    Brain fart, 3phase

    Hello all!

    Hope its a good Tuesday.

    I am having a bit of a brain fart and I guess a bit sleep deprived from the little one.

    But below image i have drawn is a 3phase supply then supplying 3 x single phase main switches, your typical 3 phase house...

    Now my brain is not working on:

    - can each phase pull lets say 60Amps each and not trip the CB as it is rated at 80Amps
    Or will the combined amps which is over 80A trip the CB. ?

    Essentially is the 3phase CB like 3 single pole breakers joined, so each "single pole" has the trip at 80Amps thus allowing each of the phases to pull a max of 80Amps? And if one of them trips it then trips the whole CB ?

    Apologies if this is basic but I am having a struggle today.



    Sent from my SM-N960F using Tapatalk
  • Leecatt
    Silver Member

    • Jul 2008
    • 404

    #2
    The three phase breaker is actually three separate breakers joined together mechanically. Unless it has only one handle then it is constructed differently but works the same.

    Sent from my SM-A705FN using Tapatalk
    To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

    Comment

    • Lourens.dL
      Junior Member
      • Apr 2014
      • 23

      #3
      Just to add, each of the three beakers is rated at 80A and if one phase overload then all will trip.

      Sent from my SM-N975F using Tapatalk

      Comment

      • Dylboy
        Gold Member

        • Jun 2020
        • 777

        #4
        Ahhh ok brilliant, I thought as much, thanks gents, really appreciate it !

        Sent from my SM-N960F using Tapatalk

        Comment

        • Justloadit
          Diamond Member

          • Nov 2010
          • 3518

          #5
          Originally posted by Lourens.dL
          Just to add, each of the three beakers is rated at 80A and if one phase overload then all will trip.

          Sent from my SM-N975F using Tapatalk
          You would not have it any other way, switching one phase off on a 3 phase load is detrimental to the equipment, unless it is a heater bank