    [Question] Earth Leakage Trips On All Circuits

    I came across an earth leakage which trips on whichever circuit I switched on.

    With only the Main breaker and the earth leakage switched on, the earth leakage stays on and operates normally when the test button is pressed. However when I switch on any of the other circuits ( plugs, lights, ect.), the unit trips. I replaced the Earth leakage and the same problem persists.

    Any idea what the problem might be?

  • Dylboy
    Gold Member

    • Jun 2020
    • 777

    #2
    Hello

    Is this a new DB or an existing one that now has this tripping issue ?

    Sent from my SM-N960F using Tapatalk

    Comment

    • Derlyn
      Platinum Member

      • Mar 2019
      • 1748

      #3
      Originally posted by Elec-JP
      I came across an earth leakage which trips on whichever circuit I switched on.

      With only the Main breaker and the earth leakage switched on, the earth leakage stays on and operates normally when the test button is pressed. However when I switch on any of the other circuits ( plugs, lights, ect.), the unit trips. I replaced the Earth leakage and the same problem persists.

      Any idea what the problem might be?

      Neutral - earth fault.

      Turn off the main breaker.
      Measure resistance between neutral and earth. Chances are 80% that they are touching somewhere.

      Peace out .. Derek Stuart.

      Comment

      • Leecatt
        Silver Member

        • Jul 2008
        • 404

        #4
        Originally posted by Derlyn
        Neutral - earth fault.

        Turn off the main breaker.
        Measure resistance between neutral and earth. Chances are 80% that they are touching somewhere.

        Peace out .. Derek Stuart.
        I agree, many times I found that the fault was inside of a light fitting where the collection of neutral wires had burned at the connection point and was touching onto Earth.

        Sent from my SM-A705FN using Tapatalk
        To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

        Comment

        • Justloadit
          Diamond Member

          • Nov 2010
          • 3518

          #5
          What I have done in the past, is to switch all the circuit breakers off.
          Then with a multimeter set on Ohms, I check each switched off "Live" (Load) side of the circuit breaker to earth.
          Once I find the circuit which has a resistance reading.
          I then proceed to maintain the meter connected to the offending circuit, then remove one Neutral wire at a time from the bus bar.
          Once I find the Neutral that is causing the issue, I then proceed to identify where the circuit is, or if that is a mixed circuit, I will identify it by switching all the other breakers on, and check around the site to see what is not working.
          Then proceed from there.

          On most occasions, I have found humidity or water in a junction box on a wall where there has been a badly made connection, or that has been badly insulated from the elements