                            To add a little bit more here. Whilst the Neutral is connected to the negative of the PV panels and battery, it is not a permanent connection, but rather a high speed switching, in which the Neutral of the AC output is effectively alternated On/Off between the battery/PV positive and negative terminals.
                            Only in the case that the battery/PV are isolated from the AC output may the DC negative side be earthed. However I doubt that they are isolated, as this would increase the cost and physical size of the inverter by introducing an isolating transformer.
                            Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
                            Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

                            Comment

                            • ians
                              Diamond Member

                              • Apr 2010
                              • 3943

                              #29
                              Ok so I phoned a friend ... now I am pissed off because a I stalled purchasing ed 3 ... edition 3.1 was launched 2 weeks ago and by the way apparently there are many changes in the new edition and it still doesnt include the other draft that is still in draft ...

                              I also need to get the NRS 097 code to understand solar installations.

                              I enquired about the functional earth and that kind of stuff and as usual ... its never just as simple as we think
                              Comments are based on opinion...not always facts....that's why people use an alias.

                              Comment

                              • GCE
                                Platinum Member
                                • Jun 2017
                                • 1495

                                #30
                                Originally posted by ians
                                You must like in the Cape ... I have never in all the time of hiring purchasing or installing a 5 kva generator ever seen a generator with vibrating pads ... other than the bigger diesel floor standing units ... we install vibration pads.
                                The alternator and petrol motor are normally fastened to the frame of a portable set with a rubber vibration pad as per attached pic

                                Click image for larger version

Name:	genset.jpg
Views:	1
Size:	72.6 KB
ID:	266103

                                Comment